Displaying a List of Unconfigured Trendlogs in WebStation

You display a list of unconfigured trendlogs to identify the trendlogs that needs to be started or configured. From the list you can start and configure trendlogs.

Mostrar más
action_close

Diagnostics in WebStation is a method of check the health of your system. Using Diagnostics you can also resolve several issues in the system, for example unconfigured trend log and forced values. You can check the following using diagnostics in WebStation:

  • Disabled alarms

  • Offline or invalid devices

  • Objects that require uploading or downloading to be synchronized with the current configuration

  • Forced values

  • Communication issues between servers

  • Unconfigured and stopped trendlogs

  • Time and time zone settings

  • Logged in users

  • Zoning issues

To display a list of unconfigured trendlogs in WebStation
  1. In WebStation, click the Workspace menu.

  2. Expand the server.

  3. Click System .

  4. In the List view, click Diagnostics .

  5. Click Trendlogs .

  • Diagnostics in WebStation
  • Diagnostics Trendlogs List in WebStation