Introduction

As part of a scalable EcoStruxure Building Management System (BMS), Edge Server provides key functionality, such as control logic, trend logging, and alarm supervision, and supports communication and connectivity to IP based field buses. The distributed intelligence of the EcoStruxure BMS helps ensure fault tolerance against detected faults and provides a fully featured user interface through WorkStation and WebStation.

Edge Server has the same role in an EcoStruxure BMS as the automation server, such as SpaceLogic AS-P, but is software only using modern deployment and orchestration technologies.

Caractéristiques

Edge Server is a powerful software component for customers who prefer use of container technologies for hosting software applications. In a small installation with IP based field controllers, Edge Server acts as a standalone server. In medium and large installations, functionality is distributed over multiple Edge Server instances that communicate over TCP/IP with Enterprise Server as the Operational Technology (OT) orchestrator.

Edge Server possède les caractéristiques suivantes :

  • Hub de communication

  • Conteneur

  • Authentification et autorisations

  • Interface WorkStation/WebStation

  • Prise en charge native BACnet certifiée BTL

  • Nœud, hub ou routeur BACnet/SC

  • Prise en charge native du client OPC UA

  • Prise en charge native de Modbus

  • Prise en charge des services Web basés sur des normes ouvertes

  • Prise en charge des services Web EcoStruxure

  • Prise en charge du protocole MQTT

  • Option de stockage de journal externe

  • Rapports

  • Outils de programmation texte et graphiques

  • Option d’extension E/S

  • Mise en réseau informatique conviviale basée sur la suite de protocoles de communication TCP/IP

  • Prise en charge de TLS

Communications hub

Capable of coordinating traffic from above and below its location, Edge Server can deliver data directly to you or to other servers throughout the site. Edge Server can run multiple control programs, manage alarms and users, handle scheduling and logging, and communicate using a variety of protocols. Because of this, most parts of the system function autonomously and continue to run as a whole even if communication is interrupted or individual EcoStruxure BMS servers or devices go offline.

Container support

Edge Server can be seen as a software-only version of SpaceLogic AS-P, enabling very fast and more secure deployment, a high level of resiliency, and ultra-fast disaster recovery. Edge Server can be deployed on operating systems with Linux container support and in large installations, and orchestration infrastructure such as Kubernetes can be used.

Authentication and permissions

An EcoStruxure BMS provides a powerful permission system that is easy to manage, flexible, and adapts to all kinds of system sizes. The permission system provides a high standard of authentication. Authentication is done against the built-in user account management system or, if used with Enterprise Server, against Windows Active Directory or a SAML 2.0 identity provider. The built-in account management system allows an administrator to establish password policies that meet stringent cybersecurity guidelines. When Windows Active Directory is used, the administration costs are lower because users do not have to be managed in multiple directories.

Interface WorkStation/WebStation

Sur tout client, l’expérience utilisateur est similaire quel que soit le serveur de GTB EcoStruxure auquel est connecté l’utilisateur. L’utilisateur peut se connecter directement au serveur Edge Server pour concevoir, mettre en service, superviser et surveiller le serveur ainsi que les contrôleurs de bus de terrain basés sur IP que le serveur héberge. Consultez les fiches de spécifications WorkStation et WebStation pour de plus amples détails.

Support natif des protocoles ouverts du bâtiment

Une caractéristique essentielle de la solution de GTB EcoStruxure est la prise en charge des normes ouvertes. Edge Server peut communiquer nativement avec deux des normes les plus courantes pour les bâtiments : BACnet (y compris BACnet/SC) et Modbus.

Prise en charge native de BACnet certifiée par BTL

Edge Server communique directement avec les réseaux BACnet/IP. Edge Server est certifié par BTL en tant que contrôleurs de bâtiment BACnet (B-BC), le profil d’appareil BACnet le plus avancé. Cette fonctionnalité permet d’accéder à une vaste gamme d’appareils BACnet de Schneider Electric et d’autres fournisseurs. Des informations à jour sur les versions de micrologiciel certifiées par BTL sont disponibles dans le catalogue des produits BTL sur la page d’accueil de BACnet International. Edge Server peut également servir de dispositif de gestion de diffusion BACnet (BBMD) pour faciliter les systèmes BACnet qui couvrent plusieurs sous-réseaux IP.

BACnet/SC (Secure Connect) support

Edge Server supports BACnet/SC applications as a BACnet/SC node, hub, and router. This allows Edge Server to be in BACnet/SC networks and support applications that connect BACnet/IP with BACnet/SC networks. A major benefit of BACnet/SC is that it allows more secure transport of BACnet traffic and information between BACnet/SC devices over private and public networks without the need for BBMDs, VLANs, and VPNs, because the BACnet/SC protocol uses WebSocket technology and TLS 1.3 encryption. In addition, BACnet/SC uses certificate management to help ensure only those devices authorized to be on a BACnet/SC network can operate on that network.

Native OPC UA Client support

OPC UA Client functionality is natively supported in Enterprise Server and automation servers, enabling powerful and high-capacity integration of devices or systems that have OPC UA Server capability. OPC Unified Architecture (OPC UA) is a standard originating from industrial automation and process control that provides methods intended to provide improved security, performance, and engineering efficiency. With OPC UA Client support, the EcoStruxure Building Operation software can monitor and control a wide variety of devices or systems, from Schneider Electric as well as from other companies.

Native Modbus support

Edge Server natively integrates Modbus TCP client and server configurations. This allows full access to third-party products and the range of Schneider Electric products that communicate on the Modbus protocol, such as power meters, UPS, circuit breakers, and lighting controllers.

Modbus device types are pre-configured Modbus applications for quick and easy Modbus device integration in EcoStruxure Building Operation solutions.

Prise en charge des services Web

Edge Server prend en charge l’utilisation de services Web basés sur des normes ouvertes, telles que SOAP et REST, pour consommer des données dans la GTB EcoStruxure. Utilisez des données entrantes tierces (prévisions de températures, coûts énergétiques) sur le Web afin de déterminer les modes des sites, les calendriers et la programmation.

EcoStruxure Web Services support

EcoStruxure Web Services, Schneider Electric’s Web Services standard, is natively supported in the EcoStruxure BMS servers. EcoStruxure Web Services offers extra features between compliant systems whether within Schneider Electric or other authorized systems. These features include system directory browsing, read/write of current values, alarm receipt and acknowledgement, and historical trend log data. EcoStruxure Web Services requires user name and password to log on to the system.

MQTT IoT protocol support

The Enterprise Server and automation servers support MQTT as an option for publishing data to, and receiving updates from, other systems. MQTT is a messaging transport protocol that with its small footprint, light bandwidth utilization, and simplicity, is ideal for M2M and IoT communication. The MQTT capability supports communication with any MQTT broker, for example, Amazon, Microsoft, Google or IBM.

Option de stockage de journal externe

EcoStruxure BMS servers can be configured to automatically store all historical data, trend log data, event log and audit trail data, in an external database. If data needs to be available for longer periods of time, an external log storage can be incorporated into the EcoStruxure BMS without the need for extensive engineering work. The supported databases are TimescaleDB, which is built on PostgreSQL, and Microsoft SQL Server. The data in the external log storage is available natively to the viewers built into the EcoStruxure Building Operation clients and to the built-in reporting functionality.

You can use the powerful Log Processor functionality for custom processing of trend data for viewing in charts, dashboards and for inclusion in reports. The Log Processor enables advanced calculations on one or multiple trend logs and point values.

Examples of advanced calculations:

  • Energy usage normalization

  • Virtual submeters and summaries

  • Calculation of Mean Kinetic Temperature

  • Unit conversions

  • Average, maximum, and mini m um over custom periods

The output of the Log Processor can be saved in the database, including the External Log Storage or calculated automatically on demand.

From EcoStruxure Building Operation version 5.0.3 and later, selected trend logs and the event log can be sent to AVEVA PI System directly without the need for intermediate storage or specialized PI System connectors.

Reporting

The EcoStruxure BMS servers provide built-in functionality for basic reporting that can deliver reports in any text format and XLSX, without any dependencies to other external software. Reports for XLSX can be enriched by using advanced functionality such as formulas, conditional formatting, charts and sparklines.

Reports can be generated on schedule, on an alarm event or other custom conditions, and you can get the output delivered via email or written to file.

Extension des E/S

For applications that require remote I/O resources, the SpaceLogic IP-IO modules provide a versatile mix of I/O points for any application. For more information, see the SpaceLogic IP-IO Specification Sheet.

Text and graphics-based programming tools

Unique to the industry, the EcoStruxure BMS servers have both Script and Function Block programming options. This flexibility helps assure that a suitable programming method can be selected for the application.

IT friendly

The EcoStruxure BMS servers communicate using the networking standards. This makes installations easy, management simple, and transactions more secure.

Protocoles pris en charge
  • Adressage IP

  • Communications TCP

  • DNS pour une recherche d’adresses en toute simplicité

  • HTTP/HTTPS pour l’accès à Internet via des pare-feux, ce qui permet la surveillance et le contrôle à distance

  • SMTP/SMTPS avec prise en charge de l’authentification basée sur SSL/TLS pour envoyer des e-mails déclenchés par programmation ou alarme

  • SNMP pour la supervision du réseau et la réception des alarmes d’application dans les outils de gestion du réseau désignés

  • Cryptage WebSocket Secure (WSS) et TLS 1.3 (applications BACnet/SC)

TLS support

Communication between clients and the EcoStruxure BMS servers , and between EcoStruxure BMS servers, can be encrypted using Transport Layer Security (TLS ). The servers are delivered with a default self-signed certificate. Commercial Certification Authority (CA) server certificates are supported to lower the risk of malicious information technology attacks. Use of encrypted communication can be enforced for both WorkStation and WebStation access.

Spécifications

Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
BACnet profile
BACnet Building Controller (B-BC), BACnet Secure Connect Hub (B-SCHUB)
BACnet certification
BTL Certification (BTL Listing a , WSPCert)
OPC UA Client
Profile group UACore 1.03
Core Client Facet, Base Client Behaviour Facet a , AddressSpace Lookup Client Facet, Attribute Read Client Facet a , Attribute Write Client Facet a , DataChange Subscriber Client Facet a , Method Client Facet, UA-TCP UA-SC UA-Binary, SecurityPolicy – Basic256, SecurityPolicy – Basic256Sha256, User Token – Anonymous Facet, User Token – User Name Password Client Facet, DataAccess Client Facet, Base Event Processing Client Facet, and Historical Access Client Facet.
Modbus
Modbus TCP, client and server
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.3, 1.2, 1.1 a , and 1.0 a , port configurable default 443
WSS a
Encrypted supporting TLS 1.3, port configurable
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
Part numbers
In the following description, a Connected Product is a communicating device directly connected to a BACnet/IP or Modbus TCP network driven by Edge Server. A device connected to an RP or MP controller is not a Connected Product.
Edge Server – Standalone SW
Support for 10 Connected Products and Modbus TCP.
SXWSWEBU0000SA
Edge Server – Standard SW
Support for 25 Connected Products, Modbus TCP, and Enterprise Server communication.
SXWSWEBU0000SD
Edge Server – Enhanced SW
Support for 100 Connected Products, Modbus TCP, and Enterprise Server communication.
SXWSWEBU0000EN
Edge Server – Full SW
Support for 300 Connected Products, Modbus TCP, and Enterprise Server communication.
SXWSWEBU0000FU
Upgrade software bundles
Edge Server License Upgrade – Standalone to Standard
Upgrades from 10 to 25 Connected Products and adds Enterprise Server communication.
SXWSWEUP00SASD
Edge Server License Upgrade – Standalone to Enhanced
Upgrades from 10 to 100 Connected Products and adds Enterprise Server communication.
SXWSWEUP00SAEN
Edge Server License Upgrade – Standalone to Full
Upgrades from 10 to 300 Connected Products and adds Enterprise Server communication.
SXWSWEUP00SAFU
Edge Server License Upgrade – Standard to Enhanced
Upgrades from 25 to 100 Connected Products.
SXWSWEUP00SDEN
Edge Server License Upgrade – Standard to Full
Upgrades from 25 to 300 Connected Products.
SXWSWEUP00SDFU
Edge Server License Upgrade – Enhanced to Full
Upgrades from 100 to 300 Connected Products.
SXWSWEUP00ENFU
Edge Server Upgrade from software version 5.x – Standalone
Standalone Edge Server upgrade. Upgrades Edge Server from EcoStruxure Building Operation software version 5.x to 6.0.
SXWSWEDGUP50SA
Edge Server Upgrade from software version 5.x – Standard
Standard Edge Server upgrade. Upgrades Edge Server from EcoStruxure Building Operation software version 5.x to 6.0.
SXWSWEDGUP50SD
Edge Server Upgrade from software version 5.x – Enhanced
Enhanced Edge Server upgrade. Upgrades Edge Server from EcoStruxure Building Operation software version 5.x to 6.0.
SXWSWEDGUP50EN
Edge Server Upgrade from software version 5.x – Full
Full Edge Server upgrade. Upgrades Edge Server from EcoStruxure Building Operation software version 5.x to 6.0.
SXWSWEDGUP50FU
Add-on options
SW-EWS-1, EcoStruxure Web Services (run-time) option
Consume only for one automation server
SXWSWEWSXX0001
SW-EWS-2, EcoStruxure Web Services (run-time) option
Serve & Consume for one automation server
SXWSWEWSXX0002
SW-EWS-3, EcoStruxure Web Services (run-time) option
Serve & Consume, plus Historical trend log data for one automation server
SXWSWEWSXX0003
SW-GWS-1, Web Services (Generic Consume) option
For one automation server
SXWSWGWSXX0001
SW-SNMP-1, Alarm notifications via SNMP option
For one automation server
SXWSWSNMPX0001
EcoStruxure Building Operation SmartDriver option
For one AS-P server or Edge Server
SXWSWSDRVX0001
Building Operation Personal Dashboards option, 1 per server required for users logging on to that server to have Personal Dashboard capabilities
For one automation server
SXWSWDASHX0001
SW-ASDBTS-1, TimescaleDB connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBXS001
EcoStruxure Building Operation, Microsoft SQL Server connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBMS001
EcoStruxure Building Operation, AVEVA PI System connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBPI001
SW-ASMQTT-1, MQTT option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWMQTTXRW01
Building Operation Zoning option
For one automation server or Edge Server
SXWSWASSDZR001
Sustainability Pack option
For one automation server or Edge Server
SXWSWASXSUSPK1
OPC UA Client option
For one automation server or Edge Server
SXWSWASXOPCL01
Hardware requirements
Processor frequency
1 GHz
Processor architecture
AMD64 or x86-64
Processor cores
2
Memory
1 GB
Storage capacity
4 GB
Software requirements
Operating systems
OCI compliant container runtime on Linux x86-64
Quality assurance testing has been performed on, and support is provided with, Ubuntu 20.04 and 22.04 with Docker Engine version 20.10.00. Other deployment scenarios have not been tested by Schneider Electric. Product Support Services may require that potential issues can be reproduced in tested and supported environment for full support.
External log storage PostgreSQL option
TimescaleDB 1.2 and later
  
For use of compression: TimescaleDB 2.11 and later
  
PostgreSQL version compatible with the TimescaleDB version
Quality assurance testing has been performed by Schneider Electric with TimescaleDB and PostgreSQL installed natively in Windows 10, Windows Server 2012, 2016, and 2019. Other deployment scenarios have not been tested by Schneider Electric.
External log storage Microsoft SQL option
Microsoft SQL Server 2016 SP1 and later
The following Microsoft SQL Server editions are supported: Enterprise, Standard, and Express.
External log storage AVEVA PI System option
PI Web API 2021 SP3 and database compatible with that version
Quality assurance testing has been performed by Schneider Electric with PI Web API 2021 SP3, and database compatible with that version, installed on Windows Server 2019. Other deployment scenarios have not been tested by Schneider Electric.
  • Enterprise Server
  • SpaceLogic AS-P
  • WorkStation