earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : MP-V
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
02/05/2023

MP-V Modbus

The MP controller Modbus RTU (RS-485) subnetwork allows standard Modbus devices to be connected to the controller. An adapter is required for converting the controller RS-485 Com port with RJ45 interface to screw terminals.

A separate power supply unit (PSU) is needed to power the Modbus devices on the network.

The Modbus RTU protocol is used for the communication. The Modbus communications is characterized by communication between client device(s), which initiate communication and make requests of server device(s), which process requests and return an appropriate response. The MP controller acts as the Modbus client device and the connected (hosted) devices act as server devices.

It is recommended to use the Non-isolated RS-485 Adapter (SXWNISORS48510001) to provide screw termination of the Modbus device wiring and help avoid miswiring. The adapter converts an RS-485 RJ45 interface to screw terminals. Pour plus d'informations, voir Non-isolated RS-485 Adapter .

The maximum total length of the Modbus (RS-485) network is 72 m (236 ft).

The Modbus (RS-485) network cable should be routed in a continuous daisy-chain bus configuration without cable stubs. Pour plus d'informations, voir Cable Routing .

Cable selection is important to achieve good performance and reliability of the Modbus (RS-485) network. The cable must provide twisted pairs and be specified for RS-485 data communications. It is recommended to use a shielded, low-capacitance twisted pair cable with an impedance of 120 ohm and a wire size (cross-sectional area) of 22 to 24 AWG (0.33 to 0.20 mm²). Pour plus d'informations, voir Cable Selection .

The cable shield should be connected to earth ground at one location (preferred at the hosting controller) and should be connected through to the next segment at each device without additional connections to ground.

When the controller is installed in a space that handles conditioned air or return air, the Modbus network cables and IP network cables frequently must be plenum-rated to meet applicable building codes.

Déclaration

LOSS OF COMMUNICATION

  • Ensure that the total length of the Modbus network does not exceed 72 m (236 ft).

  • Use a shielded, low-capacitance twisted pair cable specified for RS-485 data communications, with an impedance of 120 ohm, a cross-sectional area of 22 to 24 AWG (0.33 to 0.20 mm2), and a rating that meets the requirements of the target environment.

Failure to follow these instructions can result in loss of communication.

You need to reconfigure the RS-485 Com A port (RJ45) on the MP-V controller for the Modbus network. The RS-485 Com A port is by default configured for the sensor bus. The Modbus communication parameters can be freely configured regardless of that. Pour plus d'informations, voir MP-V Communication Ports .

 
action_zoom_plus_stroke Location of the RS-485 Com A port on the MP-V controllers
Figure : Location of the RS-485 Com A port on the MP-V controllers

The maximum number of Modbus devices that can be connected to an MP controller depends on the type of Modbus device and the number of Modbus registers.

The maximum number of Modbus registers that can be connected to and managed by an MP controller depends on the communication capacity of the controller's Modbus network.

The MP controller Modbus network supports up to 20 connected Modbus devices with the following restrictions:

  • Maximum of 1,000 Modbus registers per network

64-bit Modbus registers are supported, which can be used in energy metering.

 
action_zoom_plus_stroke Example with a maximum of 20 standard Modbus devices connected to an MP-V controller in a daisy-chain configuration
Figure : Example with a maximum of 20 standard Modbus devices connected to an MP-V controller in a daisy-chain configuration
  • Hardware Overview
  • MP-V Controllers
  • Non-isolated RS-485 Adapter
  • Wiring
  • RS-485 Communications
  • Cable Routing
  • Cable Selection
  • MP-V Communication Ports
  • SpaceLogic MP-V