0
Koncept

Koncept


Produkter: RP-C
Funktionaliteter: Maskinvara
Produktversion: 2023, 2024, 7.0
2023-03-30

RP-C-16A-M-24V Screw Terminals

The RP-C-16A-M-24V model has 16 I/O points and the controller is equipped with 30 fixed screw terminals and a 3-position removable screw terminal block.

Fara Fara

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, RP-C-16A-M-24V
Figur: Screw terminals and other connectors, RP-C-16A-M-24V

The 30 fixed screw terminals are used as follows:

  • Two screw terminals for the power input

  • One screw terminal for ground input

  • Two screw terminals for the return (RET) terminals 4 and 5

  • Six screw terminals for the four solid-state relay (SSR) outputs

  • Four screw terminals for the three relay outputs

  • Three screw terminals for the high power relay output

  • 12 screw terminals for the eight universal inputs/outputs of type Ub

The 3-position removable screw terminal block is used for connection to the BACnet MS/TP (RS-485) network.

Tabell: Screw Terminals, RP-C-16A-M-24V

Terminal number

Designation

Usage

Power input

1

 
action_zoom_plus_stroke
/+

24 VAC, 50/60 Hz, 14 VA

Positive lead (+) when operating the device from 24-30 VDC, 8 W

2

 
action_zoom_plus_stroke
/–

The other output from the 24 VAC transformer connects to terminal 2.

Negative (–) lead when operating the device from 24-30 VDC, 8 W

3

RET

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground.

Return terminals

4

RET

Internally connected to all earth ground and RET terminals

5

RET

Internally connected to all earth ground and RET terminals

RS-485 terminals

6

RS-485+

Connection to TX/RX+ (RS-485+) signal in the BACnet MS/TP (RS-485) network.

7

RS-485–

Connection to TX/RX– (RS-485–) signal in the BACnet MS/TP (RS-485) network.

8

Shield

Convenience terminal to interconnect two shield drain wires (incoming and outgoing). There is no electrical connection in the device. The shield should be connected to ground at only one location and that is recommended to be at the automation server. The shield should not be connected directly to the RET terminal on the automation server. The transient energy on the drain wire should be conducted to ground and not through the automation server.

Solid-state relay (SSR) outputs

9

DO1

SSR output

10

COM1

Common connection for DO1 and DO2

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

11

DO2

SSR output

12

DO3

SSR output

13

COM2

COM2

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

14

DO4

SSR output

Relay outputs

15

COM1

Common connection for DO1, DO2, and DO3

16

DO1

Relay output, type Form A

17

DO2

Relay output, type Form A

18

DO3

Relay output, type Form A

High power relay outputs

19

NC

Normally Closed terminal. High power relay output, type Form C.

20

DO4

Common terminal. High power relay output, type Form C.

21

NO

Normally Open terminal. High power relay output, type Form C.

Universal inputs/outputs

22

Ub1

Universal input/output, type Ub

23

RET

Internally connected to all earth ground and RET terminals

24

Ub2

Universal input/output, type Ub

25

Ub3

Universal input/output, type Ub

26

RET

Internally connected to all earth ground and RET terminals

27

Ub4

Universal input/output, type Ub

28

Ub5

Universal input/output, type Ub

29

RET

Internally connected to all earth ground and RET terminals

30

Ub6

Universal input/output, type Ub

31

Ub7

Universal input/output, type Ub

32

RET

Internally connected to all earth ground and RET terminals

33

Ub8

Universal input/output, type Ub

  • RP-C Controllers
  • RP-C Screw Terminals
  • Wiring