earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos RP-IO
Funcionalidades: Hardware
Versión del producto: 2023, 2024
30/03/2023

RP-IO-16E-M-24V Screw Terminals

The RP-IO-16E-M-24V model has 16 I/O points and the controller is equipped with 30 fixed screw terminals and a 3-position removable screw terminal block.

Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, RP-IO-16E-M-24V
Figura: Screw terminals and other connectors, RP-IO-16E-M-24V

The 30 fixed screw terminals are used as follows:

  • Two screw terminals for the power input

  • One screw terminal for ground input

  • Two screw terminals for the return (RET) terminals 4 and 5

  • 25 screw terminals for the eight universal inputs/outputs of type Ub

The 3-position removable screw terminal block is used for connection to the BACnet MS/TP (RS-485) network.

Tabla: Screw Terminals, RP-IO-16-E-M-24V

Terminal number

Designation

Usage

Power input

1

 
action_zoom_plus_stroke
/+

24 VAC, 50/60 Hz, 7 VA

Positive lead (+) when operating the device from 24-30 VDC, 3 W

2

 
action_zoom_plus_stroke
/–

The other output from the 24 VAC transformer connects to terminal 2.

Negative (–) lead when operating the device from 24-30 VDC, 3 W

3

RET

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground.

Return terminals

4

RET

Internally connected to all earth ground and RET terminals

5

RET

Internally connected to all earth ground and RET terminals

RS-485 terminals

6

RS-485+

Connection to TX/RX+ (RS-485+) signal in the BACnet MS/TP (RS-485) network.

7

RS-485–

Connection to TX/RX– (RS-485–) signal in the BACnet MS/TP (RS-485) network.

8

SHIELD

Convenience terminal to interconnect two shield drain wires (incoming and outgoing). There is no electrical connection in the device. The shield should be connected to ground at only one location and that is recommended to be at the automation server. The shield should not be connected directly to the RET terminal on the automation server. The transient energy on the drain wire should be conducted to ground and not through the automation server.

Universal inputs/outputs

9

Ub9

Universal input/output, type Ub

10

RET

Internally connected to all earth ground and RET terminals2

11

Ub10

Universal input/output, type Ub

12

Ub11

Universal input/output, type Ub

13

RET

Internally connected to all earth ground and RET terminals

14

Ub12

Universal input/output, type Ub

15

Ub13

Universal input/output, type Ub

16

RET

Internally connected to all earth ground and RET terminals

17

Ub14

Universal input/output, type Ub

18

RET

Internally connected to all earth ground and RET terminals

19

Ub15

Universal input/output, type Ub

20

RET

Internally connected to all earth ground and RET terminals

21

Ub16

Universal input/output, type Ub

Universal inputs/outputs

22

Ub1

Universal input/output, type Ub

23

RET

Internally connected to all earth ground and RET terminals

24

Ub2

Universal input/output, type Ub

25

Ub3

Universal input/output, type Ub

26

RET

Internally connected to all earth ground and RET terminals

27

Ub4

Universal input/output, type Ub

28

Ub5

Universal input/output, type Ub

29

RET

Internally connected to all earth ground and RET terminals

30

Ub6

Universal input/output, type Ub

31

Ub7

Universal input/output, type Ub

32

RET

Internally connected to all earth ground and RET terminals

33

Ub8

Universal input/output, type Ub

  • RP-IO Modules
  • RP-IO Screw Terminals
  • RP-IO-12A-M-24V Screw Terminals
  • Wiring