The RP-V sensor bus allows SpaceLogic Sensor devices to be connected to the controller.
The sensor bus is a proprietary RS-485 bus, which provides both 24 VDC power supply and communications for the sensors.
The maximum total length of the sensor bus is 61 m (200 ft). The sensor bus uses a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) and RJ45 connectors. The wire size (cross-sectional area) should be 22 to 26 AWG (0.34 to 0.14 mm²). When the RP-V controller is installed in a space that handles conditioned air or return air, the sensor bus cables and IP network cables frequently must be plenum-rated to meet applicable building codes. 有关更多信息,请参阅 Wiring .
By default, the RP-V controller's RS-485 Com A port is configured and allocated for the sensor bus. 有关更多信息,请参阅 RP-V Communication Ports .
You can connect a single SpaceLogic Sensor to the sensor bus, or you can connect up to four SpaceLogic Sensor devices in a daisy-chain configuration.
When connecting SpaceLogic Sensor devices to the sensor bus through a daisy-chain configuration, the sensor bus ports on the SpaceLogic Sensor are interchangeable.
The maximum number of SpaceLogic Sensor devices that can be connected to the sensor bus is regardless of the sensor model and the combination of cover and sensor base type.
The RS-485 Com A and B ports on the RP-V-4A and -5A models can supply maximum 3000 mW per port and maximum 4000 mW in total for both ports.
The RS-485 Com A port on the RP-V-5C-M model can supply maximum 3000 mW.
The following table shows the power consumption for the different SpaceLogic Sensor models, sensor bases, covers, and devices that can be connected to the sensor bus.
Description |
Model Number |
Power (mW) |
Sensor base with temperature sensor |
SXWSBTXXXSXX |
90 |
Sensor base with temperature and humidity sensors |
SXWSBTHXXSXX |
90 |
Sensor base with temperature and CO 2 sensors |
SXWSBTXCXSXX |
490 |
Sensor base with temperature, humidity, and CO 2 sensors |
SXWSBTHCXSXX |
490 |
Blank cover |
SXWSCBXSELXn a |
0 |
Blank cover with occupancy sensor |
SXWSCBPSELXn a |
20 |
3-button cover (buttons for override and setpoint control) |
SXWSC3XSELXn a |
190 |
3-button cover (buttons for override and setpoint control) with occupancy sensor |
SXWSC3PSELXn a |
210 |
Touchscreen display cover |
SXWSCDXSELXn a |
190 |
Touchscreen display cover with occupancy sensor |
SXWSCDPSELXn a |
210 |
Touchscreen display cover with light control buttons |
SXWSC2XSELXn a |
190 |
Touchscreen display cover with light control buttons and occupancy sensor |
SXWSC2PSELXn a |
210 |
Touchscreen display cover with light and blind control buttons |
SXWSC4XSELXn a |
190 |
Touchscreen display cover with light and blind control buttons and occupancy sensor |
SXWSC4PSELXn a |
210 |
Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover |
SXWSATXXXSLn a |
80 |
Complete non-communicating b SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover |
SLAnXXX c SXWSATXXXRXX d |
0 |
SpaceLogic Bluetooth Adapter e |
SXWBTAECXX10001 |
300 e |
To summarize the power conditions, the sensor bus supports the following key SpaceLogic Sensor combinations:
Blank covers: Up to four sensors of any combination of sensor base types
3-button and touchscreen covers: Up to four sensors of any combination of sensor base types
SpaceLogic LCD temperature sensors: Up to four sensors are supported
Each SpaceLogic Sensor has two 2-position DIP switches, which are used to give the sensor a unique address on the sensor bus. An incorrectly configured or improper DIP switch can cause two sensors to have the same address on the sensor bus, which means that both sensors will be offline. 有关更多信息,请参阅 SpaceLogic Sensors .
SpaceLogic Sensor devices connected to the sensor bus through a daisy-chain configuration can be assigned addresses regardless of the order in which the sensors appear in the daisy chain. For example, sensor number 1 can have the address 4, sensor number 2 can have the address 3, and so on.