This section provides recommendations on wire sizes and lengths for the RP-V controllers.
Para obtener más información, consulte RP-V Models .
The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.
With central transformer wiring, the wire length (distance to the transformer) must be limited to maintain minimum 24 VAC power level to the RP-V controller. Larger wire size (cross-sectional area) helps reduce voltage drop on the 24 VAC line. Para obtener más información, consulte Grounding and Power for Systems with RP-V Controllers .
Terminals |
Minimum Cross-sectional Area |
Maximum Cable Length |
Power input terminals (1, 2) |
0.75 mm² (18 AWG) a |
According to local wiring rules b |
Earth ground terminal (3) |
0.75 mm² (18 AWG) a |
Protective earth ground connection on or within the controller panel |
RS-485 terminals (12, 13, 14) c |
Para obtener más información, consulte RS-485 Communications . |
Para obtener más información, consulte RS-485 Communications . |
Universal inputs/outputs as digital d inputs |
0.34 mm² (22 AWG) |
200 m (650 ft) |
Universal inputs/outputs as analog e inputs |
0.34 mm² (22 AWG) |
100 m (330 ft) |
Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) |
0.75 mm² (18 AWG) |
75 m (250 ft) |
Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) |
1.5 mm² (15 AWG) |
150 m (500 ft) |
Universal inputs/outputs as temperature (thermistor) inputs, up to 150 °C (302 °F) |
1.5 mm² (15 AWG) |
75 m (250 ft) |
Universal inputs/outputs, for actuators and transmitters powered from the same transformer as the RP-V controller |
0.75 mm² (18 AWG) |
20 m (65 ft) |
Universal inputs/outputs, for actuators and transmitters powered from their own transformer (external or internal) |
0.34 mm² (22 AWG) |
200 m (650 ft) |
Universal inputs/outputs as voltage outputs, for actuators powered from their own transformer (external or internal) or when the outputs have isolated converters |
0.34 mm² (22 AWG) |
200 m (650 ft) |
Solid-state relay (SSR) outputs |
According to local wiring rules f |
According to local wiring rules f |