earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: RP-IO
Functionalities: Hardware
Product version: 2023, 2024, 7.0, 7.1
2/22/2024

RP-IO Modules

The RP-IO module provides I/O expansion to your HVAC application over BACnet MS/TP. The I/O module can share its I/O resources across applications running in automation servers, RP and MP controllers, or third-party systems. With the support of local alarms and local trend logs, the I/O module avoids unnecessary traffic over the network while being able to log important information locally. The I/O module can be installed near facilities in the field, away from the automation server or the RP or MP controller.

The RP-IO module is an I/O module that allows for flexible control solutions due to the versatile mix of universal inputs/outputs and solid-state relay (SSR) outputs.

When RP-IO modules are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

 
action_zoom_plus_stroke RP-IO module (RP-IO-16E-M-24V)
Figure: RP-IO module (RP-IO-16E-M-24V)

RP-IO Models

The RP-IO module is available in two models that only support BACnet MS/TP communication. These two models offer two different combinations (sets) of the number and types of I/O points. Both models support 24 VAC/VDC input power.

For more information, see RP-IO Models .

RP-IO Onboard I/O

The RP-IO module models provide 12 or 16 I/O points, consisting of two different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.

For more information, see RP-IO Onboard I/O .

RP-IO Module Built-in Power Supply

The RP-IO module has a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power.

For more information, see RP-IO Module Built-in Power Supply .

Memory in RP and MP Controllers and I/O Modules

RP and MP controllers and I/O modules are devices that have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

For more information, see Memory in RP and MP Controllers and I/O Modules .

RP-IO Module Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the RP-IO module complies with the BACnet open standard, one of the most popular standards for buildings.

For more information, see RP-IO Module Supported Building Standards .

RP-IO Module Communication Port

The RP-IO module provides the following communication port:

  • One RS-485 port with terminal block

For more information, see RP-IO Module Communication Port .

RP-IO BACnet MS/TP Support

The RP-IO modules are designed for connection to a BACnet MS/TP (RS-485) network and can only communicate with automation servers using the BACnet MS/TP protocol.

For more information, see RP-IO BACnet MS/TP Support .

MS/TP DIP Switches

You must configure the DIP switches as part of the commissioning process for the RP and MP controllers and RP-IO modules that only support MS/TP communications.

For more information, see MS/TP DIP Switches .

RP-IO Screw Terminals

The RP-IO module has fixed screw terminals for the power input, SSR outputs, and universal inputs/outputs and a removable screw terminal block for connection to the BACnet MS/TP (RS-485) network.

For more information, see RP-IO Screw Terminals .

RP-IO Module LED

There is one LED on the front panel of the RP-IO module.

For more information, see RP-IO Module LED .

RP-IO Module Reset Modes

You can reset and restart the RP-IO module in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

For more information, see IP-IO and RP-IO Module Reset Modes .

RP-IO Module Device Installation

The RP-IO module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

For more information, see RP-IO Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, RP and MP controllers, IP-IO and RP-IO modules, RP controller expansion modules, and Operator Display.

For more information, see Wiring .

RP-IO Module Firmware Management

Using WorkStation, you can update the firmware of multiple RP-IO IO modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

For more information, see RP-IO Module Firmware Management .

RP-IO Module Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP-IO modules.

For more information, see RP-IO Module Regulatory Compliance and Approvals .

Specifications

AC input
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
7 VA
Power input protection
MOV suppression and internal fuse
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
3 W
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Plenum rating
UL 2043
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-IO-12A-M-24V
0.336 kg (0.741 lb)
Weight, RP-IO-16E-M-24V
0.334 kg (0.736 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Terminal blocks
Power and I/O: Fixed
  
BACnet MS/TP communications: Removable
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, optional covers
0.070 kg (0.154 lb)
Communication ports
RS-485 port
RS-485 (3-pole screw terminal block)
  
Transient voltage suppressors on communication signals
RS-485 transceiver characteristics
All device models
Transceiver type
Failsafe
  
Non-isolated
External biasing
None required
Total Unit Load (UL) per device
Maximum 0.5 UL
Communications
BACnet
BACnet MS/TP, maximum bus length: 1200 m (4000 ft), maximum baud rate: 76800
  
BTL B-ASC (BACnet Application Specific Controller) a
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 single-core
Internal SRAM
6 MB
NOR flash memory
32 MB
Memory backup
128 kB a , FRAM, non-volatile

Internal Configuration

 
action_zoom_plus_stroke RP-IO module internal configuration
Figure: RP-IO module internal configuration
  • Hardware Overview
  • RP-IO Models
  • RP-IO Onboard I/O
  • RP-IO Module Built-in Power Supply
  • Memory in RP and MP Controllers and I/O Modules
  • RP-IO Module Supported Building Standards
  • RP-IO Module Communication Port
  • RP-IO BACnet MS/TP Support
  • MS/TP DIP Switches
  • RP-IO Screw Terminals
  • RP-IO Module LED
  • IP-IO and RP-IO Module Reset Modes
  • RP-IO Module Device Installation
  • Wiring
  • RP-IO Module Firmware Management
  • RP-IO Module Regulatory Compliance and Approvals