Produkte: RP-IO
Funktionen: Hardware
Produktversion: 2023, 2024, 7.0
02.05.2023

RP-IO BACnet MS/TP Support

The RP-IO modules are designed for connection to a BACnet MS/TP (RS-485) network and can only communicate with automation servers using the BACnet MS/TP protocol.

The RP-IO modules have an RS-485 port with a 3-pole removable screw terminal block that is used for connection to the BACnet MS/TP (RS-485) network and MS/TP communication with the automation server (AS-P or AS-B). Connecting to an IP network is not supported as the RP-IO modules do not have Ethernet ports. Für weitere Informationen siehe RP-IO Module Communication Port .

You need to configure a unique MS/TP address for the device during installation using the address DIP switches on the device. Für weitere Informationen siehe MS/TP DIP Switches .

As part of the commissioning process for the device, you also need to configure the baud rate for the automation server BACnet MS/TP (RS-485) bus. Für weitere Informationen siehe MS/TP Communications Baud Rate .

 
action_zoom_plus_stroke Location of the RS-485 screw terminal block on the RP-IO modules
Abbildung: Location of the RS-485 screw terminal block on the RP-IO modules
Automation Server BACnet MS/TP (RS-485) Network with b3 BACnet devices

The RP-IO modules can be mixed with b3 BACnet devices on the BACnet MS/TP (RS-485) network. Für weitere Informationen siehe RS-485 Communications .

Hinweis

The RP-IO modules are not isolated and connection of the I/O modules to a network comprised of isolated RS-485 interfaces is not recommended. The RS-485 application guidelines provide additional details. Für weitere Informationen siehe RS-485 Communications .

A mix of up to 50 devices per RS-485 Com port can be connected to an automation server.

 
action_zoom_plus_stroke Examples of automation server BACnet MS/TP (RS-485) networks mixing RP-IO modules with b3 BACnet devices
Abbildung: Examples of automation server BACnet MS/TP (RS-485) networks mixing RP-IO modules with b3 BACnet devices