The RP-C-16C-F-230V controller model offers selectable power supply to the solid-state relay (SSR) outputs. An external power supply (24 VAC / VDC, 8 A) or the internal transformer (24 VAC, 19 VA) can be selected via jumpers.
The internal 24 VAC transformer is rated 19 VA. When the total load connected to the SSR outputs (DOs) exceeds 19 VA, the internal transformer can be supplemented with an external AC or DC power supply to supply one or more of the DO groups. The external power supply is connected to the EXT Input connector on the controller. The EXT Input is marked 24 VAC / VDC, 8 A. 有关更多信息,请参阅 Solid-state Relay (SSR) Outputs with Power Distribution on RP-C-16C-F-230V .
The SSR outputs (DOs) are divided into four different DO groups, and for each DO group there is a 3-pin header accessible from the front of the controller.
DO Group |
SSR Outputs (DOs) |
“A” |
DO1, DO2, DO3, DO4 |
“B” |
DO5, DO6, DO7, DO8 |
“C” |
DO9, DO10 |
“D” |
DO11, DO12 |
The 3-pin headers have an upper and a lower position. You select the power source to a DO group by placing a 2-position jumper in either the upper or lower position on the pin header for that group.
Pin Header Position |
Jumper Placement |
Power Source Selected |
Upper |
![]() |
External power supply (24 VAC/VDC) |
Lower |
![]() |
Internal transformer (24 VAC, 19 VA) |
Any of the DO groups can be connected to and powered from either an external power supply or the internal transformer.
The controller is delivered with the jumpers placed in the lower position on the pin headers. This means that the internal transformer is preselected as power supply to all SSR outputs (DOs).
Spare jumpers can be ordered separately using the Samtec part number SNT-100-BK-G-H.