This section provides recommendations on wire sizes and lengths for the MP-C controllers.
有关更多信息,请参阅 MP-C Models .
The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.
Terminals |
Minimum Cross-sectional Area |
Maximum Cable Length |
Power input terminals (1, 2) |
0.75 mm² (18 AWG) a |
6 m (20 ft) to local 24 VAC transformer |
Earth ground terminal (3) |
0.75 mm² (18 AWG) a |
Protective earth ground connection on or within the controller panel |
RS-485 terminals (4, 5, 6) b |
有关更多信息,请参阅 RS-485 Communications . |
有关更多信息,请参阅 RS-485 Communications . |
Universal inputs/outputs as digital c inputs |
0.34 mm² (22 AWG) |
200 m (650 ft) |
Universal inputs/outputs as analog d inputs |
0.34 mm² (22 AWG) |
100 m (330 ft) |
Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) |
0.75 mm² (18 AWG) |
75 m (250 ft) |
Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F) |
1.5 mm² (15 AWG) |
150 m (500 ft) |
Universal inputs/outputs as temperature (thermistor) inputs, up to 150 °C (302 °F) |
1.5 mm² (15 AWG) |
75 m (250 ft) |
Universal inputs/outputs, for actuators and transmitters powered from the same transformer as the controller |
0.75 mm² (18 AWG) |
20 m (65 ft) |
Universal inputs/outputs, for actuators and transmitters powered from their own transformer (external or internal) |
0.34 mm² (22 AWG) |
200 m (650 ft) |
Universal inputs/outputs as voltage or current outputs, for actuators powered from their own transformer (external or internal) or when the outputs have isolated converters |
0.34 mm² (22 AWG) |
200 m (650 ft) |
Relay outputs |
According to local wiring rules e |
According to local wiring rules e |
High power relay output |
According to local wiring rules e |
According to local wiring rules e |
Triac outputs |
According to local wiring rules e |
According to local wiring rules e |