earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos AO-8, AO-V-8, AS-P-3, DI-16, DO-FA-12, DO-FC-8, PS-24 V, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-4 v2, UI-8/AO-V-4, UI-8/AO-V-4 v2, UI-8/DO-FC-4, UI-8/DO-FC-4 v2
Funcionalidades: Hardware
Versión del producto: 7.1
05/12/2025

AS-P-3 Servers

AS-P-3 is a one-piece automation server and power supply unit, without terminal bases, for DIN-rail mounting. AS-P-3 is the successor to AS-P. Compared to AS-P, it provides an additional 1 Gbit/s Ethernet port, two fully configurable 10/100 Mbit/s Ethernet ports, an additional configurable RS-485 port, two USB 3.0 host ports, and significantly more memory and power. When replacing an AS-P server, the AS-P-3 server can replace both the AS-P server and the PS-24V module, and it matches the combined size of these two devices.

The automation server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier EcoStruxure BMS server within the EcoStruxure BMS. The automation server controls and supervises equipment, typically HVAC equipment. The AS-P-3 server uses Central IO modules with connected field devices, such as sensors and actuators, to do that.

The AS-P-3 server communicates with and provides power to the Central IO modules through the I/O bus. The AS-P-3 server requires an input voltage of either 24 VAC ±20 % or 24 to 30 VDC.

The AS-P-3 server is installed with the Central IO modules on DIN rails in cabinets.

 
action_zoom_plus_stroke AS-P-3 server
Figura: AS-P-3 server

AS-P-3 Server Models

The AS-P-3 server comes in two models that differ only in the support for LonWorks communication and the number of ports available for RS-485 serial communication.

Model

LON TP/FT Ports

RS-485 Ports

AS-P-3

0

3

AS-P-L-3

1

2

The AS-P-3 and AS-P-L-3 models are hardware only. An AS-P-3 server software package needs to be purchased separately. For more information, see the SpaceLogic Automation Server V3 - Premium Specification Sheet.

AS-P-3 Server Built-in Power Supply

The AS-P-3 server has a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power.

Para obtener más información, consulte AS-P-3 Server Built-in Isolated Power Supply .

Memory in AS-P-3 Servers

An AS-P-3 server has two types of memory:

  • 2 GB LPDDR4 SDRAM (for program execution)

  • 32 GB eMMC memory (for storage)

Para obtener más información, consulte Memory in AS-P-3 Servers .

AS-P-3 Server Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. The AS-P-3 server can natively communicate with open standards such as BACnet (including BACnet/SC), Modbus, and LonWorks.

Para obtener más información, consulte AS-P-3 Server Supported Building Standards .

AS-P-3 Server Communication Ports

An AS-P-3 server has the following communication ports:

  • 1 Ethernet 10/100/1000 megabit port

  • 2 Ethernet 10/100 megabit ports

  • 3 RS-485 ports (only 2 ports on AS-P-L-3 model)

  • 1 LonWorks TP/FT port (only available on AS-P-L-3 model)

  • 2 USB 3.0 host ports (only one of the ports at a time can use USB 3.0)

  • 1 USB 3.0 device port

  • 1 I/O bus port

Para obtener más información, consulte AS-P-3 Server Communication Ports .

AS-P-3 Server Screw Terminals

The AS-P-3 server models have removable (pluggable) screw terminal blocks on the top of the device. The terminal blocks are easy to install and remove from the device. The terminal blocks are delivered with the device.

Para obtener más información, consulte AS-P-3 Server Screw Terminals .

AS-P-3 Server LEDs

There are several LEDs on the front panel of an AS-P-3 server.

Para obtener más información, consulte AS-P-3 Server LEDs .

Reset Functions

There are four different types of reset for the automation servers: warm start, cold start, reset, and reset to DFU mode. Depending on the type of reset, the automation server can be reset using the reset button or a command from WorkStation.

Para obtener más información, consulte Automation Server Reset Functions .

AS-P-3 Server Device Installation

The AS-P-3 servers are designed for installation on DIN rails in a cabinet.

Para obtener más información, consulte AS-P-3 Server Device Installation .

I/O Bus

The I/O bus is a common bus that delivers power, address information, and communication to all devices connected to the bus. The term I/O bus also denotes the chain of devices that are connected together.

Para obtener más información, consulte I/O Bus .

Automatic Device Addressing on the I/O Bus

Each device on the I/O bus can detect its order in the chain of connected devices and assigns itself an address accordingly. This auto-addressing feature is provided by the terminal base backplane of the Central IO modules, the AS-P server, and the PS-24V power supply. The AS-P-3 server differs in that it is a one-piece device, without a terminal base, but the addressing works the same as for the two-piece devices.

Para obtener más información, consulte Automatic Device Addressing on the I/O Bus .

Power Budget for AS-P-3 Servers

Use the power budget to calculate the maximum number of Central IO modules that the AS-P-3 server can supply. If more I/O modules are used, PS-24V power supplies must be added to the I/O bus.

Para obtener más información, consulte Power Budget for AS-P-3 Servers .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, RP and MP controllers, IP-IO and RP-IO modules, RP controller expansion modules, and Operator Display.

Para obtener más información, consulte Wiring .

AS-P-3 Server Software

Before you engineer an AS-P-3 server, install the AS-P-3 server software on the server using Device Administrator. The software is not pre-loaded on the AS-P-3 servers.

Para obtener más información, consulte Installing Automation Server Software .

Automation Server Replacement Using Restore

Backup and Restore helps assure that automation server data can be restored to a replacement automation server in the event of detected failure, or to the same automation server in the event of data loss. As a precaution, you back up your automation servers regularly so that you can use the most current backup to restore the automation server data to a replacement automation server. You also configure the new automation server to match the name and the network settings of the replaced automation server so the system can identify this automation server when online.

Para obtener más información, consulte Field Server Replacement Using Restore .

Replace Automation Server AS-P or AS with Automation Server AS-P-3

You can replace an AS-P server or Automation Server (AS Classic) with an AS-P-3 server using the Convert backup set server type feature in Device Administrator. The replacement process for an AS-P server and Automation Server (AS Classic) follows the same steps.

Para obtener más información, consulte Replace Automation Server AS-P or AS (Classic) with Automation Server AS-P-3 Workflow .

AS-P-3 Server Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the AS-P-3 servers.

Para obtener más información, consulte AS-P-3 Server Regulatory Compliance and Approvals .

Especificaciones

AC input
Type
Isolated Class 2 input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum current
2.5 A rms
Recommended transformer rating
60 VA or higher
Power input protection
MOV suppression and internal fuse
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
40 W
DC output
Voltage
24 VDC
Accuracy
+/-1 VDC
Maximum power
20 W
Environment
AS-P-3
Ambient temperature, operating
0 to 55 °C (32 to 131 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
AS-P-L-3
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 114 H x 64 D mm (7.1 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, including terminal blocks
0.571 kg (1.26 lb)
Weight, excluding terminal blocks
0.550 kg (1.21 lb)
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
AS-P-3
Ethernet
Single 10/100/1000BASE-TX (RJ45), IEEE 802.3 compliant
  
Dual 10/100BASE-TX (RJ45), IEEE 802.3 compliant
USB Device
1 USB 3.0 device port (type-C)
USB Host
2 USB host ports (type-A), USB 3.0 or 2.0
  
USB 3.0: 5 VDC, 0.9 A from either port 1 or 2
  
USB 2.0: 5 VDC, 0.5 A from both port 1 and 2
RS-485
Triple 2-wire ports, bias 5.0 VDC
AS-P-L-3
Ethernet
Single 10/100/1000BASE-TX (RJ45), IEEE 802.3 compliant
  
Dual 10/100BASE-TX (RJ45), IEEE 802.3 compliant
USB Device
1 USB 3.0 device port (type-C)
USB Host
2 USB host ports (type-A), USB 3.0 or 2.0
  
USB 3.0: 5 VDC, 0.9 A from either port 1 or 2
  
USB 2.0: 5 VDC, 0.5 A from both port 1 and 2
RS-485
Dual 2-wire ports, bias 5.0 VDC
LonWorks a
TP/FT-10
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
BACnet profile
BACnet Building Controller (B-BC), BACnet Secure Connect Hub (B-SCHUB), AMEV AS-B
BACnet certification
BTL Certification (BTL Listing a , WSPCert)
OPC UA Client
Profile group UACore 1.03
Core Client Facet, Base Client Behaviour Facet a , AddressSpace Lookup Client Facet, Attribute Read Client Facet a , Attribute Write Client Facet a , DataChange Subscriber Client Facet a , Method Client Facet, UA-TCP UA-SC UA-Binary, SecurityPolicy – Basic256, SecurityPolicy – Basic256Sha256, User Token – Anonymous Facet, User Token – User Name Password Client Facet, DataAccess Client Facet, Base Event Processing Client Facet, Historical Access Client Facet, A & C Alarm Client Facet, and A & C Address Space Instance Client Facet.
OPC UA Server
Profile group UACore 1.04
Core 2022 Server Facet a , User Token – User Name Password Server Facet, SecurityPolicy – None, SecurityPolicy [B] – Basic256Sha256, UA-TCP UA-SC UA-Binary.
Modbus
Modbus TCP, client and server
  
Modbus RTU and ASCII, RS-485, client and server
ION
ION TCP, port configurable, default 7700
MQTT
MQTT over TLS, port configurable, default 8883
  
MQTT over TCP, port configurable, default 1883
  
MQTT over WebSocket Secure (WSS), port configurable, default 443
  
MQTT over WebSocket (WS), port configurable, default 80
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.3, 1.2, 1.1 a , and 1.0 a , port configurable default 443
WSS a
Encrypted supporting TLS 1.3, port configurable
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
LNS
LNS version
OpenLNS
  
Installed on WorkStation PC
LonMark
Resource files version
14.00
CPU
Frequency
2 GHz
Type
ARM Cortex-A72 dual-core
LPDDR4
2 GB
eMMC memory
32 GB
Memory backup
Yes, battery-free, no maintenance

Internal Configuration

All serial communication ports of the AS-P-3 server module refer to signal ground as shown in the figure below.

 
action_zoom_plus_stroke  AS-P-3 model internal configuration
Figura: AS-P-3 model internal configuration
Aviso

The AS-P-3 model does not have LonWorks (LON) communication ports.

 
action_zoom_plus_stroke AS-P-L-3 model internal configuration
Figura: AS-P-L-3 model internal configuration

An AS-P-3 automation server is the leftmost device in the I/O bus of chain devices, which consist of Central IO modules and, if needed, also PS-24V power supplies. An AS-P-3 server has address 2 on the I/O bus. The I/O bus provides the Central IO modules with power and an address. The address on the I/O bus is increased by one for each connected device. The I/O bus also enables RS-485 serial communication between the Central IO modules and the automation server.

  • Hardware Overview
  • SpaceLogic Automation Server V3 - Premium
  • AS-P-3 Server Built-in Isolated Power Supply
  • Memory in AS-P-3 Servers
  • AS-P-3 Server Supported Building Standards
  • AS-P-3 Server Communication Ports
  • AS-P-3 Server Screw Terminals
  • AS-P-3 Server LEDs
  • Automation Server Reset Functions
  • AS-P-3 Server Device Installation
  • Power Budget for AS-P-3 Servers
  • I/O Bus
  • Automatic Device Addressing on the I/O Bus
  • Wiring
  • Installing Automation Server Software
  • Field Server Replacement Using Restore
  • Replace Automation Server AS-P or AS (Classic) with Automation Server AS-P-3 Workflow
  • AS-P-3 Server Regulatory Compliance and Approvals