earth_america
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Концепт

Концепт


Продукты: AS-P-3
Функции: Аппаратное обеспечение
Версия продукта: 7.0
22.09.2025

AS-P-3 Server Device Installation

The AS-P-3 servers are designed for installation on DIN rails in a cabinet.

Consider a simple example:

 
action_zoom_plus_stroke SpaceLogic AS-P-3 server and Central IO modules v2
Рисунок: SpaceLogic AS-P-3 server and Central IO modules v2

Installation orientation restrictions

Примечание

REDUCED DEVICE LIFE SPAN

Follow the installation orientation restrictions that apply to the device.

Failure to follow these instructions can result in reduced life span of the device.

The AS-P-3 server must be installed horizontally, with the device label text in the upright position reading left to right. See “a” in the following figure. Any other installation orientations (“b”, “c”, “d”, “e”, and “f” in the figure) may exceed the automation server's thermal specifications, which can reduce the life span of the device.

 
action_zoom_plus_stroke Installation orientation restrictions
Рисунок: Installation orientation restrictions

Installation on a DIN rail

Примечание

REDUCED DEVICE LIFE SPAN

Install the device on a horizontal DIN rail to provide sufficient cooling air flow through the device.

Failure to follow these instructions can result in reduced life span of the device.

A DIN rail is a common and convenient technique for installing an automation server along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the automation server rail and adjacent rails or other panel-mounted devices.

The AS-P-3 server must be installed on a horizontal DIN rail (going from left to right), with the device label text in the upright position reading left to right.

Installing the device on a horizontal DIN rail provides sufficient cooling air flow through the device. Installing the device on a vertical DIN rail can reduce the life span of the device.

 
action_zoom_plus_stroke  AS-P-3 server installed on a horizontal DIN rail
Рисунок: AS-P-3 server installed on a horizontal DIN rail
DIN rail end clip

To prevent the modules from sliding sideways on the DIN rail, fix an end clamp for DIN 35 (part number SXWDINEND10001) tightly against the rightmost device on the rail. The end clamp is easily removed if you bend the snap lock open with a screwdriver.

 
action_zoom_plus_stroke End clamp for DIN 35 fixed across the DIN rail
Рисунок: End clamp for DIN 35 fixed across the DIN rail

Installation in a cabinet

Install the AS-P-3 servers horizontally in the cabinet with ample space between the DIN rails and devices for sufficient cooling air flow through the devices.

 
action_zoom_plus_stroke  AS-P-3 servers with connected Central IO modules installed on horizontal DIN rails in a cabinet
Рисунок: AS-P-3 servers with connected Central IO modules installed on horizontal DIN rails in a cabinet

Screw terminals

Примечание

EQUIPMENT DAMAGE

  • Do not connect 230 VAC or 110 VAC to any terminal.

  • Install only a wired terminal block that matches the markings of the terminals on the device.

  • Use only terminal blocks delivered with the device or ordered from Schneider Electric using the part number SXWASPCON10002.

Failure to follow these instructions can result in equipment damage.

The AS-P-3 server models have removable (pluggable) screw terminal blocks on the top of the device. The terminal blocks are easy to install and remove from the device. The terminal blocks are delivered with the device.

Spare terminal blocks can be ordered separately using the part number SXWASPCON10002.

Install only a wired terminal block that matches the labeling of the terminals on the device. A mismatch can damage the electronics in the device. If the labels on the wires do not indicate the intended terminals, consult the control panel documentation to determine the intended terminals.

Connection of the next device on the I/O bus

The next device (I/O module terminal base) on the I/O bus is connected to the AS-P-3 server by sliding the two devices together using their built-in I/O bus connectors.

 
action_zoom_plus_stroke ​​Connection of the next device on the I/O bus
Рисунок: ​​Connection of the next device on the I/O bus
S-cables

The chain of devices can be split on multiple DIN rails (rows) by using an extension cord called S-cable. Maximum five S-cables are allowed per system. The S-cable connects the last (rightmost) device on one DIN rail with the first (leftmost) device on the next DIN rail.

The complete chain of devices must remain within one cabinet for EMC reasons. When the I/O bus size or quantity of I/O modules exceeds the capacity of a single cabinet, you can extend the I/O bus using an S-cable to a second, adjacent cabinet. Both cabinets must be securely fastened together and electrically connected to function as a single unit. This ensures continuous electromagnetic compatibility (EMC) protection, equivalent to that of a single cabinet. Mechanical bonding involves securely fastening the cabinets together, while electrical bonding ensures a common grounding and shielding system, minimizing electromagnetic interference and maintaining signal integrity.

The following figure shows an example of how you can use an S-cable to connect devices that are installed on separate DIN rails in a cabinet. For sufficient cooling air flow through the devices, the DIN rails and the devices are installed horizontally in the cabinet.

 
action_zoom_plus_stroke Devices installed on separate, horizontal rails and connected using an S-cable
Рисунок: Devices installed on separate, horizontal rails and connected using an S-cable

The S-cable is available with right angle connectors and in 1.5 m (5 ft) and 0.75 m (2 ft 5 in) lengths. You can serially connect up to two S-cables to extend the length.

The following image shows the minimum space required for plugging/unplugging the S-cable from the device but also provides information on the minimum bend radius required to reduce the stress of the cable. The S-cable with straight connectors is a discontinued product, which can no longer be ordered from Schneider Electric.

 
action_zoom_plus_stroke S-cable connecting devices on separate rails
Рисунок: S-cable connecting devices on separate rails

Device order

The order in which the devices are installed in the chain (I/O bus) is important. When the automation server is an AS-P-3 server, the devices are installed on the I/O bus in the following order:

  • Position 1: Not used.

  • Position 2 (leftmost): AS-P-3 server (mandatory).

    The AS-P-3 server can supply power for loads up to 20 W. Более подробную информацию см. Power Budget for AS-P-3 Servers .

  • Position 3 to 32: Central IO modules and extra power supplies as needed based on power budget.

    One power supply can supply power for loads up to 30 W. Более подробную информацию см. Power Budget .

Примечание

The following restrictions apply to the I/O bus:

  • Maximum one automation server per I/O bus

  • Maximum 31 devices in total per I/O bus

Примечание

Position 1 is reserved for a power supply, which is used only when the automation server in position 2 is an AS-P server, but not when it is an AS-P-3 server.

Примечание

The AS-P-3 server has the address 2 on the I/O bus. The next device gets the address 3, and so on, up to 32.

The rules are summarized in the following illustration.

 
action_zoom_plus_stroke Order of devices on the I/O bus
Рисунок: Order of devices on the I/O bus
  • Hardware Overview
  • AS-P-3 Servers
  • Installing an AS-P-3 Server on a DIN Rail
  • Connecting a Central IO Module Terminal Base to an AS-P-3 Server
  • Installing a Terminal Block on an AS-P-3 Server
  • Wiring a Terminal Block on an AS-P-3 Server
  • Powering Up an AS-P-3 Server
  • Power Budget for AS-P-3 Servers
  • Power Budget