Wire Sizes and Lengths for the Power Input and Power Output of the RP Controller Expansion Modules
This section provides recommendations on wires sizes and lengths for the power input and power output (power distribution) of the RP controller expansion modules.
The recommendations apply to the following RP controller expansion modules:
Power input: All models (supporting 230 VAC or 100-277 VAC).
Power output: Models with power distribution: RP-C-EXT-DALI-M-PD, RP-C-EXT-0-10V-4-PD, RP-C-EXT-BL-4-HV-PD, RP-C-EXT-BL-SMI-4-HV-PD, and RP-C-EXT-REL-4.
The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.
Table: Wire Sizes and Lengths for the Power Input and Power Output of the RP Controller Expansion Modules
Terminals
|
Minimum Cross-sectional Area
|
Maximum Cable Length
|
Power input terminals (N, PE, L)
|
0.75 mm² (18 AWG)
or larger according to local wiring rules
|
According to local wiring rules
|
Power output
terminals (N, PE, L)
|
0.75 mm² (18 AWG)
a
or larger according to local wiring rules
|
According to local wiring rules
|
I/O Wiring
Wire Sizes and Lengths
RP-C Controllers
DALI Inputs/Outputs with Power Distribution
DALI Inputs/Outputs without Power Distribution
0-10V Light Outputs with Power Distribution
0-10V Light Outputs without Power Distribution
High-Voltage Blind Outputs
Low-Voltage Blind Outputs
SMI Blind Outputs
SMI LoVo Blind Outputs
Relay Outputs on RP-C-EXT-REL-4
Wire Sizes and Lengths for the Digital Inputs of the RP Controller Expansion Modules
Wire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules
Wire Sizes and Lengths for the SMI Interface of the RP Controller Expansion SMI Blind Modules
Wire Sizes and Lengths for the Low-Voltage (24 VDC) Blind Outputs of the RP Controller Expansion Blind Modules
Wire Sizes and Lengths for the 0-10V Light Outputs of the RP Controller Expansion Light Modules
Wiring