The AO-V-8 I/O module is an analog output, 8-channel I/O module.
Module names with an -H indicate the presence of Hand-Off-Auto override switches.
The override switches on Central IO modules with manufacturing date earlier than 2021-W26 must be disabled to remove the risk of an improper output. 有关更多信息,请参阅 Important Information on Central IO Modules with Manufacturing Date Earlier Than 2021-W26 .
The front panel shows the module status LED, override switches, and adjustable potentiometers.
The analog outputs of the AO-V-8 and AO-V-8-H I/O modules are designed to be used for voltage outputs.
R OUT is approximately equal to 10 ohm.
V OUT range is 0 to 10 VDC.
R LOAD minimum is 5 kohm.
The I/O bus in the terminal base provides the I/O module with power and an address.
The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the I/O module and the SmartX server.
Output channels
|
8
|
DC input supply power
|
0.7 W
|
DC input supply voltage
|
24 VDC
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Maximum humidity
|
95 % RH non-condensing
|
Material | |
Plastic flame rating
|
UL94-5VB
|
Enclosure
|
PC/ABS
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions including terminal base
|
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
|
|
|
Weight including terminal base
|
0.279 kg (0.61 lb)
|
Weight excluding terminal base
|
0.156 kg (0.34 lb)
|
Terminal base
|
TB-IO-W1
|
Analog outputs, AO | |
|
|
Voltage | |
Range
|
0 to 10 VDC
|
Accuracy
|
+/-100 mV
|
Resolution
|
42 mV
|
Minimum load resistance
|
5 kohm
|
Load range
|
-1 to +2 mA
|
Reliability check
|
Yes
|