Products: AO-8, AO-V-8, DI-16, DO-FA-12, DO-FC-8, AS-P, PS-24V, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Functionalities: Hardware
Product version: 3.2, 3.3, 2022, 2023, 2024
10/15/2020

Connecting Terminal Bases

You connect terminal bases together to provide continuity of the power supply and the address bus.

Show More
action_close

The devices are designed mainly for installing on DIN rails in a cabinet.

Consider a simple example:

 
action_zoom_plus_stroke ​System ex. 1. A Power supply, a SmartX server, and two I/O modules
Figure: ​System ex. 1. A Power supply, a SmartX server, and two I/O modules

Each device consists of two parts:

  • Terminal base

  • Electronics module

 
action_zoom_plus_stroke ​A hardware device: the electronics module and the terminal base
Figure: ​A hardware device: the electronics module and the terminal base

A separate terminal base means the terminal base can be installed and wired before the electronics module with the application program and data is supplied.

The terminal base is usually installed on a DIN rail, but it can also be mounted directly on the wall. The electronics module is easily plugged in to the terminal base and firmly locked by pushing the handles in place.

Replacing an electronics module is done in seconds because no terminal wiring is affected.

DIN Rail Installation

Install the terminal bases on a horizontal DIN rail.

 
action_zoom_plus_stroke Terminal base installed on a horizontal DIN rail 
Figure: Terminal base installed on a horizontal DIN rail 

A DIN rail is a common and convenient technique for installing a SmartX device along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the SmartX device rail and adjacent rails or other panel-mounted devices.

Notice
  • For SmartX AS-P servers: Always install the terminal base on a horizontal DIN rail. This position is required to provide sufficient cooling air flow through the electronics module. Installation on a vertical DIN rail can significantly reduce the life span of the module.

  • For I/O modules and PS-24V power supply: Install the terminal base on a horizontal DIN rail. This position provides proper cooling air flow through the electronics module.

 
action_zoom_plus_stroke

The terminal bases are connected to each other by sliding the terminal bases together using the built-in connectors.

To ensure that the correct electronics module is used with the correct terminal base, you must always check that the warning label on the terminal base backplane indicates which module type is to be connected. Write the intended module type, if it is not already printed, on the label.

 
action_zoom_plus_stroke ​​Terminal base with label for intended module type
Figure: ​​Terminal base with label for intended module type

Install only the module type that is indicated on the label on the terminal base backplane. A mismatch can cause electric shock and damage the electronics module.

Warning Warning

HAZARD OF ELECTRIC SHOCK OR EQUIPMENT DAMAGE

Install only the module type that is indicated on the label on the terminal base backplane.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

If the label does not indicate the intended module type, consult the control panel documentation to determine the intended module type.

To prevent the modules from sliding sideways on the DIN rail, fix an end clamp for DIN 35 (part number SXWDINEND10001) tightly against the rightmost device on the rail. The end clamp is easily removed if you bend the snap lock open with a screwdriver.

 
action_zoom_plus_stroke ​End clamp for DIN 35 fixed across the DIN rail
Figure: ​End clamp for DIN 35 fixed across the DIN rail

The chain of devices can be split on multiple DIN rails (rows) by using an extension cord called S-cable. Maximum five S-cables are allowed per system. The S-cable connects the last (rightmost) device on one DIN rail with the first (leftmost) device on the next DIN rail. The complete chain of devices must remain within one cabinet for EMC reasons.

The following figure shows an example of how you can use an S-cable to connect devices that are installed on separate DIN rails in a cabinet. For sufficient cooling air flow through the devices, the DIN rails and the devices are installed horizontally in the cabinet.

 
action_zoom_plus_stroke Devices installed on separate, horizontal rails and connected using an S-cable
Figure: Devices installed on separate, horizontal rails and connected using an S-cable

The S-cable is available with right angle connectors and in 1.5 m (5 ft) and 0.75 m (2 ft 5 in) lengths. You can serially connect up to two S-cables to extend the length.

The following image shows the minimum space required for plugging/unplugging the S-cable from the device but also provides information on the minimum bend radius required to reduce the stress of the cable. The S-cable with straight connectors is a discontinued product, which can no longer be ordered from Schneider Electric.

 
action_zoom_plus_stroke S-cable connecting devices on separate rails
Figure: S-cable connecting devices on separate rails

Device Order

The order in which the devices are installed in the chain (I/O bus) is important. The devices should be installed in the following order:

  • Position 1 (leftmost): Power supply (mandatory)

  • Position 2: SmartX AS-P server (mandatory)

  • Position 3 to 32: I/O modules and extra power supplies as needed based on power budget. One power supply can supply power for loads up to 30 W. For more information, see Power Budget .

Note:

There is a limit of one SmartX server per I/O bus.

The rules are summarized in the following illustration.

 
action_zoom_plus_stroke Order of devices on the I/O bus
Figure: Order of devices on the I/O bus

To connect terminal bases
  1. Ensure that each terminal base is clipped to the DIN-rail.

  2. Push each terminal base firmly against its neighbor to the left, ensuring that the power supply and address bus connector is properly mated.

     
    action_zoom_plus_stroke
  3. On the backplane label of each terminal base, write the type of module to be connected to that terminal base.

You can now wire the terminal base.

  • Device Installation