Creating a Change of State Alarm

You create a change of state alarm to trigger an alarm when a variable, such as a switch, is either true or false.

Mehr zeigen
action_close

The change of state alarm monitors the state changes of digital variables. You configure the alarm ​to trigger when the variable changes its state to true or to false.

 
action_zoom_plus_stroke Change of state alarm when the monitored variable goes true
Abbildung: Change of state alarm when the monitored variable goes true
 
action_zoom_plus_stroke Change of state alarm when the monitored variable goes false
Abbildung: Change of state alarm when the monitored variable goes false

For example, you set up a change of state alarm that monitors a ventilation fan. If the fan breaks or stops working, the alarm is triggered.

You can configure the change of state alarms using shunt variable and time delay. Für weitere Informationen siehe Alarm Functions .

To create a change of state alarm
  1. In WorkStation, in the System Tree pane, select the folder or SmartStruxure server where you want to create the alarm.

  2. On the File menu, point to New and then click Alarm .

  3. In the object type list, select Change of State Alarm .

     
    action_zoom_plus_stroke
  4. In the Name box, type a name for the alarm.

  5. In the Description box, type a description for the alarm.

  6. Click Next .

  7. Select the state of the monitored variable that triggers the alarm:

    • Click True to trigger the alarm when the monitored variable is equal to True .

    • Click False to trigger the alarm when the ​monitored variable is equal to False .

     
    action_zoom_plus_stroke
  8. In the Monitored variable box, ​enter the variable that the alarm monitors.

  9. In the Disable alarm box, select whether or not to create the alarm in disabled mode.

  10. Under Time Delay and Shunt Variables , in the Alarm delay box, enter the time delay.

  11. In the Reset delay box, enter the time delay.

  12. Select Invert to have the alarm enabled when the first shunt variable is active.

  13. In the Shunt variable 1 box, enter the binary variable that enables or disables the alarm.

  14. In the Operator list, select AND or OR to add logic between the first shunt variable and the second shunt variable.

  15. Select Invert to have the alarm enabled when the second shunt variable is active.

  16. In the Shunt variable 2 box, enter the binary variable that enables or disables the alarm.

     
    action_zoom_plus_stroke
  17. Click Next .

  18. ​In the Alarm message box, type the message to display when the monitored variable exceeds the alarm limit.

     
    action_zoom_plus_stroke
  19. ​In the Reset message box, type the message to display when the alarm is reset.

  20. In the Category box, enter a category for the alarm.

  21. In the Prefix for alarm source name box, type a prefix that is added to the beginning of the source name property of an alarm record.

  22. In the Alarm priority box, enter the priority for the alarm state.

  23. Select Same priority to let the Reset priority box inherit the value in the Alarm priority box.

  24. In the Reset priority box, enter the priority for the reset state.

  25. Select Auto hide to automatically hide the alarm in the Alarms pane or Alarm View.

  26. Select Flashing alert to make the alarm flash in the Alarms pane and Alarm Views when it is triggered.

  27. Select Audible alert to make the alarm sound when it is triggered.

     
    action_zoom_plus_stroke
  28. Select Disable state-change logging to prevent an alarm state change from creating an event.

  29. Click Next .

  30. Select the type of acknowledgement to use:

    • Click No when the alarm does not need to be acknowledged.

    • Click Single when the alarm needs to be acknowledged in the alarm state.

    • Click Extended when the alarm needs to be acknowledged in the alarm state and the reset state.

     
    action_zoom_plus_stroke
  31. In the Cause note group box, enter a cause note group that you want to connect to the alarm.

  32. In the Action note group box, enter an action note group that you want to connect to the alarm.

  33. In the Checklist box, enter a checklist that you want to connect to the alarm.

  34. Select When acknowledging an alarm: Comment to force the user to add a comment to the alarm before the alarm can be acknowledged.

  35. Select When acknowledging an alarm: Cause note to force the user to edit the connected cause note before the alarm can be acknowledged.

  36. Select When acknowledging an alarm: Action note to force the user to edit the connected action note before the alarm can be acknowledged.

  37. Select When acknowledging an alarm: Checklist to force the user to go through the connected checklist before the alarm can be acknowledged.

  38. Under Required User Actions , select the actions for Comment , Cause note , and Action note ​to specify how the user should respond to the actions.

     
    action_zoom_plus_stroke
  39. Click Next .

  40. Click the Add attachment button

     
    action_zoom_plus_stroke
    to add an attachment.

     
    action_zoom_plus_stroke
  41. In the Select Object dialog box, select the object you want to attach to the alarm .

  42. Click Select .

  43. On the Attachment page, in the Display on alarm column, select the check box to automatically open the attachment when the alarm is triggered.

     
    action_zoom_plus_stroke
  44. Click Create .

  • Change of State Alarms
  • Create Change of State Alarm Wizard – Alarm Trigger Page
  • Change of State Alarm Properties – Basic Tab
  • Create Alarm Wizard – User Action Page
  • Create Alarm Wizard – Presentation Page
  • Create Alarm Wizard – Attachment Page
  • Alarm States