Creating an Analog Schedule

You create an analog schedule to control the state of an analog value.

Visa mer
action_close

An analog schedule controls a device that gauges the output in real numbers. The real numbers include positive or negative numbers, fractions, and decimal values.

For example, you can create an analog schedule to regulate a thermostat setpoint in an office area. To control the temperature from 08:00 to 17:00, you can set the value to 22 °C (72 °F) when the schedule is active and 16 °C (62 °F) when the schedule is inactive.

 
action_zoom_plus_stroke Analog Schedule
Figur: Analog Schedule

To create an analog schedule
  1. In WorkStation, in the System Tree pane, select the EcoStruxure BMS server or the folder.

  2. On the File menu, point to New and then click Schedule .

  3. In the Create Object wizard, in the object type list, select Analog Schedule .

  4. In the Name box, type a name for the schedule.

  5. In the Description box, type a description for the schedule.

  6. Click Create .

Now you can add events to the analog schedule and bind the schedule to an analog value.

  • Schedule Types
  • Analog Schedules
  • Binding an Analog Value to an Analog Schedule
  • Adding a Weekly Event
  • Adding a Calendar Exception Event
  • Adding a Date Exception Event
  • Adding a Date Range Exception Event
  • Adding a Calculated Exception Event