earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : DO-FA-12
Fonctionnalités : Matériel
Version produit : 3.3, 2022, 2023, 2024, 7.0
02/09/2025

DO-FA-12 and DO-FA-12-H Central IO Modules

arrow1_rotationDigital outputs arrow1_rotationSpécifications

These Central IO modules are digital output, Form A relay, 12-channel I/O modules. The Form A relays are designed for direct load applications for up to 2 A loads.

Déclaration

Module names with an -H indicate the presence of Hand-Off-Auto override switches.

Déclaration

The override switches on Central IO modules with manufacturing date earlier than 2021-W26 must be disabled to remove the risk of an improper output. Pour plus d'informations, voir Important Information on Central IO Modules with Manufacturing Date Earlier Than 2021-W26 .

The supported output types include the following:

  • Digital (Form A)

  • Tristate

Each channel has a dedicated two-color (red and green) status LED that provides local monitoring of the digital output. The front panel contains both the I/O channel and module status LEDs.

 
action_zoom_plus_stroke DO-FA-12-H Central IO module
Figure : DO-FA-12-H Central IO module

Digital outputs

The Form A digital outputs are normally open contacts with one common terminal (C) and one normally open terminal (NO). The terminals are isolated from signal ground.

 
action_zoom_plus_stroke Form A digital output internal configuration
Figure : Form A digital output internal configuration

The I/O bus in the terminal base provides the Central IO module with power and an address.

The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the Central IO module and the automation server.

Spécifications

Output channels
12
DC input supply power
1.8 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.317 kg (0.70 lb)
Weight excluding terminal base
0.194 kg (0.43 lb)
Terminal base
TB-IO-W1
Digital outputs
 
action_zoom_plus_stroke
Contact rating
250 VAC/30 VDC, 2 A, Pilot Duty (Power Factor 0.35)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Isolation contact to system ground
3000 VAC
Cycle life (Resistive load)
At least 100,000 cycles
Minimum pulse width
100 ms
LED polarity energized relay
On
LED polarity non-energized relay
Off
LED color
Green
  • Central IO Modules
  • Output Modules
  • Important Information on Central IO Modules with Manufacturing Date Earlier Than 2021-W26