earth_america
user_standard Anmelden
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Ratgeber

Ratgeber


Produkte: AS-C, AS-B, Enterprise Server, AS-P, WorkStation, Projekt Configuration Server, Project Configuration Tool
Funktionen: Trends
Produktversion: 1.8
13.10.2016

Editing the Interval of an Interval Trend Log

You edit the interval property of a trend log to increase or decrease the frequency of records.

Mehr zeigen
action_close

​The interval trend log collects data at a specific time interval. Each logged value is stored as a record in the trend log. Use this trend log when the logging interval is less than 1 hour.

You create interval trend logs using WorkStation or WebStation. In WorkStation, you configure the properties of the interval trend log to meet the specific needs of your site. 

For example, in the figure below, the interval trend log records a variable every minute. The records are printed in a trend chart. The interval trend log does not record the values between the intervals.

 
action_zoom_plus_stroke Interval trend log schematic.
Abbildung: Interval trend log schematic.

The interval of the interval trend log is aligned with the activation time of the trend. For example, if the activation time is 09:01:00 and the interval is 15 minutes, the trend will log at 09:16:00, 09:31:00, 09:46:00, and so on.

Interval Trend Log Delta

An interval trend log with delta can reduce the storage of similar records, and may not fill up the storage capacity as quickly as an interval trend log with no delta.

An interval trend log with delta checks the monitored value at each interval and records the new value if it differs from the previously recorded value by more than the delta. Delta is the difference between the current variable value and the last log value. To log a variable according to the time interval, use a delta of zero.

For example, in the figure below, the interval trend log records a variable every minute but only if the variable exceeds or falls below the delta of 3. The records are printed in a trend chart. Notice that the interval trend log with delta does not record the values between the intervals, or on intervals where the variable is within the delta.

Hinweis
  • To log a variable only according to the time interval, set Delta to zero.

 
action_zoom_plus_stroke Interval trend log with delta schematic.
Abbildung: Interval trend log with delta schematic.

If an interval trend log has a delta and a calculation method that uses periods, make sure the period contains the required amount of records to generate a correct calculation. If the value does not differ from the previously logged value by more than the delta within the period, then none or too few values are recorded for the calculation.

Hinweis
  • Adapt the period so it contains the required amount of records to generate a correct calculation.

  • If a calculation method is connected to an interval trend log with delta, make sure that the period and delta are adapted for the calculation.

To edit the interval of an interval trend log
  1. In WorkStation, in the System Tree pane, click the interval trend log whose interval you want to edit.

     
    action_zoom_plus_stroke
  2. In the Interval box, type the new value.

  3. Click the Save button

     
    action_zoom_plus_stroke
    .

  • Configuring an Interval Trend Log
  • Interval Trend Logs
  • Interval Trend Log Properties
  • Trend Log Activation
  • Log Record Storage
  • Trend Log Does Not Start Record Due to the Start Condition
  • Missing Trend Log Records