The implicit log is a change of value trend log which monitors the IO variable and records a new value if the variable exceeds the delta. Each log value is stored as a record in the trend log. The delta is automatically defined by the EcoStruxure Building Operation software depending on the measured unit of the device that is connected to the IO port.
Implicit records that have not been collected by the extended trend log will be lost on server restart.
The implicit log is not manually created as with the other trend logs in WorkStation.
The implicit trend log exists on all IO points. When a device is connected to an IO port, the implicit trend log is automatically configured and starts recording values.
Implicit records that have not been collected by the extended trend log will be lost on server restart.
Unit |
Delta |
Temp |
0.2 ºC (0.2 ºF) |
Voltage |
0.2 V |
Current |
0.3 mA |
Resistance |
200 Ω |
The implicit trend log stores approximately 500 records before old records are overwritten.