0
Benutzeroberfläche

Benutzeroberfläche


Produkte: AS-B, Enterprise Central, Enterprise Server, AS-P, Project Configuration Tool
Funktionen: Alarme
Produktversion: 3.2, 3.3, 2022
15.10.2020

Out of Reference Range Alarm Properties – Basic Tab

Use the Basic tab to view or edit the basic properties of an out of reference range alarm.

 
action_zoom_plus_stroke Basic tab
Abbildung: Basic tab

Tabelle: Basic Tab

Component

Description

Alarm state

​Displays the present state of the alarm. Für weitere Informationen siehe Alarm States .

Basic evaluation state

Displays False when the alarm is in its normal state.

Evaluation state

​Displays the present evaluation state of the alarm. For example, Upper limit alarm is displayed when the monitored value reaches the upper alarm limit.

Disabled cause

Displays the cause for the alarm being disabled:

  • Shunt variable means that the alarm has been disabled by a shunt variable

  • User means that the alarm has been disabled by the user

  • System means that the alarm has been disabled by the system

Monitored variable

​Enter the path to the variable that is monitored by the alarm.

Reference variable

​Enter the reference variable that is compared with the monitored variable.

Upper deviation limit

​Enter the highest value the monitored variable can increase to before the alarm is triggered.

Lower deviation limit

​Enter the lowest value the monitored variable can decrease to before the alarm is triggered.

Deadband

​Enter the range the monitored variable has to pass within the normal range before the alarm is reset.

Für weitere Informationen siehe Deadband .

Reset delay (s)

​Enter the time, in seconds, the alarm has to be within the reset criteria before the alarm state is changed from alarm to reset.

Für weitere Informationen siehe Time Delay .

Alarm delay (s)

​Enter the time, in seconds, the alarm has to be within the alarm criteria before the alarm is triggered.

Für weitere Informationen siehe Time Delay .

Shunt variable 1

​Enter the shunt variable that is used to enable or disable the alarm. Für weitere Informationen siehe Shunt Variables .

Invert shunt value 1

Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. Für weitere Informationen siehe Shunt Variables .

Shunt operator

Select AND or OR to add logic between the first and the second shunt variable. Für weitere Informationen siehe Shunt Variables .

Shunt variable 2

​Enter the second shunt variable that is used to enable or disable the alarm. Für weitere Informationen siehe Shunt Variables .

Invert shunt value 2

Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. Für weitere Informationen siehe Shunt Variables .

  • Out of Reference Range Alarms
  • Out of Reference Range Alarm Properties – Alarm Settings
  • References Tab
  • Alarm States
  • Deadband
  • Time Delay