Produits : PS-24V
Fonctionnalités : Matériel
Version produit : 2.0, 2.1, 3.0, 3.1
19/11/2020

PS-24V Power Supplies

arrow1_rotationElectronics Modules arrow1_rotationTerminal Bases arrow1_rotationPower Supply PS-24V LEDs arrow1_rotationPower Budget arrow1_rotationSpécifications arrow1_rotationInternal Configuration

PS-24V is the power supply for the SmartX AS-P servers, Automation Server, and I/O modules. The PS-24V power supply requires an input voltage of either 24 VAC +/–20 % or 24–30 VDC.

The PS-24V power supply is based on the patented two-piece design. Each PS-24V device consists of an electronics module and a terminal base.

PS-24V is usually installed on a DIN rail in a cabinet and provides power to the subsequent devices in the chain through the terminal base backplane. A PS-24V power supply consumes one address position, even though the address is not used.

A system may contain more than one PS-24V to supply the power needed, depending on the type and number of connected devices. A power budget table can be used for proper calculations. Pour plus d'informations, voir Power Budget .

The output voltage is 24 VDC supplied on the backplane, maximum 30 W. If the output is overloaded, the power is automatically shut down and the Status LED turns red. At an interval of a couple of seconds the power supply retries to switch on the power output. This is sometimes called ‘the hiccup mode’. Pour plus d'informations, voir Power Supply Overload .

The power supply has galvanic isolation between the primary (input power) and secondary (output power) side of the power supply.

 
action_zoom_plus_stroke Power supply PS-24V
Figure : Power supply PS-24V

Electronics Modules

The electronics module is the main component of SmartX devices that are based on the patented two-piece design. The electronics module is installed on a terminal base, which constitutes the second component of the device.

Pour plus d'informations, voir Electronics Modules .

Terminal Bases

The terminal bases are used for SmartX devices that are based on the patented two-piece design. The terminal base provides the I/O bus to the electronics module installed on the terminal base as well as to the SmartX device installed to the right (next terminal base in the chain).

Pour plus d'informations, voir Terminal Bases .

Power Supply PS-24V LEDs

There are two LEDs on the front panel of the PS-24V. The LEDs indicate status for input and output power.

Pour plus d'informations, voir Power Supply PS-24V LEDs .

Power Budget

Use the power budget to calculate the maximum number of devices that the power supply can supply. If more devices are used, additional power supplies must be added to the I/O bus.

Pour plus d'informations, voir Power Budget .

Spécifications

DC output
Voltage
24 VDC
Accuracy
+/-1 VDC
Maximum power
30 W
AC input
Nominal voltage
24 VAC
Operating voltage range
+/-20 %
Frequency
50/60 Hz
Maximum current
2.5 A rms
Recommended transformer rating
60 VA or higher
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
40 W
Terminals
 
action_zoom_plus_stroke
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.285 kg (0.63 lb)
Weight excluding terminal base
0.186 kg (0.41 lb)

Internal Configuration

The PS-24V power supply module does not connect to the address and communication busses in the terminal base. The AC/DC converter terminals L/+ and N/- are isolated from the circuits on the secondary side of the converter. You can wire these terminals without concern for polarity matching, but it is good practice to connect the positive supply voltage to L/+ and the negative supply voltage to N/- in order to prevent confusion.

 
action_zoom_plus_stroke PS-24V internal configuration
Figure : PS-24V internal configuration

The earth ground terminal (

 
action_zoom_plus_stroke
) on the PS-24V power supply is connected to signal ground, which is the same as the negative output from the power supply. The purpose of this connection is to comply with EMC directives.

  • Hardware Overview
  • Electronics Modules
  • Terminal Bases
  • Power Supply PS-24V LEDs
  • Power Budget
  • Power Supply Overload