Schedule Events

arrow1_rotationWeekly Events in WorkStation arrow1_rotationWeekly Events in WebStation arrow1_rotationException Events in WorkStation arrow1_rotationException Events in WebStation arrow1_rotationPriorities arrow1_rotationTime Zones

A schedule has two types of events: weekly events and exception events. Weekly events occur every week at specified times. Exception events occur when the schedule deviates from the weekly schedule, such as during holidays. Exception events override the weekly events when there is an overlap.

For each schedule except Xenta schedules, you can set a default value. The default value goes into effect after the exception events and weekly events are complete or relinquish control. For example, the weekly event for a fan ends at 17:00. The fan ran at a value of 3 (high) throughout the event. There are no scheduled events after the weekly event. Because you have assigned 0 as the default value, the fan adjusts to the default value and turns to 0 (off). The value remains at 0 until the next scheduled event.

Events occur in the following order of precedence:

  • Exception events

  • Weekly events

  • Default value

Xenta schedules do not have any default values.

Example:

The weekly event for a fan is set to '08:00 - 17:00'. An exception event is set to '17:00 - 20:00' for a specific date. The exception event overrides the weekly event so that the fan only runs from 17:00 to 20:00 on the specified date.

Xenta schedule events occur in the following order of precedence:

  • Exception events

  • Weekly events

Weekly Events in WorkStation

A weekly event occurs every week for an extended period of time on a regular basis. You can schedule more than one weekly event for each day of the week.

Pour plus d'informations, voir Weekly Events in WorkStation .

Weekly Events in WebStation

A weekly event occurs every week for an extended period of time on a regular basis. You can schedule more than one weekly event for each day of the week.

Pour plus d'informations, voir Événements hebdomadaires dans WebStation .

Exception Events in WorkStation

An exception event occurs instead of the scheduled weekly events for a single date, date range, calculated date, or calendar reference.

Pour plus d'informations, voir Exception Events in WorkStation .

Exception Events in WebStation

An exception event occurs instead of the scheduled weekly events for a single date, date range, calculated date, or calendar reference.

Pour plus d'informations, voir Événements exceptionnels dans WebStation .

Priorities

Priority is a number that corresponds to a preassigned level of importance. When used in schedules, priority numbers range from one to sixteen. One is the most important or highest priority and sixteen is the lowest priority.

Pour plus d'informations, voir Priorities .

Time Zones

When you create a schedule, the time zone of the EcoStruxure BMS server that contains the schedule determines the execution of the events. If the schedule is copied to an EcoStruxure BMS server in a different time zone, the specified dates and times relate to the new time zone.

Pour plus d'informations, voir Time Zones .