0
Specifications

Specifications


Products: DO-FC-8
Functionalities: Central IO , Engineering, Hardware, Smoke Control
Product version: 1.8, 1.9
9/4/2025

DO-FC-8 and DO-FC-8-H

arrow1_rotationIntroduction arrow1_rotationFunction arrow1_rotationSpecifications
 
action_zoom_plus_stroke I/O Modules DO-FC-8 and DO-FC-8-H
Figure: I/O Modules DO-FC-8 and DO-FC-8-H

Introduction

The DO-FC-8 and DO-FC-8-H are digital output 8 channel I/O modules.

The digital outputs support digital Form C point types. The Form C relays are designed for direct load applications.

Function

Modular and scalable system

The modules are part of a modular system that delivers power and communications on a common bus. Connecting modules is a one-step process: just slide the modules together using the built-in connectors.

Patented two-piece design

Each module can be separated from its terminal base to allow the site to be wired prior to the installation of the electronics. The patented locking mechanism serves as handles for removing the module from its base. All critical components have a protective cover that permits convection cooling to occur.

 
action_zoom_plus_stroke Two-piece design
Figure: Two-piece design
Hot-connect and Hot-swap

Because critical applications require 24-hour operation, Schneider Electric designed the I/O modules for hot-connection of terminal bases and hot-swapping of the modules to their bases. This design ensures continuous power and communication during service operations.

Auto-addressing

The auto-addressing feature helps eliminating the need for setting DIP switches or pressing commission buttons. Each module automatically knows its order in the chain and assigns itself accordingly – significantly reducing engineering and maintenance time.

Simple DIN-rail installation

Fasteners easily snap into a locked position for panel installation. The fastener has a quick-release feature for easy DIN-rail removal.

Efficient terminal management

The I/O module terminals are clearly labeled and protected by transparent covers. The input and output terminals are at the top and bottom of each module and are accessible for maintenance without removing the module. The StruxureWare Building Operation WorkStation software can generate custom as-built labels for each module. Pre-perforated letter and A4 size label sheets are available as an accessory.

Accommodates multiple row panel installations

The SmartStruxure devices use built-in connectors for single row connectivity, side by side. If a panel size requires multiple rows, extension cords are available.

LED status indicators

The I/O module has a status indicator that denotes the health and status of the module.

Each digital output channel has a dedicated status indicator using a green LED.

Hand/Off/Auto switches

The front panel of the DO-FC-8-H includes Hand/Off/Auto (HOA) switches to provide override control of the digital outputs.

The position of the HOA switch is readable through user interfaces, such as the StruxureWare Building Operation WorkStation software, enabling more precise monitoring and control.

Specifications

Output channels
8
DC input supply power
2.2 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.332 kg (0.73 lb)
Weight excluding terminal base
0.209 kg (0.46 lb)
Terminal base
TB-IO-W1
Agency compliances
Emission
RCM; BS/EN 61000-6-3; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2
Safety standards
BS/EN 61010-1; UL 916 C-UL US Listed
Product
BS/EN 61326-1
Smoke control product safety
UL 864
Part numbers
DO-FC-8, I/O module
8 Form C digital outputs
SXWDOC8XX10001
DO-FC-8-H, I/O module with HOA switches
8 Form C digital outputs with Hand/Off/Auto override switches
SXWDOC8HX10001
TB-IO-W1, terminal base for I/O module
(Required for each I/O module)
SXWTBIOW110001
Accessory part numbers
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
PRINTOUT-A4-W1, printout sheets for terminal labels
A4 sheet size, 100 sheets, 18 labels per sheet
SXWTERLBL10011
PRINTOUT-LTR-W1, printout sheets for terminal labels
Letter sheet size, 100 sheets, 16 labels per sheet
SXWTERLBL10012
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
1.5 m
SXWSCABLE10002
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
0.75 m
SXWSCABLE10003
Digital outputs
 
action_zoom_plus_stroke
Contact rating
250 VAC/30 VDC, 3 A, Pilot Duty (Power Factor 0.35)
Switch type
Form C Relay
  
Single Pole Double Throw
  
Normally Open or Normally Closed
Isolation contact to system ground
5000 VAC
Cycle life (Resistive load)
At least 100,000 cycles
Minimum pulse width
100 ms
LED polarity energized relay
On
LED polarity non-energized relay
Off
LED color
Green

For protection from excess current that could be produced by field wiring, see Hardware Reference Guide.

  • UI-16
  • DI-16
  • RTD-DI-16
  • AO-8 and AO-8-H
  • AO-V-8 and AO-V-8-H
  • DO-FA-12 and DO-FA-12-H
  • UI-8/AO-4 and UI-8/AO-4-H
  • UI-8/AO-V-4 and UI-8/AO-V-4-H
  • UI-8/DO-FC-4 and UI-8/DO-FC-4-H