SpaceLogic™DO-FC-8 和 DO-FC-8-H 中央 IO 模块直接连接到 SpaceLogic AS-P 服务器,为工厂或设备室内大型机械系统的集中控制提供输出点。带有 AS-P 服务器的中央 IO 模块是模块化系统的一部分,该系统在通用 I/O 总线上提供电源和通信,以实现可扩展的自定义配置。
SpaceLogic DO-FC-8 和 DO-FC-8-H 中央 IO 模块为数字输出 8 通道 I/O 模块。
The digital outputs support digital Form C point types. The Form C relays are designed for direct load applications.
The modules are part of a modular system that delivers power and communications on a common bus. Connecting modules is a one-step process: just slide the modules together using the built-in connectors.
Each module can be separated from its terminal base to allow the site to be wired prior to the installation of the electronics. The patented locking mechanism serves as handles for removing the module from its base. All critical components have a protective cover that permits convection cooling to occur.
Because critical applications require 24-hour operation, Schneider Electric designed the Central IO modules for hot-connection of terminal bases and hot-swapping of the modules to their bases. This design ensures continuous power and communication during service operations.
The auto-addressing feature helps eliminating the need for setting DIP switches or pressing commission buttons. Each module automatically knows its order in the chain and assigns itself accordingly – significantly reducing engineering and maintenance time.
Fasteners easily snap into a locked position for panel installation. The fastener has a quick-release feature for easy DIN-rail removal.
The Central IO module terminals are clearly labeled and protected by transparent covers. The input and output terminals are at the top and bottom of each module and are accessible for maintenance without removing the module. The EcoStruxure Building Operation WorkStation software can generate custom as-built labels for each module. Pre-perforated letter and A4 size label sheets are available as an accessory.
The SpaceLogic devices use built-in connectors for single row connectivity, side by side. If a panel size requires multiple rows, extension cords are available.
The Central IO module has a status indicator that denotes the health and status of the module.
Each digital output channel has a dedicated status indicator using a green LED.
DO-FC-8-H 的前面板包含手动/关闭/自动 (HOA) 开关,以提供对数字输出的超驰控制。
The position of the HOA switch is readable through user interfaces, such as the EcoStruxure Building Operation WorkStation software, enabling more precise monitoring and control.
Output channels
|
8
|
DC input supply power
|
2.2 W
|
DC input supply voltage
|
24 VDC
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Maximum humidity
|
95 % RH non-condensing
|
Material | |
Plastic flame rating
|
UL94-5VB
|
Enclosure
|
PC/ABS
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions including terminal base
|
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
|
![]() |
|
Weight including terminal base
|
0.332 kg (0.73 lb)
|
Weight excluding terminal base
|
0.209 kg (0.46 lb)
|
Terminal base
|
TB-IO-W1
|
Agency compliances | |
Emission
|
RCM; BS/EN 61000-6-3; FCC Part 15, Sub-part B, Class B
|
Immunity
|
BS/EN 61000-6-2
|
Safety standards
|
BS/EN 61010-1; UL 916 C-UL US Listed
|
Product
|
BS/EN 61326-1
|
Smoke control product safety
|
UL 864
|
Part numbers | |
DO-FC-8, Central IO module
|
|
8 Form C digital outputs
|
SXWDOC8XX10001
|
DO-FC-8-H, Central IO module with HOA switches
|
|
8 Form C digital outputs with Hand/Off/Auto override switches
|
SXWDOC8HX10001
|
TB-IO-W1, terminal base for Central IO module
|
|
(Required for each Central IO module)
|
SXWTBIOW110001
|
Accessory part numbers | |
DIN-RAIL-CLIP, DIN-rail end clip
|
|
package of 25 pieces
|
SXWDINEND10001
|
PRINTOUT-A4-W1, printout sheets for terminal labels
|
|
A4 sheet size, 100 sheets, 18 labels per sheet
|
SXWTERLBL10011
|
PRINTOUT-LTR-W1, printout sheets for terminal labels
|
|
Letter sheet size, 100 sheets, 16 labels per sheet
|
SXWTERLBL10012
|
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
|
|
1.5 m
|
SXWSCABLE10002
|
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
|
|
0.75 m
|
SXWSCABLE10003
|
Digital outputs | |
![]() |
|
Contact rating
|
250 VAC/30 VDC, 3 A, Pilot Duty (Power Factor 0.35)
|
Switch type
|
Form C Relay
|
Single Pole Double Throw
|
|
Normally Open or Normally Closed
|
|
Isolation contact to system ground
|
5000 VAC
|
Cycle life (Resistive load)
|
At least 100,000 cycles
|
Minimum pulse width
|
100 ms
|
LED polarity energized relay
|
On
|
LED polarity non-energized relay
|
Off
|
LED color
|
Green
|
For protection from excess current that could be produced by field wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.