An enumeration is a range of values representing a specific command or event.
The table lists the enumeration values for System Alarm ID. For more information, see Event and Alarm Enumerations .
Enumeration value |
Enumeration definition |
0 |
EcoStruxure BMS server restarted |
1 |
IO module offline |
2 |
EcoStruxure BMS server offline |
4 |
E-mail service failed to connect to SMTP server |
5 |
E-mail service failed to login to SMTP server |
6 |
System cold start |
7 |
System warm start |
8 |
System factory reset |
9 |
Device offline |
a |
Signal alarm |
b |
Cannot verify lead object status |
c |
Duplicate of local network |
d |
Duplicate network identifier |
e |
Duplicate device identifier |
f |
Invalid device identifier |
10 |
Duplicate device address |
11 |
Duplicate device name |
12 |
Defective protocol implementation |
13 |
BACnet did not start |
14 |
Failed to create object |
15 |
Failed to initialize references |
16 |
Database update failed |
17 |
A log sample was missed |
18 |
A log data transfer was missed |
19 |
File I/O error |
1a |
EcoStruxure BMS server configuration error |
1b |
Network offline |
1c |
IP connection offline |
1d |
Signal event |
1e |
New application program |
1f |
Parser failed |
20 |
Unit is locked |
21 |
Unit is unlocked |
22 |
Logging started |
23 |
Logging stopped |
24 |
Log stopped because it is full |
25 |
Log full |
26 |
Not enough RAM memory for log |
27 |
Too many log definitions |
28 |
Error in log definition |
29 |
Not enough flash memory for log |
2a |
Log variable error |
2b |
No valid Blueprint File |
2c |
Unhandled buffer ready notification |
2d |
Alarm signal trigger buffer full |
2e |
Bad lead object reference |
2f |
Bad lead object type |
30 |
Shadow update failed |
31 |
Unable to access lead object |
32 |
Incorrect lead object back-reference |
33 |
Unable to access shadow object |
34 |
Server not restarted Backup in process |
25 |
Server not restarted Restore in process |
36 |
Server not restarted Other |
37 |
Failure retrieving backup set from remote server |
38 |
Failure restoring server database |
39 |
Failure backing up server database |
3a |
E-mail service fail to send message |
3b |
E-mail service configuration error |
3c |
Port offline |
3d |
Wrong alarm unit |
3e |
BACnet server failure |
3f |
Sigma system schedule executed |
40 |
Subnet offline |
41 |
Invalid device address |
64 |
Invalid archive path |
65 |
Archive path must be set to enable archiving |
66 |
Archive directory does not exist! Retrying in 5 minutes! |
67 |
Archive directory does not exist! |
68 |
Can not enable archiving |
69 |
Invalid archiving format |
6a |
Archiving is not enabled |
6b |
IO error when generating archive |
6c |
IO error when writing to archive temporary |
6d |
IO error, cannot write to archive directory! |
6e |
IO error, cannot write to archive directory! Retrying in 5 minutes! |
6f |
IO error, not enough space left in the archive directory! |
70 |
IO error, not enough space left in the archive directory! Retrying in 5 minutes! |
73 |
Archiving failed because of an ongoing operation |
74 |
Archiving canceled due to configuration change |
100 |
Communication failed |
101 |
Communication failed Configuration error |
102 |
Communication failed Unexpected Server fullpath |
103 |
Communication failed Unexpected Server type |
104 |
Communication failed Authentication error |
105 |
Communication failed Authorization error |
106 |
Communication failed Domain is not available |
107 |
Communication failed Hostname is invalid |
108 |
Communication failed Version Mismatch |
200 |
Task 1 CPU limit reached, disabling real time priority |
201 |
Task 2 CPU limit reached, disabling real time priority |
211 |
Email service no sender email address |
212 |
Email service no recipient email address |
213 |
Email service no sender and recipient email address |
214 |
Task period extended |
215 |
No file name set |
216 |
Module type mismatch |
217 |
Serial port in use |
1f40 |
NETWORK 8000 message |
1f41 |
NW8 Unrecognized command |
1f42 |
NW8 Command failure |
1f43 |
NW8 Leaves network event |
1f44 |
NW8 Joins network event |
1f45 |
NW8 ASD message |
1f46 |
NW8 Leaves/joins network |
1f4a |
NW8 Database initialized |
1f4b |
NW8 ROM failure |
1f4c |
NW8 RAM failure |
1f4d |
NW8 Freeze error |
1f4e |
NW8 Database modified |
1f4f |
NW8 Device warm reset |
1f50 |
NW8 Device cold reset |
1f51 |
NW8 AS1 diagnostic |
1f52 |
NW8 AT1 diagnostic |
1f53 |
NW8 AT2 diagnostic |
1f54 |
NW8 UI diagnostic |
1f55 |
NW8 UI1 diagnostic |
1f56 |
NW8 UI2 diagnostic |
1f57 |
NW8 UI3 diagnostic |
1f58 |
NW8 UI4 diagnostic |
1f59 |
NW8 UI5 diagnostic |
1f5a |
NW8 UI6 diagnostic |
1f5b |
NW8 UI7 diagnostic |
1f5c |
NW8 UI8 diagnostic |
1f5e |
NW8 Relay failure |
1f5f |
NW8 Relay failure 01 |
1f60 |
NW8 Relay failure 02 |
1f61 |
NW8 Relay failure 03 |
1f62 |
NW8 Relay failure 04 |
1f63 |
NW8 Relay failure 05 |
1f64 |
NW8 Relay failure 06 |
1f65 |
NW8 Relay failure 07 |
1f66 |
NW8 Relay failure 08 |
1f67 |
NW8 Relay failure 09 |
1f68 |
NW8 Relay failure 10 |
1f69 |
NW8 Relay failure 11 |
1f6a |
NW8 Relay failure 12 |
1f6b |
NW8 Relay failure 13 |
1f6c |
NW8 Relay failure 14 |
1f6d |
NW8 Relay failure 15 |
1f6e |
NW8 Relay failure 16 |
1f6f |
NW8 Relay failure 17 |
1f70 |
NW8 Relay failure 18 |
1f71 |
NW8 Relay failure 19 |
1f72 |
NW8 Relay failure 20 |
1f73 |
NW8 Relay failure 21 |
1f74 |
NW8 Relay failure 22 |
1f75 |
NW8 Relay failure 23 |
1f76 |
NW8 Relay failure 24 |
1f77 |
NW8 Relay failure 25 |
1f78 |
NW8 Relay failure 26 |
1f79 |
NW8 Relay failure 27 |
1f7a |
NW8 Relay failure 28 |
1f7b |
NW8 Relay failure 29 |
1f7c |
NW8 Relay failure 30 |
1f7d |
NW8 Relay failure 31 |
1f7e |
NW8 Relay failure 32 |
1f7f |
NW8 Relay failure 33 |
1f80 |
NW8 Relay failure 34 |
1f81 |
NW8 Relay failure 35 |
1f82 |
NW8 Relay failure 36 |
1f83 |
NW8 Relay failure 37 |
1f84 |
NW8 Relay failure 38 |
1f85 |
NW8 Relay failure 39 |
1f86 |
NW8 Relay failure 40 |
1f87 |
NW8 Relay failure 41 |
1f88 |
NW8 Relay failure 42 |
1f89 |
NW8 Relay failure 43 |
1f8a |
NW8 Relay failure 44 |
1f8b |
NW8 Relay failure 45 |
1f8c |
NW8 Relay failure 46 |
1f8d |
NW8 Relay failure 47 |
1f8e |
NW8 Relay failure 48 |
1f90 |
NW8 Setpoint out of range |
1f91 |
NW8 Duct temperature out of range |
1f92 |
NW8 Zone temperature out of range |
1f93 |
NW8 Device reset |
1f94 |
NW8 Configuration error |
1f95 |
NW8 Damper range error |
1f96 |
NW8 Pressure error |
1f97 |
NW8 EEprom memory error |
1f98 |
NW8 Application modified |
1f99 |
NW8 Missing changeover input |
1f9a |
NW8 EEprom checksum error |
1f9b |
NW8 Sensor input failure |
1f9c |
NW8 System fault 32 |
1f9d |
NW8 No U-Link communication |
1f9e |
NW8 Application error 1 |
1f9f |
NW8 Application error 2 |
1fa0 |
NW8 Application error 4 |
1fa1 |
NW8 Application error 16 |
1fa4 |
NW8 Press sensor |
1fa5 |
NW8 Duct temperature |
1fa6 |
NW8 Minimum flow potentiometer |
1fa7 |
NW8 Maximum flow potentiometer |
1fa8 |
NW8 Hot water potentiometer |
1fa9 |
NW8 Induction auxilary potentiometer |
1faa |
NW8 Space setpoint |
1fab |
NW8 Space temperature |
1faf |
NW8 Sensor failure GCS 01 |
1fc3 |
NW8 Sensor failure GCS 02 |
1fd7 |
NW8 Sensor failure GCS 03 |
1feb |
NW8 Sensor failure GCS 04 |
1fff |
NW8 Sensor failure GCS 05 |
2013 |
NW8 Sensor failure GCS 06 |
2027 |
NW8 Sensor failure GCS 07 |
203b |
NW8 Sensor failure GCS 08 |
204f |
NW8 Sensor failure GCS 09 |
2063 |
NW8 Sensor failure GCS 10 |
2077 |
NW8 Sensor failure GCS 21 |
208b |
NW8 Sensor failure GCS 22 |
209f |
NW8 Sensor failure GCS 23 |
20b3 |
NW8 Sensor failure GCS 24 |
20c7 |
NW8 Sensor failure GCS 25 |
20db |
NW8 Sensor failure GCS 26 |
20ef |
NW8 Sensor failure GCS 27 |
2103 |
NW8 Sensor failure GCS 28 |
2117 |
NW8 Sensor failure GCS 29 |
212b |
NW8 Sensor failure GCS 30 |
213f |
NW8 Sensor failure GCS 31 |
2150 |
NW8 Sensor failure end |
2151 |
NW8 Leaves LCM network event |
2152 |
NW8 Joins LCM network event |
2153 |
NW8 Leaves/joins LCM network |
2197 |
NETWORK 8000 message end |
2198 |
CWS Method Error |
2199 |
CWS Value Poll failed |
219a |
CWS Alarm Poll failed |
219b |
CWS Browse failed |
219c |
CWS GetObject failed |
219d |
CWS GetHistory failed |
219e |
See gap after 0x200 |
219f |
Device address changed |
21A0 |
Blacklisted device detected |
21A1 |
Local administrator account has empty or default password |
21A2 |
X509 certificate error |
21A3 |
Web server failure |
21A4 |
IO driver unexpectedly timed out |
21A5 |
Error - Upgrade using DFU mode |
21A6 |
Database file is corrupt |
21A7 |
Xenta schedule update failure |
21A8 |
Xenta central schedule update failure |
21A9 |
SNMP send trap failure |
21AA |
Error in retrieving Xenta device Trend Log data |
21AB |
Corrupt backup set detected |
21AC |
Trend storage capacity reached |
21AD |
SmartDriver network configuration invalid |
21AE |
An error was found in a communication module during server startup |
21AF |
Licensing violation |
21B0 |
Notification files storage capacity reached |
21B1 |
Driver loading disabled |
21B2 |
Sigma RUDs exceeded the network limit |
21B3 |
Sigma RUDs exceeded the controller limit |
21B4 |
Sigma globals exceeded the network limit |
21B5 |
Another server has hosted device |
21B6 |
More than one server with the same name in the system |
21B7 |
Device model mismatch detected |
21B8 |
Unexpected type information |
21B9 |
Cloud failure |
21BA |
Cloud SystemDiscovery failure |
21BB |
Invalid License Server Configuration |
21BC |
Server has too many created objects and upgrade is disabled |
21BD |
Cloud SMS channel offline |
21BE |
Cloud telemetry channel offline |
21BF |
Cloud file channel offline |
21C0 |
Missing response from server |
21C1 |
External storage unavailable |
21C2 |
External storage failed to connect |
21C3 |
External storage no database schema found |
21C4 |
Too many failing attempts to verify signature |
21C5 |
External storage incorrect schema version upgrade schema |
21C6 |
External storage incorrect schema version upgrade server |
21C7 |
Log on failed - authentication |
21C8 |
Remote Server does not support transport of 64 bit sequence numbers and needs to be upgraded |
21C9 |
Remote Server does not support transport of 64 bit sequence numbers and needs to be upgraded soon |
21CA |
Notification error |
21CB |
Math expression error |
21CC |
Circular binding |
21CD |
Email service failed to add attachment |
21CE |
MQTT - Failed to connect to broker |
21CF |
MQTT - Buffer overflow |
21D0 |
Failed to generate PDF |
21D1 |
Failed to generate signed PDF - No certificate found |
21D2 |
TLS configuration error |
21D3 |
Failed to generate signed PDF - No license found |
21D4 |
Failed to generate signed PDF - No certificate or license found |
21D5 |
External storage merge log failed source log not found |
21D6 |
External storage merge log failed target log not found |
21D7 |
Failed to generate signed PDF - Signing process timeout |
21D8 |
Log processing error - Loop detected |
21D9 |
Alarm buffer full |
21DA |
Invalid certificate for https communication |
21DB |
Insight sensor frame error |
21DC |
Federation - SAML - Service does not exist |
21DD |
Federation - SAML - Service could not be launched |
21DE |
Semantic DB has default admin password |
21DF |
Semantic DB query failed |
21E0 |
Semantic DB offline |
21E1 |
Semantic DB authentication failure |
21E2 |
Semantic DB timeout query |
21E3 |
Semantic DB timeout search |
21E4 |
Semantic DB timeout export |
21E5 |
Semantic DB timeout update |
21E6 |
Semantic DB timeout update file |
21E7 |
Semantic DB backup failed |
21E8 |
Federation - SAML - Configuration Synchronization Failed |
21E9 |
Failed to get platform property |
21EA |
Failed to set platform property |
21EB |
Insufficient Function Block Program engine version detected |
21EC |
Log on failed - account has been temporarily locked |
21ED |
Semantic DB no valid license |
21EE |
Schedule evaluation overrun |
21EF |
Device backup to flash disabled |
4000 |
Unknown fault |
4001 |
Unknown maintenance |
4002 |
Anytype config, not found |
4003 |
Address found, no config |
4004 |
Beam sensor local test fail |
4005 |
Beam sensor remote test fail |
4006 |
Memory fault in unit |
4007 |
Sounder fault in unit |
4008 |
Beacon fault in unit |
4009 |
Sounder and beacon fault in unit |
400A |
Fault in unit |
400B |
Remote LED config, not supported |
400C |
Battery missing |
400D |
Unit fault |
400E |
Head missing |
400F |
Sounder missing |
4010 |
Tamper |
4011 |
Signal strength |
4012 |
Battery fault |
4013 |
CO element fault |
4014 |
Heat element fault |
4016 |
Sensor and module unit have same address |
4017 |
Double address |
4018 |
Bad scan response of device |
4019 |
Comm. error frame ID vs mem. ID |
401A |
Protocol family vs config. |
401B |
Double address (SLC) |
401C |
Double address (LC and SLC) |
401D |
Module subaddress overlap |
401E |
Configured, not found |
401F |
Device internal error |
4020 |
Open circuit in loop |
4021 |
Short circuit in loop |
4022 |
Earth leakage fault (positive) |
4023 |
Earth leakage fault (negative) |
4024 |
Loop scanning trouble |
4025 |
PS mains fault |
4026 |
PS charger fault |
4027 |
PS charger overvoltage fault |
4028 |
PS battery low voltage fault |
4029 |
PS battery fault |
402A |
Device detached and attached |
402B |
Open circuit in monitored input |
402C |
Short circuit in monitored input |
402D |
Voice evac. fault input activated |
402E |
Fault input activated |
402F |
Fire router fault |
4030 |
Fault router fault |
4031 |
Extinguisher fault |
4032 |
Address configuration missing |
4033 |
Text configuration missing |
4034 |
Panel configuration missing |
4035 |
Multimod. subaddr too high |
4036 |
Event register cleared |
4037 |
Fire detection unit halted |
4038 |
Fire panel restarted |
4039 |
Short circuit in MC monitored output |
403A |
Open circuit in MC monitored output |
403B |
Short circuit in monitored output |
403C |
Open circuit in monitored output |
403D |
Too old sw version of (monitored output |
403E |
Fire alarm device mute input timeout |
403F |
Fault in info port comm. |
4040 |
Short circuit in module input |
4041 |
IO-configuration missing |
4042 |
LC communication fault |
4043 |
LC communication restarted |
4044 |
I/O communication fault |
4045 |
I/O communication restarted |
4046 |
IOU installation conflict |
4047 |
PS communication fault |
4048 |
PS communication restarted |
4049 |
SA unit |
404A |
Configuration information missing |
404B |
Fault in MC power output PO |
404C |
Fault in PS power output PO |
404D |
Fault in power output PO |
404E |
Fault in LC power output PO |
404F |
LC installation conflict |
4050 |
Fault in MC power input PI |
4051 |
Connection fault to panel |
4052 |
Connection to panel restarted |
4053 |
Connection line to panel |
4054 |
Panel message queue overflow |
4055 |
Incompatible software in panel |
4056 |
More than devices of 200-series in the loop |
4057 |
Communication failure in loop |
4058 |
Info port cannot handle address numbers higher than 255. |
4059 |
Extra battery package connection fault |
405A |
Extra battery package connection fault |
405B |
Extra battery package connection fault |
405C |
Extra battery package connection fault |
405D |
PS charger temperature fault |
405E |
PS unknown HW version |
405F |
Too high resistance in loop |
4060 |
Resistive load in loop |
4061 |
Too high current in loop |
4062 |
Too high voltage drop in loop |
4063 |
Maintenance service period expired |
4064 |
Maintenance input activated |
4065 |
Configured not same as found |
4066 |
Info external device fault |
4067 |
Info external device fault |
4068 |
Info external device fault |
4069 |
Info transmitter fault |
406A |
Info receiver fault |
406B |
Info external device fault |
406C |
Info external device fault |
406D |
Info external device fault |
406E |
Info transmitter watchdog fault |
406F |
Info receiver watchdog fault |
4070 |
Info unknown external device fault |
4071 |
User interface communication fault |
4072 |
Info device board not installed |
4073 |
Active config file content error |
4074 |
Active config file open error |
4075 |
Active config checksum file open error |
4076 |
Active config file checksum error |
4077 |
Configuration data missing |
4078 |
APU communication fault |
4079 |
APU communication restarted |
407A |
Short circuit in APU monitored output |
407B |
Open circuit in APU monitored output |
407C |
APU installation conflict |
407D |
Communication missing in APU line |
407E |
Communication missing in APU line |
407F |
Database out of memory |
4080 |
Connection fault in Ethernet line |
4081 |
Connection fault in Ethernet line |
4082 |
Failed to read factory settings |
4084 |
Address not set |
4085 |
Too low analog value |
4086 |
No/invalid reply from address |
4017 |
Double address |
4087 |
Break in module input |
4088 |
Break in module output |
4089 |
Short circuit in mod. output |
402E |
Fault input activated |
408A |
Zone disabl. time exceeded |
408B |
Maint. input activated |
408C |
Unknown type of device |
408D |
Contaminated detector |
408E |
months to CO cl expiration |
408F |
Conv.subloop break/shortc. |
4090 |
Invalid response from device |
4091 |
Device type changed while loop was running |
4092 |
Extinguisher input activated |
4093 |
Infrared saturation on det. |
4094 |
80% drift limit reached |
4095 |
99% drift limit reached |
4096 |
Device removed on loop disab. |
4097 |
Unknown fault from device |
4098 |
Device mem. write failed |
4099 |
Device mem. read failed |
409A |
Device comm. trouble |
409B |
Device self test failed |
409C |
Beam sensor CPU fault |
409D |
Beam sensor align targeting |
409E |
Beam sensor general fault |
409F |
Beam sensor signal too high |
40A0 |
Detector CO cell expiration |
40A1 |
Device type changed while loop was starting up |
40A2 |
ALC SW not compatible |
40A3 |
Router fault input activated |
40A4 |
Output mod. power failure |
40A5 |
Not Esmi device |
40A6 |
Output control failure |
40A7 |
Device SW not compatible |
40A8 |
Isolator disappeared |
40A9 |
Isolator appeared |
40AA |
New address in the loop |
40AB |
Unacceptable device (family) |
40AC |
Break in CLC input |
40AD |
Short circuit in CLC input |
40AE |
Voltage problem in CLC input |
40AF |
VoiceEvac mute input timeout |
40B0 |
Unit memory checksum |
40B1 |
Beam sensor signal blocked |
40B2 |
Simulated maint/serv command |
40B3 |
Simulated fault/serv command |
40B4 |
Fire |
40B5 |
Local fire |
40B6 |
Coincidence fire |
40B7 |
Delayed fire |