earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: Enterprise Central, Enterprise Server, Virtual Project Servers
Functionalities: Basic Functionality
Product version: 2023, 2024
8/30/2024

System Alarm ID Enumerations

An enumeration is a range of values representing a specific command or event.

The table lists the enumeration values for System Alarm ID. For more information, see Event and Alarm Enumerations .

Table: System Alarm ID

Enumeration value

Enumeration definition

0

EcoStruxure BMS server restarted

1

IO module offline

2

EcoStruxure BMS server offline

4

E-mail service failed to connect to SMTP server

5

E-mail service failed to login to SMTP server

6

System cold start

7

System warm start

8

System factory reset

9

Device offline

a

Signal alarm

b

Cannot verify lead object status

c

Duplicate of local network

d

Duplicate network identifier

e

Duplicate device identifier

f

Invalid device identifier

10

Duplicate device address

11

Duplicate device name

12

Defective protocol implementation

13

BACnet did not start

14

Failed to create object

15

Failed to initialize references

16

Database update failed

17

A log sample was missed

18

A log data transfer was missed

19

File I/O error

1a

EcoStruxure BMS server configuration error

1b

Network offline

1c

IP connection offline

1d

Signal event

1e

New application program

1f

Parser failed

20

Unit is locked

21

Unit is unlocked

22

Logging started

23

Logging stopped

24

Log stopped because it is full

25

Log full

26

Not enough RAM memory for log

27

Too many log definitions

28

Error in log definition

29

Not enough flash memory for log

2a

Log variable error

2b

No valid Blueprint File

2c

Unhandled buffer ready notification

2d

Alarm signal trigger buffer full

2e

Bad lead object reference

2f

Bad lead object type

30

Shadow update failed

31

Unable to access lead object

32

Incorrect lead object back-reference

33

Unable to access shadow object

34

Server not restarted Backup in process

25

Server not restarted Restore in process

36

Server not restarted Other

37

Failure retrieving backup set from remote server

38

Failure restoring server database

39

Failure backing up server database

3a

E-mail service fail to send message

3b

E-mail service configuration error

3c

Port offline

3d

Wrong alarm unit

3e

BACnet server failure

3f

Sigma system schedule executed

40

Subnet offline

41

Invalid device address

64

Invalid archive path

65

Archive path must be set to enable archiving

66

Archive directory does not exist! Retrying in 5 minutes!

67

Archive directory does not exist!

68

Can not enable archiving

69

Invalid archiving format

6a

Archiving is not enabled

6b

IO error when generating archive

6c

IO error when writing to archive temporary

6d

IO error, cannot write to archive directory!

6e

IO error, cannot write to archive directory! Retrying in 5 minutes!

6f

IO error, not enough space left in the archive directory!

70

IO error, not enough space left in the archive directory! Retrying in 5 minutes!

73

Archiving failed because of an ongoing operation

74

Archiving canceled due to configuration change

100

Communication failed

101

Communication failed Configuration error

102

Communication failed Unexpected Server fullpath

103

Communication failed Unexpected Server type

104

Communication failed Authentication error

105

Communication failed Authorization error

106

Communication failed Domain is not available

107

Communication failed Hostname is invalid

108

Communication failed Version Mismatch

200

Task 1 CPU limit reached, disabling real time priority

201

Task 2 CPU limit reached, disabling real time priority

211

Email service no sender email address

212

Email service no recipient email address

213

Email service no sender and recipient email address

214

Task period extended

215

No file name set

216

Module type mismatch

217

Serial port in use

1f40

NETWORK 8000 message

1f41

NW8 Unrecognized command

1f42

NW8 Command failure

1f43

NW8 Leaves network event

1f44

NW8 Joins network event

1f45

NW8 ASD message

1f46

NW8 Leaves/joins network

1f4a

NW8 Database initialized

1f4b

NW8 ROM failure

1f4c

NW8 RAM failure

1f4d

NW8 Freeze error

1f4e

NW8 Database modified

1f4f

NW8 Device warm reset

1f50

NW8 Device cold reset

1f51

NW8 AS1 diagnostic

1f52

NW8 AT1 diagnostic

1f53

NW8 AT2 diagnostic

1f54

NW8 UI diagnostic

1f55

NW8 UI1 diagnostic

1f56

NW8 UI2 diagnostic

1f57

NW8 UI3 diagnostic

1f58

NW8 UI4 diagnostic

1f59

NW8 UI5 diagnostic

1f5a

NW8 UI6 diagnostic

1f5b

NW8 UI7 diagnostic

1f5c

NW8 UI8 diagnostic

1f5e

NW8 Relay failure

1f5f

NW8 Relay failure 01

1f60

NW8 Relay failure 02

1f61

NW8 Relay failure 03

1f62

NW8 Relay failure 04

1f63

NW8 Relay failure 05

1f64

NW8 Relay failure 06

1f65

NW8 Relay failure 07

1f66

NW8 Relay failure 08

1f67

NW8 Relay failure 09

1f68

NW8 Relay failure 10

1f69

NW8 Relay failure 11

1f6a

NW8 Relay failure 12

1f6b

NW8 Relay failure 13

1f6c

NW8 Relay failure 14

1f6d

NW8 Relay failure 15

1f6e

NW8 Relay failure 16

1f6f

NW8 Relay failure 17

1f70

NW8 Relay failure 18

1f71

NW8 Relay failure 19

1f72

NW8 Relay failure 20

1f73

NW8 Relay failure 21

1f74

NW8 Relay failure 22

1f75

NW8 Relay failure 23

1f76

NW8 Relay failure 24

1f77

NW8 Relay failure 25

1f78

NW8 Relay failure 26

1f79

NW8 Relay failure 27

1f7a

NW8 Relay failure 28

1f7b

NW8 Relay failure 29

1f7c

NW8 Relay failure 30

1f7d

NW8 Relay failure 31

1f7e

NW8 Relay failure 32

1f7f

NW8 Relay failure 33

1f80

NW8 Relay failure 34

1f81

NW8 Relay failure 35

1f82

NW8 Relay failure 36

1f83

NW8 Relay failure 37

1f84

NW8 Relay failure 38

1f85

NW8 Relay failure 39

1f86

NW8 Relay failure 40

1f87

NW8 Relay failure 41

1f88

NW8 Relay failure 42

1f89

NW8 Relay failure 43

1f8a

NW8 Relay failure 44

1f8b

NW8 Relay failure 45

1f8c

NW8 Relay failure 46

1f8d

NW8 Relay failure 47

1f8e

NW8 Relay failure 48

1f90

NW8 Setpoint out of range

1f91

NW8 Duct temperature out of range

1f92

NW8 Zone temperature out of range

1f93

NW8 Device reset

1f94

NW8 Configuration error

1f95

NW8 Damper range error

1f96

NW8 Pressure error

1f97

NW8 EEprom memory error

1f98

NW8 Application modified

1f99

NW8 Missing changeover input

1f9a

NW8 EEprom checksum error

1f9b

NW8 Sensor input failure

1f9c

NW8 System fault 32

1f9d

NW8 No U-Link communication

1f9e

NW8 Application error 1

1f9f

NW8 Application error 2

1fa0

NW8 Application error 4

1fa1

NW8 Application error 16

1fa4

NW8 Press sensor

1fa5

NW8 Duct temperature

1fa6

NW8 Minimum flow potentiometer

1fa7

NW8 Maximum flow potentiometer

1fa8

NW8 Hot water potentiometer

1fa9

NW8 Induction auxilary potentiometer

1faa

NW8 Space setpoint

1fab

NW8 Space temperature

1faf

NW8 Sensor failure GCS 01

1fc3

NW8 Sensor failure GCS 02

1fd7

NW8 Sensor failure GCS 03

1feb

NW8 Sensor failure GCS 04

1fff

NW8 Sensor failure GCS 05

2013

NW8 Sensor failure GCS 06

2027

NW8 Sensor failure GCS 07

203b

NW8 Sensor failure GCS 08

204f

NW8 Sensor failure GCS 09

2063

NW8 Sensor failure GCS 10

2077

NW8 Sensor failure GCS 21

208b

NW8 Sensor failure GCS 22

209f

NW8 Sensor failure GCS 23

20b3

NW8 Sensor failure GCS 24

20c7

NW8 Sensor failure GCS 25

20db

NW8 Sensor failure GCS 26

20ef

NW8 Sensor failure GCS 27

2103

NW8 Sensor failure GCS 28

2117

NW8 Sensor failure GCS 29

212b

NW8 Sensor failure GCS 30

213f

NW8 Sensor failure GCS 31

2150

NW8 Sensor failure end

2151

NW8 Leaves LCM network event

2152

NW8 Joins LCM network event

2153

NW8 Leaves/joins LCM network

2197

NETWORK 8000 message end

2198

CWS Method Error

2199

CWS Value Poll failed

219a

CWS Alarm Poll failed

219b

CWS Browse failed

219c

CWS GetObject failed

219d

CWS GetHistory failed

219e

See gap after 0x200

219f

Device address changed

21A0

Blacklisted device detected

21A1

Local administrator account has empty or default password

21A2

X509 certificate error

21A3

Web server failure

21A4

IO driver unexpectedly timed out

21A5

Error - Upgrade using DFU mode

21A6

Database file is corrupt

21A7

Xenta schedule update failure

21A8

Xenta central schedule update failure

21A9

SNMP send trap failure

21AA

Error in retrieving Xenta device Trend Log data

21AB

Corrupt backup set detected

21AC

Trend storage capacity reached

21AD

SmartDriver network configuration invalid

21AE

An error was found in a communication module during server startup

21AF

Licensing violation

21B0

Notification files storage capacity reached

21B1

Driver loading disabled

21B2

Sigma RUDs exceeded the network limit

21B3

Sigma RUDs exceeded the controller limit

21B4

Sigma globals exceeded the network limit

21B5

Another server has hosted device

21B6

More than one server with the same name in the system

21B7

Device model mismatch detected

21B8

Unexpected type information

21B9

Cloud failure

21BA

Cloud SystemDiscovery failure

21BB

Invalid License Server Configuration

21BC

Server has too many created objects and upgrade is disabled

21BD

Cloud SMS channel offline

21BE

Cloud telemetry channel offline

21BF

Cloud file channel offline

21C0

Missing response from server

21C1

External storage unavailable

21C2

External storage failed to connect

21C3

External storage no database schema found

21C4

Too many failing attempts to verify signature

21C5

External storage incorrect schema version upgrade schema

21C6

External storage incorrect schema version upgrade server

21C7

Log on failed - authentication

21C8

Remote Server does not support transport of 64 bit sequence numbers and needs to be upgraded

21C9

Remote Server does not support transport of 64 bit sequence numbers and needs to be upgraded soon

21CA

Notification error

21CB

Math expression error

21CC

Circular binding

21CD

Email service failed to add attachment

21CE

MQTT - Failed to connect to broker

21CF

MQTT - Buffer overflow

21D0

Failed to generate PDF

21D1

Failed to generate signed PDF - No certificate found

21D2

TLS configuration error

21D3

Failed to generate signed PDF - No license found

21D4

Failed to generate signed PDF - No certificate or license found

21D5

External storage merge log failed source log not found

21D6

External storage merge log failed target log not found

21D7

Failed to generate signed PDF - Signing process timeout

21D8

Log processing error - Loop detected

21D9

Alarm buffer full

21DA

Invalid certificate for https communication

21DB

Insight sensor frame error

21DC

Federation - SAML - Service does not exist

21DD

Federation - SAML - Service could not be launched

21DE

Semantic DB has default admin password

21DF

Semantic DB query failed

21E0

Semantic DB offline

21E1

Semantic DB authentication failure

21E2

Semantic DB timeout query

21E3

Semantic DB timeout search

21E4

Semantic DB timeout export

21E5

Semantic DB timeout update

21E6

Semantic DB timeout update file

21E7

Semantic DB backup failed

21E8

Federation - SAML - Configuration Synchronization Failed

21E9

Failed to get platform property

21EA

Failed to set platform property

21EB

Insufficient Function Block Program engine version detected

21EC

Log on failed - account has been temporarily locked

21ED

Semantic DB no valid license

21EE

Schedule evaluation overrun

21EF

Device backup to flash disabled

4000

Unknown fault

4001

Unknown maintenance

4002

Anytype config, not found

4003

Address found, no config

4004

Beam sensor local test fail

4005

Beam sensor remote test fail

4006

Memory fault in unit

4007

Sounder fault in unit

4008

Beacon fault in unit

4009

Sounder and beacon fault in unit

400A

Fault in unit

400B

Remote LED config, not supported

400C

Battery missing

400D

Unit fault

400E

Head missing

400F

Sounder missing

4010

Tamper

4011

Signal strength

4012

Battery fault

4013

CO element fault

4014

Heat element fault

4016

Sensor and module unit have same address

4017

Double address

4018

Bad scan response of device

4019

Comm. error frame ID vs mem. ID

401A

Protocol family vs config.

401B

Double address (SLC)

401C

Double address (LC and SLC)

401D

Module subaddress overlap

401E

Configured, not found

401F

Device internal error

4020

Open circuit in loop

4021

Short circuit in loop

4022

Earth leakage fault (positive)

4023

Earth leakage fault (negative)

4024

Loop scanning trouble

4025

PS mains fault

4026

PS charger fault

4027

PS charger overvoltage fault

4028

PS battery low voltage fault

4029

PS battery fault

402A

Device detached and attached

402B

Open circuit in monitored input

402C

Short circuit in monitored input

402D

Voice evac. fault input activated

402E

Fault input activated

402F

Fire router fault

4030

Fault router fault

4031

Extinguisher fault

4032

Address configuration missing

4033

Text configuration missing

4034

Panel configuration missing

4035

Multimod. subaddr too high

4036

Event register cleared

4037

Fire detection unit halted

4038

Fire panel restarted

4039

Short circuit in MC monitored output

403A

Open circuit in MC monitored output

403B

Short circuit in monitored output

403C

Open circuit in monitored output

403D

Too old sw version of (monitored output

403E

Fire alarm device mute input timeout

403F

Fault in info port comm.

4040

Short circuit in module input

4041

IO-configuration missing

4042

LC communication fault

4043

LC communication restarted

4044

I/O communication fault

4045

I/O communication restarted

4046

IOU installation conflict

4047

PS communication fault

4048

PS communication restarted

4049

SA unit

404A

Configuration information missing

404B

Fault in MC power output PO

404C

Fault in PS power output PO

404D

Fault in power output PO

404E

Fault in LC power output PO

404F

LC installation conflict

4050

Fault in MC power input PI

4051

Connection fault to panel

4052

Connection to panel restarted

4053

Connection line to panel

4054

Panel message queue overflow

4055

Incompatible software in panel

4056

More than devices of 200-series in the loop

4057

Communication failure in loop

4058

Info port cannot handle address numbers higher than 255.

4059

Extra battery package connection fault

405A

Extra battery package connection fault

405B

Extra battery package connection fault

405C

Extra battery package connection fault

405D

PS charger temperature fault

405E

PS unknown HW version

405F

Too high resistance in loop

4060

Resistive load in loop

4061

Too high current in loop

4062

Too high voltage drop in loop

4063

Maintenance service period expired

4064

Maintenance input activated

4065

Configured not same as found

4066

Info external device fault

4067

Info external device fault

4068

Info external device fault

4069

Info transmitter fault

406A

Info receiver fault

406B

Info external device fault

406C

Info external device fault

406D

Info external device fault

406E

Info transmitter watchdog fault

406F

Info receiver watchdog fault

4070

Info unknown external device fault

4071

User interface communication fault

4072

Info device board not installed

4073

Active config file content error

4074

Active config file open error

4075

Active config checksum file open error

4076

Active config file checksum error

4077

Configuration data missing

4078

APU communication fault

4079

APU communication restarted

407A

Short circuit in APU monitored output

407B

Open circuit in APU monitored output

407C

APU installation conflict

407D

Communication missing in APU line

407E

Communication missing in APU line

407F

Database out of memory

4080

Connection fault in Ethernet line

4081

Connection fault in Ethernet line

4082

Failed to read factory settings

4084

Address not set

4085

Too low analog value

4086

No/invalid reply from address

4017

Double address

4087

Break in module input

4088

Break in module output

4089

Short circuit in mod. output

402E

Fault input activated

408A

Zone disabl. time exceeded

408B

Maint. input activated

408C

Unknown type of device

408D

Contaminated detector

408E

months to CO cl expiration

408F

Conv.subloop break/shortc.

4090

Invalid response from device

4091

Device type changed while loop was running

4092

Extinguisher input activated

4093

Infrared saturation on det.

4094

80% drift limit reached

4095

99% drift limit reached

4096

Device removed on loop disab.

4097

Unknown fault from device

4098

Device mem. write failed

4099

Device mem. read failed

409A

Device comm. trouble

409B

Device self test failed

409C

Beam sensor CPU fault

409D

Beam sensor align targeting

409E

Beam sensor general fault

409F

Beam sensor signal too high

40A0

Detector CO cell expiration

40A1

Device type changed while loop was starting up

40A2

ALC SW not compatible

40A3

Router fault input activated

40A4

Output mod. power failure

40A5

Not Esmi device

40A6

Output control failure

40A7

Device SW not compatible

40A8

Isolator disappeared

40A9

Isolator appeared

40AA

New address in the loop

40AB

Unacceptable device (family)

40AC

Break in CLC input

40AD

Short circuit in CLC input

40AE

Voltage problem in CLC input

40AF

VoiceEvac mute input timeout

40B0

Unit memory checksum

40B1

Beam sensor signal blocked

40B2

Simulated maint/serv command

40B3

Simulated fault/serv command

40B4

Fire

40B5

Local fire

40B6

Coincidence fire

40B7

Delayed fire

  • Event and Alarm Enumerations
  • Archive Log Contents
  • Event Archive File