An enumeration is a range of values representing a specific command or event.
The table lists the enumeration values for System Alarm ID. Para obtener más información, consulte Event and Alarm Enumerations .
| Enumeration value | Enumeration definition | 
| 0 | EcoStruxure BMS server restarted | 
| 1 | IO module offline | 
| 2 | EcoStruxure BMS server offline | 
| 4 | E-mail service failed to connect to SMTP server | 
| 5 | E-mail service failed to login to SMTP server | 
| 6 | System cold start | 
| 7 | System warm start | 
| 8 | System factory reset | 
| 9 | Device offline | 
| a | Signal alarm | 
| b | Cannot verify lead object status | 
| c | Duplicate of local network | 
| d | Duplicate network identifier | 
| e | Duplicate device identifier | 
| f | Invalid device identifier | 
| 10 | Duplicate device address | 
| 11 | Duplicate device name | 
| 12 | Defective protocol implementation | 
| 13 | BACnet did not start | 
| 14 | Failed to create object | 
| 15 | Failed to initialize references | 
| 16 | Database update failed | 
| 17 | A log sample was missed | 
| 18 | A log data transfer was missed | 
| 19 | File I/O error | 
| 1a | EcoStruxure BMS server configuration error | 
| 1b | Network offline | 
| 1c | IP connection offline | 
| 1d | Signal event | 
| 1e | New application program | 
| 1f | Parser failed | 
| 20 | Unit is locked | 
| 21 | Unit is unlocked | 
| 22 | Logging started | 
| 23 | Logging stopped | 
| 24 | Log stopped because it is full | 
| 25 | Log full | 
| 26 | Not enough RAM memory for log | 
| 27 | Too many log definitions | 
| 28 | Error in log definition | 
| 29 | Not enough flash memory for log | 
| 2a | Log variable error | 
| 2b | No valid Blueprint File | 
| 2c | Unhandled buffer ready notification | 
| 2d | Alarm signal trigger buffer full | 
| 2e | Bad lead object reference | 
| 2f | Bad lead object type | 
| 30 | Shadow update failed | 
| 31 | Unable to access lead object | 
| 32 | Incorrect lead object back-reference | 
| 33 | Unable to access shadow object | 
| 34 | Server not restarted Backup in process | 
| 25 | Server not restarted Restore in process | 
| 36 | Server not restarted Other | 
| 37 | Failure retrieving backup set from remote server | 
| 38 | Failure restoring server database | 
| 39 | Failure backing up server database | 
| 3a | E-mail service fail to send message | 
| 3b | E-mail service configuration error | 
| 3c | Port offline | 
| 3d | Wrong alarm unit | 
| 3e | BACnet server failure | 
| 3f | Sigma system schedule executed | 
| 40 | Subnet offline | 
| 41 | Invalid device address | 
| 64 | Invalid archive path | 
| 65 | Archive path must be set to enable archiving | 
| 66 | Archive directory does not exist! Retrying in 5 minutes! | 
| 67 | Archive directory does not exist! | 
| 68 | Can not enable archiving | 
| 69 | Invalid archiving format | 
| 6a | Archiving is not enabled | 
| 6b | IO error when generating archive | 
| 6c | IO error when writing to archive temporary | 
| 6d | IO error, cannot write to archive directory! | 
| 6e | IO error, cannot write to archive directory! Retrying in 5 minutes! | 
| 6f | IO error, not enough space left in the archive directory! | 
| 70 | IO error, not enough space left in the archive directory! Retrying in 5 minutes! | 
| 73 | Archiving failed because of an ongoing operation | 
| 74 | Archiving canceled due to configuration change | 
| 100 | Communication failed | 
| 101 | Communication failed Configuration error | 
| 102 | Communication failed Unexpected Server fullpath | 
| 103 | Communication failed Unexpected Server type | 
| 104 | Communication failed Authentication error | 
| 105 | Communication failed Authorization error | 
| 106 | Communication failed Domain is not available | 
| 107 | Communication failed Hostname is invalid | 
| 108 | Communication failed Version Mismatch | 
| 200 | Task 1 CPU limit reached, disabling real time priority | 
| 201 | Task 2 CPU limit reached, disabling real time priority | 
| 211 | Email service no sender email address | 
| 212 | Email service no recipient email address | 
| 213 | Email service no sender and recipient email address | 
| 214 | Task period extended | 
| 215 | No file name set | 
| 216 | Module type mismatch | 
| 217 | Serial port in use | 
| 1f40 | NETWORK 8000 message | 
| 1f41 | NW8 Unrecognized command | 
| 1f42 | NW8 Command failure | 
| 1f43 | NW8 Leaves network event | 
| 1f44 | NW8 Joins network event | 
| 1f45 | NW8 ASD message | 
| 1f46 | NW8 Leaves/joins network | 
| 1f4a | NW8 Database initialized | 
| 1f4b | NW8 ROM failure | 
| 1f4c | NW8 RAM failure | 
| 1f4d | NW8 Freeze error | 
| 1f4e | NW8 Database modified | 
| 1f4f | NW8 Device warm reset | 
| 1f50 | NW8 Device cold reset | 
| 1f51 | NW8 AS1 diagnostic | 
| 1f52 | NW8 AT1 diagnostic | 
| 1f53 | NW8 AT2 diagnostic | 
| 1f54 | NW8 UI diagnostic | 
| 1f55 | NW8 UI1 diagnostic | 
| 1f56 | NW8 UI2 diagnostic | 
| 1f57 | NW8 UI3 diagnostic | 
| 1f58 | NW8 UI4 diagnostic | 
| 1f59 | NW8 UI5 diagnostic | 
| 1f5a | NW8 UI6 diagnostic | 
| 1f5b | NW8 UI7 diagnostic | 
| 1f5c | NW8 UI8 diagnostic | 
| 1f5e | NW8 Relay failure | 
| 1f5f | NW8 Relay failure 01 | 
| 1f60 | NW8 Relay failure 02 | 
| 1f61 | NW8 Relay failure 03 | 
| 1f62 | NW8 Relay failure 04 | 
| 1f63 | NW8 Relay failure 05 | 
| 1f64 | NW8 Relay failure 06 | 
| 1f65 | NW8 Relay failure 07 | 
| 1f66 | NW8 Relay failure 08 | 
| 1f67 | NW8 Relay failure 09 | 
| 1f68 | NW8 Relay failure 10 | 
| 1f69 | NW8 Relay failure 11 | 
| 1f6a | NW8 Relay failure 12 | 
| 1f6b | NW8 Relay failure 13 | 
| 1f6c | NW8 Relay failure 14 | 
| 1f6d | NW8 Relay failure 15 | 
| 1f6e | NW8 Relay failure 16 | 
| 1f6f | NW8 Relay failure 17 | 
| 1f70 | NW8 Relay failure 18 | 
| 1f71 | NW8 Relay failure 19 | 
| 1f72 | NW8 Relay failure 20 | 
| 1f73 | NW8 Relay failure 21 | 
| 1f74 | NW8 Relay failure 22 | 
| 1f75 | NW8 Relay failure 23 | 
| 1f76 | NW8 Relay failure 24 | 
| 1f77 | NW8 Relay failure 25 | 
| 1f78 | NW8 Relay failure 26 | 
| 1f79 | NW8 Relay failure 27 | 
| 1f7a | NW8 Relay failure 28 | 
| 1f7b | NW8 Relay failure 29 | 
| 1f7c | NW8 Relay failure 30 | 
| 1f7d | NW8 Relay failure 31 | 
| 1f7e | NW8 Relay failure 32 | 
| 1f7f | NW8 Relay failure 33 | 
| 1f80 | NW8 Relay failure 34 | 
| 1f81 | NW8 Relay failure 35 | 
| 1f82 | NW8 Relay failure 36 | 
| 1f83 | NW8 Relay failure 37 | 
| 1f84 | NW8 Relay failure 38 | 
| 1f85 | NW8 Relay failure 39 | 
| 1f86 | NW8 Relay failure 40 | 
| 1f87 | NW8 Relay failure 41 | 
| 1f88 | NW8 Relay failure 42 | 
| 1f89 | NW8 Relay failure 43 | 
| 1f8a | NW8 Relay failure 44 | 
| 1f8b | NW8 Relay failure 45 | 
| 1f8c | NW8 Relay failure 46 | 
| 1f8d | NW8 Relay failure 47 | 
| 1f8e | NW8 Relay failure 48 | 
| 1f90 | NW8 Setpoint out of range | 
| 1f91 | NW8 Duct temperature out of range | 
| 1f92 | NW8 Zone temperature out of range | 
| 1f93 | NW8 Device reset | 
| 1f94 | NW8 Configuration error | 
| 1f95 | NW8 Damper range error | 
| 1f96 | NW8 Pressure error | 
| 1f97 | NW8 EEprom memory error | 
| 1f98 | NW8 Application modified | 
| 1f99 | NW8 Missing changeover input | 
| 1f9a | NW8 EEprom checksum error | 
| 1f9b | NW8 Sensor input failure | 
| 1f9c | NW8 System fault 32 | 
| 1f9d | NW8 No U-Link communication | 
| 1f9e | NW8 Application error 1 | 
| 1f9f | NW8 Application error 2 | 
| 1fa0 | NW8 Application error 4 | 
| 1fa1 | NW8 Application error 16 | 
| 1fa4 | NW8 Press sensor | 
| 1fa5 | NW8 Duct temperature | 
| 1fa6 | NW8 Minimum flow potentiometer | 
| 1fa7 | NW8 Maximum flow potentiometer | 
| 1fa8 | NW8 Hot water potentiometer | 
| 1fa9 | NW8 Induction auxilary potentiometer | 
| 1faa | NW8 Space setpoint | 
| 1fab | NW8 Space temperature | 
| 1faf | NW8 Sensor failure GCS 01 | 
| 1fc3 | NW8 Sensor failure GCS 02 | 
| 1fd7 | NW8 Sensor failure GCS 03 | 
| 1feb | NW8 Sensor failure GCS 04 | 
| 1fff | NW8 Sensor failure GCS 05 | 
| 2013 | NW8 Sensor failure GCS 06 | 
| 2027 | NW8 Sensor failure GCS 07 | 
| 203b | NW8 Sensor failure GCS 08 | 
| 204f | NW8 Sensor failure GCS 09 | 
| 2063 | NW8 Sensor failure GCS 10 | 
| 2077 | NW8 Sensor failure GCS 21 | 
| 208b | NW8 Sensor failure GCS 22 | 
| 209f | NW8 Sensor failure GCS 23 | 
| 20b3 | NW8 Sensor failure GCS 24 | 
| 20c7 | NW8 Sensor failure GCS 25 | 
| 20db | NW8 Sensor failure GCS 26 | 
| 20ef | NW8 Sensor failure GCS 27 | 
| 2103 | NW8 Sensor failure GCS 28 | 
| 2117 | NW8 Sensor failure GCS 29 | 
| 212b | NW8 Sensor failure GCS 30 | 
| 213f | NW8 Sensor failure GCS 31 | 
| 2150 | NW8 Sensor failure end | 
| 2151 | NW8 Leaves LCM network event | 
| 2152 | NW8 Joins LCM network event | 
| 2153 | NW8 Leaves/joins LCM network | 
| 2197 | NETWORK 8000 message end | 
| 2198 | CWS Method Error | 
| 2199 | CWS Value Poll failed | 
| 219a | CWS Alarm Poll failed | 
| 219b | CWS Browse failed | 
| 219c | CWS GetObject failed | 
| 219d | CWS GetHistory failed | 
| 219e | See gap after 0x200 | 
| 219f | Device address changed | 
| 21A0 | Blacklisted device detected | 
| 21A1 | Local administrator account has empty or default password | 
| 21A2 | X509 certificate error | 
| 21A3 | Web server failure | 
| 21A4 | IO driver unexpectedly timed out | 
| 21A5 | Error - Upgrade using DFU mode | 
| 21A6 | Database file is corrupt | 
| 21A7 | Xenta schedule update failure | 
| 21A8 | Xenta central schedule update failure | 
| 21A9 | SNMP send trap failure | 
| 21AA | Error in retrieving Xenta device Trend Log data | 
| 21AB | Corrupt backup set detected | 
| 21AC | Trend storage capacity reached | 
| 21AD | SmartDriver network configuration invalid | 
| 21AE | An error was found in a communication module during server startup | 
| 21AF | Licensing violation | 
| 21B0 | Notification files storage capacity reached | 
| 21B1 | Driver loading disabled | 
| 21B2 | Sigma RUDs exceeded the network limit | 
| 21B3 | Sigma RUDs exceeded the controller limit | 
| 21B4 | Sigma globals exceeded the network limit | 
| 21B5 | Another server has hosted device | 
| 21B6 | More than one server with the same name in the system | 
| 21B7 | Device model mismatch detected | 
| 21B8 | Unexpected type information | 
| 21B9 | Cloud failure | 
| 21BA | Cloud SystemDiscovery failure | 
| 21BB | Invalid License Server Configuration | 
| 21BC | Server has too many created objects and upgrade is disabled | 
| 21BD | Cloud SMS channel offline | 
| 21BE | Cloud telemetry channel offline | 
| 21BF | Cloud file channel offline | 
| 21C0 | Missing response from server | 
| 21C1 | External storage unavailable | 
| 21C2 | External storage failed to connect | 
| 21C3 | External storage no database schema found | 
| 21C4 | Too many failing attempts to verify signature | 
| 21C5 | External storage incorrect schema version upgrade schema | 
| 21C6 | External storage incorrect schema version upgrade server | 
| 21C7 | Log on failed - authentication | 
| 21C8 | Remote Server does not support transport of 64 bit sequence numbers and needs to be upgraded | 
| 21C9 | Remote Server does not support transport of 64 bit sequence numbers and needs to be upgraded soon | 
| 21CA | Notification error | 
| 21CB | Math expression error | 
| 21CC | Circular binding | 
| 21CD | Email service failed to add attachment | 
| 21CE | MQTT - Failed to connect to broker | 
| 21CF | MQTT - Buffer overflow | 
| 21D0 | Failed to generate PDF | 
| 21D1 | Failed to generate signed PDF - No certificate found | 
| 21D2 | TLS configuration error | 
| 21D3 | Failed to generate signed PDF - No license found | 
| 21D4 | Failed to generate signed PDF - No certificate or license found | 
| 21D5 | External storage merge log failed source log not found | 
| 21D6 | External storage merge log failed target log not found | 
| 21D7 | Failed to generate signed PDF - Signing process timeout | 
| 21D8 | Log processing error - Loop detected | 
| 21D9 | Alarm buffer full | 
| 21DA | Invalid certificate for https communication | 
| 21DB | Insight sensor frame error | 
| 21DC | Federation - SAML - Service does not exist | 
| 21DD | Federation - SAML - Service could not be launched | 
| 21DE | Semantic DB has default admin password | 
| 21DF | Semantic DB query failed | 
| 21E0 | Semantic DB offline | 
| 21E1 | Semantic DB authentication failure | 
| 21E2 | Semantic DB timeout query | 
| 21E3 | Semantic DB timeout search | 
| 21E4 | Semantic DB timeout export | 
| 21E5 | Semantic DB timeout update | 
| 21E6 | Semantic DB timeout update file | 
| 21E7 | Semantic DB backup failed | 
| 21E8 | Federation - SAML - Configuration Synchronization Failed | 
| 21E9 | Failed to get platform property | 
| 21EA | Failed to set platform property | 
| 21EB | Insufficient Function Block Program engine version detected | 
| 21EC | Log on failed - account has been temporarily locked | 
| 21ED | Semantic DB no valid license | 
| 21EE | Schedule evaluation overrun | 
| 21EF | Device backup to flash disabled | 
| 4000 | Unknown fault | 
| 4001 | Unknown maintenance | 
| 4002 | Anytype config, not found | 
| 4003 | Address found, no config | 
| 4004 | Beam sensor local test fail | 
| 4005 | Beam sensor remote test fail | 
| 4006 | Memory fault in unit | 
| 4007 | Sounder fault in unit | 
| 4008 | Beacon fault in unit | 
| 4009 | Sounder and beacon fault in unit | 
| 400A | Fault in unit | 
| 400B | Remote LED config, not supported | 
| 400C | Battery missing | 
| 400D | Unit fault | 
| 400E | Head missing | 
| 400F | Sounder missing | 
| 4010 | Tamper | 
| 4011 | Signal strength | 
| 4012 | Battery fault | 
| 4013 | CO element fault | 
| 4014 | Heat element fault | 
| 4016 | Sensor and module unit have same address | 
| 4017 | Double address | 
| 4018 | Bad scan response of device | 
| 4019 | Comm. error frame ID vs mem. ID | 
| 401A | Protocol family vs config. | 
| 401B | Double address (SLC) | 
| 401C | Double address (LC and SLC) | 
| 401D | Module subaddress overlap | 
| 401E | Configured, not found | 
| 401F | Device internal error | 
| 4020 | Open circuit in loop | 
| 4021 | Short circuit in loop | 
| 4022 | Earth leakage fault (positive) | 
| 4023 | Earth leakage fault (negative) | 
| 4024 | Loop scanning trouble | 
| 4025 | PS mains fault | 
| 4026 | PS charger fault | 
| 4027 | PS charger overvoltage fault | 
| 4028 | PS battery low voltage fault | 
| 4029 | PS battery fault | 
| 402A | Device detached and attached | 
| 402B | Open circuit in monitored input | 
| 402C | Short circuit in monitored input | 
| 402D | Voice evac. fault input activated | 
| 402E | Fault input activated | 
| 402F | Fire router fault | 
| 4030 | Fault router fault | 
| 4031 | Extinguisher fault | 
| 4032 | Address configuration missing | 
| 4033 | Text configuration missing | 
| 4034 | Panel configuration missing | 
| 4035 | Multimod. subaddr too high | 
| 4036 | Event register cleared | 
| 4037 | Fire detection unit halted | 
| 4038 | Fire panel restarted | 
| 4039 | Short circuit in MC monitored output | 
| 403A | Open circuit in MC monitored output | 
| 403B | Short circuit in monitored output | 
| 403C | Open circuit in monitored output | 
| 403D | Too old sw version of (monitored output | 
| 403E | Fire alarm device mute input timeout | 
| 403F | Fault in info port comm. | 
| 4040 | Short circuit in module input | 
| 4041 | IO-configuration missing | 
| 4042 | LC communication fault | 
| 4043 | LC communication restarted | 
| 4044 | I/O communication fault | 
| 4045 | I/O communication restarted | 
| 4046 | IOU installation conflict | 
| 4047 | PS communication fault | 
| 4048 | PS communication restarted | 
| 4049 | SA unit | 
| 404A | Configuration information missing | 
| 404B | Fault in MC power output PO | 
| 404C | Fault in PS power output PO | 
| 404D | Fault in power output PO | 
| 404E | Fault in LC power output PO | 
| 404F | LC installation conflict | 
| 4050 | Fault in MC power input PI | 
| 4051 | Connection fault to panel | 
| 4052 | Connection to panel restarted | 
| 4053 | Connection line to panel | 
| 4054 | Panel message queue overflow | 
| 4055 | Incompatible software in panel | 
| 4056 | More than devices of 200-series in the loop | 
| 4057 | Communication failure in loop | 
| 4058 | Info port cannot handle address numbers higher than 255. | 
| 4059 | Extra battery package connection fault | 
| 405A | Extra battery package connection fault | 
| 405B | Extra battery package connection fault | 
| 405C | Extra battery package connection fault | 
| 405D | PS charger temperature fault | 
| 405E | PS unknown HW version | 
| 405F | Too high resistance in loop | 
| 4060 | Resistive load in loop | 
| 4061 | Too high current in loop | 
| 4062 | Too high voltage drop in loop | 
| 4063 | Maintenance service period expired | 
| 4064 | Maintenance input activated | 
| 4065 | Configured not same as found | 
| 4066 | Info external device fault | 
| 4067 | Info external device fault | 
| 4068 | Info external device fault | 
| 4069 | Info transmitter fault | 
| 406A | Info receiver fault | 
| 406B | Info external device fault | 
| 406C | Info external device fault | 
| 406D | Info external device fault | 
| 406E | Info transmitter watchdog fault | 
| 406F | Info receiver watchdog fault | 
| 4070 | Info unknown external device fault | 
| 4071 | User interface communication fault | 
| 4072 | Info device board not installed | 
| 4073 | Active config file content error | 
| 4074 | Active config file open error | 
| 4075 | Active config checksum file open error | 
| 4076 | Active config file checksum error | 
| 4077 | Configuration data missing | 
| 4078 | APU communication fault | 
| 4079 | APU communication restarted | 
| 407A | Short circuit in APU monitored output | 
| 407B | Open circuit in APU monitored output | 
| 407C | APU installation conflict | 
| 407D | Communication missing in APU line | 
| 407E | Communication missing in APU line | 
| 407F | Database out of memory | 
| 4080 | Connection fault in Ethernet line | 
| 4081 | Connection fault in Ethernet line | 
| 4082 | Failed to read factory settings | 
| 4084 | Address not set | 
| 4085 | Too low analog value | 
| 4086 | No/invalid reply from address | 
| 4017 | Double address | 
| 4087 | Break in module input | 
| 4088 | Break in module output | 
| 4089 | Short circuit in mod. output | 
| 402E | Fault input activated | 
| 408A | Zone disabl. time exceeded | 
| 408B | Maint. input activated | 
| 408C | Unknown type of device | 
| 408D | Contaminated detector | 
| 408E | months to CO cl expiration | 
| 408F | Conv.subloop break/shortc. | 
| 4090 | Invalid response from device | 
| 4091 | Device type changed while loop was running | 
| 4092 | Extinguisher input activated | 
| 4093 | Infrared saturation on det. | 
| 4094 | 80% drift limit reached | 
| 4095 | 99% drift limit reached | 
| 4096 | Device removed on loop disab. | 
| 4097 | Unknown fault from device | 
| 4098 | Device mem. write failed | 
| 4099 | Device mem. read failed | 
| 409A | Device comm. trouble | 
| 409B | Device self test failed | 
| 409C | Beam sensor CPU fault | 
| 409D | Beam sensor align targeting | 
| 409E | Beam sensor general fault | 
| 409F | Beam sensor signal too high | 
| 40A0 | Detector CO cell expiration | 
| 40A1 | Device type changed while loop was starting up | 
| 40A2 | ALC SW not compatible | 
| 40A3 | Router fault input activated | 
| 40A4 | Output mod. power failure | 
| 40A5 | Not Esmi device | 
| 40A6 | Output control failure | 
| 40A7 | Device SW not compatible | 
| 40A8 | Isolator disappeared | 
| 40A9 | Isolator appeared | 
| 40AA | New address in the loop | 
| 40AB | Unacceptable device (family) | 
| 40AC | Break in CLC input | 
| 40AD | Short circuit in CLC input | 
| 40AE | Voltage problem in CLC input | 
| 40AF | VoiceEvac mute input timeout | 
| 40B0 | Unit memory checksum | 
| 40B1 | Beam sensor signal blocked | 
| 40B2 | Simulated maint/serv command | 
| 40B3 | Simulated fault/serv command | 
| 40B4 | Fire | 
| 40B5 | Local fire | 
| 40B6 | Coincidence fire | 
| 40B7 | Delayed fire |