These Central IO modules combine 8 universal inputs and 4 analog outputs. You can use these modules when an application requires only a few I/O points of each type. The universal inputs can be used for any mix of temperature, pressure, flow, status points, and similar inputs. The analog outputs can be used to control a wide range of devices, such as valves and actuators, using a 0-10 VDC control signal.
Module names with an -H indicate the presence of Hand-Off-Auto override switches.
The following input types are supported:
Digital (dry contact, open collector, or open drain)
Counter (dry contact, open collector, or open drain)
Supervised
Voltage (0–10 VDC)
Current (0–20 mA)
Temperature (supports several different thermistor types)
Resistive
The following output type is supported:
Voltage (0–10 VDC)
Each universal input channel has a dedicated two-color (red and green) status LED that provides local monitoring of the input. You can configure the channel status LED for a digital or counter input to display either red or green for each input state. Each analog output channel has an override switch and an adjustable potentiometer. The front panel contains the I/O channel and module status LEDs, the override switches, and the potentiometers.
The universal inputs (UI) are designed to read several different types of inputs.
Input types:
Digital
Counter
Supervised
Voltage
Current
Temperature
Resistive
Applied voltages beyond the absolute maximum ratings will cause over current in the protection component DZ.
The I/O bus in the terminal base provides the Central IO module with power and an address.
The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the Central IO module and the automation server.
The external connection of a digital input is shown in the following figure.
K is the monitored external switch.
VS = 24 V
RPU = 10 kohm
A counter input uses the same hardware configuration as the digital input that is shown in the figure above.
Supervised inputs are contact closing inputs supplemented with the supervision of the field wiring integrity. This supervision is a required feature in many security system applications. The supervised inputs provide the ability to detect specific forms of tampering or trouble with the wire connections to the field contacts. The supervision is achieved with a combination of 1 or 2 resistors attached to the contact in the field. The resistor combination creates continuous current flow through the field contact loop and presents a defined set of expected resistance values for each of the defined conditions. If someone is attempting to defeat the monitoring of the field contact by short circuiting the wire with a jumper or cutting the wire, the objective is to detect and indicate such a condition. The resistors need to be located at the end of the cable close to the field contact, so that the point where there is a risk that the circuit is defeated is between the resistors and the I/O.
Three different types of supervised input connections are supported:
Series only
Parallel only
Series and parallel
Each type of supervised input connection provides a different capability in regards to what form of tamper/trouble can be detected regardless of switch contact open or closed condition.
Series only: A single resistor, which is connected in series with the switch, can only detect tamper/trouble in the form of a short circuit across the wire pair. A single series resistor supervision is frequently configured with a normally closed field contact. This provides for the short circuit to be detected and a cut wire will show as an alarm condition. The external connection of a series only supervised input connection is shown in the following figure.
K is the monitored external switch.
RS = 1 to 10 kohm
VS = 5 V
RPU = 10 kohm
Parallel only: A single resistor, which is connected in parallel with the switch, can only detect tamper/trouble in the form of an open circuit in the field wiring loop. With single parallel resistor supervision and use of a normally open switch in the field, the opened wiring shows as a fault and the shorted wiring shows as an alarm condition. The external connection of a parallel only supervised input connection is shown in the following figure.
K is the monitored external switch.
RP = 1 to 10 kohm
VS = 5 V
RPU = 10 kohm
Series and parallel: Two resistors, where one is connected in series with the switch and one is connected in parallel with the switch, can detect tamper/trouble conditions in the form of both an open and a shorted circuit. The external connection of a series and parallel supervised input connection is shown in the following figure.
K is the monitored external switch.
RP = RS ± 5 %, 1 to 10 kohm
VS = 5 V
RPU = 10 kohm
The external connection of a voltage input is shown in the following figure.
VG is the monitored external voltage (0 to 10 VDC).
RIN = 1 Mohm
The external connection of a current input is shown in the following figure.
IG is the monitored external current (0 to 20 mA).
RSH = 47 ohm
In the internal configuration of the current input, there is a current limit circuit in order to protect the shunt resistor from over load. The input current is limited to 40 mA with a serial connected FET transistor. If this limit is reached for 0.5 seconds, the transistor is turned off. When 5 seconds have elapsed, the transistor is turned on again to make a new start attempt.
The external connection of a temperature input is shown in the following figure.
RT is the monitored external thermistor.
When a universal input is used as a temperature input, VS and RPU in the internal configuration of the universal input are used according to the following table.
Thermistor type | VS | RPU |
20 kohm | 5 V | 10 kohm |
10 kohm | 5 V | 10 kohm |
2.2 kohm | 1 V | 1.5 kohm |
1.8 kohm | 1 V | 1.5 kohm |
1 kohm | 1 V | 1.5 kohm |
The resulting voltage across the thermistor is measured and a temperature is calculated dependent on the selected thermistor type.
The external connection of a resistive input is shown in the following figure.
RM is the monitored external resistance.
VS = 5 V
RPU = 10 kohm
The analog outputs (AO) are designed to be used for voltage outputs (VO).
ROUT is approximately equal to 10 ohm.
VOUT range is 0 to 10 VDC.
RLOAD minimum is 5 kohm.
The I/O bus in the terminal base provides the Central IO module with power and an address.
The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the Central IO module and the automation server.
|
Input channels
|
8
|
|
Output channels
|
4
|
|
DC input supply power
|
1.0 W
|
|
DC input supply voltage
|
24 VDC
|
| Environment | |
|
Ambient temperature, operating
|
0 to 60 °C (32 to 140 °F)
|
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
|
Maximum humidity
|
95 % RH non-condensing
|
| Material | |
|
Plastic flame rating
|
UL94 V-0
|
|
Ingress protection rating
|
IP 20
|
| Mechanical | |
|
Dimensions including terminal base
|
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
|
|
|
|
|
Terminal base
a
|
TB-IO-W1-2
|
| a) Existing TB-IO-W1 terminal bases can be used with UI-8/AO-V-4-2 and UI-8/AO-V-4-H-2. | |
| UI-8/AO-V-4-2 | |
|
Weight including terminal base
|
0.259 kg (0.570 lb)
|
|
Weight excluding terminal base
|
0.136 kg (0.299 lb)
|
| UI-8/AO-V-4-H-2 | |
|
Weight including terminal base
|
0.265 kg (0.583 lb)
|
|
Weight excluding terminal base
|
0.142 kg (0.313 lb)
|
| Universal inputs | |
|
|
|
|
Absolute maximum ratings
|
-0.5 to +24 VDC
|
|
A/D converter resolution
|
16 bits
|
| Digital | |
|
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
|
Minimum pulse width
|
150 ms
|
|
LED polarity
|
Software selectable, if the LED is activated when the input is high or low
|
|
LED color
|
Red or green, software selectable
|
| Counter | |
|
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
|
Minimum pulse width
|
20 ms
|
|
Maximum frequency
|
25 Hz
|
|
LED polarity
|
Software selectable, if the LED is activated when the input is high or low
|
|
LED color
|
Red or green, software selectable
|
| Supervised | |
|
5 V circuit, 1 or 2 resistors
|
|
|
Monitored switch combinations
|
Series only, parallel only, and series and parallel
|
|
Resistor range
|
1 to 10 kohm
|
| For a 2-resistor configuration, each resistor must have the same value +/- 5 % | |
| Voltage | |
|
Range
|
0 to 10 VDC
|
|
Accuracy
|
+/-(7 mV + 0.2 % of reading)
|
|
Resolution
|
1.0 mV
|
|
Impedance
|
1 Mohm
|
| Current | |
|
Range
|
0 to 20 mA
|
|
Accuracy
|
+/-(0.01 mA + 0.4 % of reading)
|
|
Resolution
|
1 μA
|
|
Impedance
|
47 ohm
|
| Resistive | |
|
10 ohm to 10 kohm accuracy
|
+/-(7 + 4 x 10
-3
x R) ohm
|
| R = Resistance in ohm | |
|
10 kohm to 60 kohm accuracy
|
+/-(4 x 10
-3
x R + 7 x 10
-8
x R
2
) ohm
|
| R = Resistance in ohm | |
| Temperature | |
|
Range
|
-50 to +150 °C (-58 to +302 °F)
|
| Supported thermistors | |
|
Honeywell
|
20 kohm
|
|
Type I (Continuum)
|
10 kohm
|
|
Type II (I/NET)
|
10 kohm
|
|
Type III (Satchwell)
|
10 kohm
|
|
Type IV (FD)
|
10 kohm
|
|
Type V (FD w/ 11k shunt)
|
Linearized 10 kohm
|
|
Satchwell D?T
|
Linearized 10 kohm
|
|
Johnson Controls
|
2.2 kohm
|
|
Xenta
|
1.8 kohm
|
|
Balco
|
1 kohm
|
| Measurement accuracy | |
|
20 kohm
|
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
|
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F) |
|
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F) |
|
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F) |
|
|
10 kohm, 2.2 kohm, and 1.8 kohm
|
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
|
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F) |
|
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F) |
|
|
Linearized 10 kohm
|
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
|
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F) |
|
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F) |
|
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F) |
|
|
1 kohm
|
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
|
| Analog outputs, AO | |
|
|
|
| Voltage | |
|
Range
|
0 to 10 VDC
|
|
Accuracy
|
+/-60 mV
|
|
Resolution
|
10 mV
|
|
Minimum load resistance
|
5 kohm
|
|
Load range
|
-1 to +2 mA
|
|
Terminals
|
Voltage Output (VO), Return (RET)
|