Part number: SXWTBIOW110002
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
Device | Part number |
SpaceLogic TB-IO-W1-2 Terminal Base | SXWTBIOW110002 |
SpaceLogic DI-16 | SXWDI16XX10001 |
SpaceLogic UI-16-2 | SXWUI16XX10002 |
SpaceLogic RTD-DI-16 | SXWRTD16X10001 |
SpaceLogic DO-FA-12 | SXWDOA12X10001 |
SpaceLogic DO-FA-12-H | SXWDOA12H10001 |
SpaceLogic DO-FC-8 | SXWDOC8XX10001 |
SpaceLogic DO-FC-8-H | SXWDOC8HX10001 |
SpaceLogic AO-8 | SXWAO8XXX10001 |
SpaceLogic AO-8-H | SXWAO8HXX10001 |
SpaceLogic AO-V-8 | SXWAOV8XX10001 |
SpaceLogic AO-V-8-H | SXWAOV8HX10001 |
SpaceLogic UI-8/DO-FC-4-2 | SXWUI8D4X10002 |
SpaceLogic UI-8/DO-FC-4-H-2 | SXWUI8D4H10002 |
SpaceLogic UI-8/AO-4-2 | SXWUI8A4X10002 |
SpaceLogic UI-8/AO-4-H-2 | SXWUI8A4H10002 |
SpaceLogic UI-8/AO-V-4-2 | SXWUI8V4X10002 |
SpaceLogic UI-8/AO-V-4-H-2 | SXWUI8V4H10002 |
TB-IO-W1-2 can also be used with UI-16, UI-8/DO-FC-4(-H), UI-8/AO-4(-H), and UI-8/AO-V-4(-H).
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
| Operation environment | |
|
Ambient temperature, operating
|
0 to 60 °C (32 to 140 °F)
|
|
Humidity
|
Maximum 95 % RH non-condensing
|
| Mechanical | |
|
Ingress protection rating
|
IP 20 (with I/O module installed)
|
|
Plastic flame rating
|
UL94 V-0
|
| Electrical | |
|
I/O bus power
|
24 VDC
|
Max. 20 W per I/O bus powered by AS-P-3 |
|
Max. 30 W per I/O bus powered by PS-24V |
|
|
Maximum addresses per I/O bus
|
32
|
| DI-16 Module | |
|
DC input power
|
24 VDC
|
|
Input rating
|
24 V, 2.4 mA
|
|
Channels
|
16 input
|
| UI-16-2 Module | |
|
DC input power
|
24 VDC
|
|
Input rating
|
24 V, 2.4 mA
|
|
Channels
|
16 input
|
| RTD-DI-16 Module | |
|
DC input power
|
24 VDC
|
|
Input rating
|
24 V, 2.4 mA
|
|
Channels
|
16 input
|
| DO-FA-12(-H) Module | |
|
DC input power
|
24 VDC
|
|
Relay contact rating
|
250 VAC
|
Pilot Duty (Power Factor 0.35) |
|
|
Channels
|
12 output
|
| DO-FC-8(-H) Module | |
|
DC input power
|
24 VDC
|
|
Relay contact rating
|
250 VAC
|
Pilot Duty (Power Factor 0.35) |
|
|
Channels
|
8 output
|
| AO-8(-H) Module | |
|
DC input power
|
24 VDC
|
|
Voltage output rating
|
0 to 10 VDC
|
|
Current output rating
|
0 to 20 mA, 650 ohm (max.)
|
|
Channels
|
8 output
|
| AO-V-8(-H) Module | |
|
DC input power
|
24 VDC
|
|
Voltage output rating
|
0 to 10 VDC
|
|
Channels
|
8 output
|
| UI-8/DO-FC-4(-H)-2 Module | |
|
DC input power
|
24 VDC
|
|
Relay contact rating
|
250 VAC
|
Pilot Duty (Power Factor 0.35) |
|
|
Input rating
|
24 V, 2.4 mA
|
|
Channels
|
4 output/8 input
|
| UI-8/AO-4(-H)-2 Module | |
|
DC input power
|
24 VDC
|
|
Voltage output rating
|
0 to 10 VDC
|
|
Current output rating
|
0 to 20 mA, 650 ohm (max.)
|
|
Input rating
|
24 V, 2.4 mA
|
|
Channels
|
4 output/8 input
|
| UI-8/AO-V-4(-H)-2 Module | |
|
DC input power
|
24 VDC
|
|
Voltage output rating
|
0 to 10 VDC
|
|
Input rating
|
24 V, 2.4 mA
|
|
Channels
|
4 output/8 input
|