earth_america
user_standard Log on
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: FDP Server
Functionalities: Engineering
6/10/2026

Zone disables

Note:

It is advisable to keep, for example, manual call points enabled, even if smoke detectors are disabled to avoid nuisance alarms.

You can select how a disablement of the zone, to which the address belongs, affects the address.

Option

Description

Nothing

Zone disablement has no effect on the address.

Address

The address is disabled when the zone to which it belongs is disabled. The disablement affects all functionality of the address. Sensor input, fault monitoring and output control are all disabled.

Fire detection/input

The address is partly disabled when the zone to which it belongs is disabled. The disablement affects the detector input, that is, fire detection. If the address is an I/O module, the disablement affects the configured input function.

Fault monitoring and output functions are not affected. This means, for example, that there is an indication on the panel if the detector is removed.