Faults and Maintenance Alerts

Faults and maintenance alerts comprise a text and a code. They are displayed on the panel, in EcoStruxure Fire Expert, and in EcoStruxure Fire Operation.

Warning Warning

COMPROMISED FUNCTIONALITY

  • If fault 328 Factory Settings: Failed to read factory settings is displayed, abort the commissioning.

  • Do not use the panel.

  • Contact your local Customer Care Center about the fault.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

The panel has not initialized correctly if fault 328 occurs. The message is displayed only once and does not reappear after it has been reset.

Table: Faults and Maintenance Alerts

Number/Alarm text/Code

Type

Text/System alarm ID

Description

Unknown fault

An undefined fault has been detected in EcoStruxure™ Fire Operation.

Unknown maintenance

An undefined maintenance issue has been detected in EcoStruxure™ Fire Operation.

0

Maintenance

Anytype config, not found

An "anytype" addressable detector or device is configured but not found.

NOTE: This message is displayed only once and does not reappear after it has been reset.

1

Maintenance

Address found, no config.

An addressable detector or device is found but not configured.

NOTE: This message is displayed only once and does not reappear after it has been reset.

2

Maintenance

Configured, not found

The configured device is not found.

Install a device corresponding to the configuration or change the configuration.

3

Maintenance

Configured not same as found

The configured type and found type of device differ.

Install the correct type of device or change the configuration.

5

Maintenance

Address not set

An addressable device has a zero address.

Attend to the cause of the incorrect address.

6

Fault

Unknown type of device

Unknown type of device installed on the loop. The address is not polled anymore. During normal operation only in ELC.

7

Fault

Device removed on loop disab.

Addressable device removed during loop disablement. The panel detects the fault when the loop is enabled again.

If the panel has not been configured: Restart the panel to update the loop database on the MCU Main Controller Unit.

8

Fault

Device type changed while loop was starting up

Addressable device type changed during loop disablement.

If the panel has not been configured: Restart the panel to update the loop database on the MCU Main Controller Unit.

9

Fault

New address in the loop

New addresses identified after panel start-up.

NOTE: This message is displayed only once and does not reappear after it has been reset.

11

Maintenance

Remote LED config, not supported

Output function is configured for an SLC addressable detector, but the installed addressable detector does not support this feature.

13

Fault

Double address

Two or more ALC or ELC addressable devices are assigned the same address.

14

Maintenance

Bad scan response of device

The panel received an incomplete response from an ALC addressable device.

15

Maintenance

Comm. error frame ID vs mem. ID

The type ID is not compatible with the memory ID of an ALC addressable device.

16

Maintenance

Protocol family vs config.

The family of an ALC addressable device does not match the configuration (S90/XP95/Discovery).

17

Fault

Double address (SLC)

Two or more Ap (SLC) addressable devices are assigned the same address. The LEDs on affected addressable devices are on.

18

Fault

Double address (LC and SLC)

Two or more Series 200 Advanced or Clip (SLC) addressable devices are assigned the same address.

19

Maintenance

Module subaddress overlap

The sub-address of a multimodule overlaps with the sub-address of another addressable device.

20

Fault

Device internal error

An internal error in an Ap SLC or ELC addressable device. Internal error faults in Esmi Impresia Conventional zone modules can be caused by internal communication issues or power interruptions to the conventional line.

21

Maintenance

Device detached and attached

An Ap SLC or ELC addressable device is disconnected and connected to the loop while the loop is powered up.

22

Fault

Multimod. subaddr too high

A sub-address of a multimodule is out of the address range. The maximum number of sub-addresses is 250 for ELC and 159 for SLC.

23

Fault

Short circuit in module input

Short circuit in the input circuit of an Ap SLC or ELC input module.

51

Fault

Too low analog value

The value received from an addressable detector is too low or the detector has an internal fault.

Values that trigger this fault depend on the type, family/series and manufacturer of the addressable detector.

52

Fault

No/invalid reply from address

A bad or an incomplete reply from an address.

53

Fault

Double address

Two or more addressable devices are assigned the same address.

54

Fault

Break in module input

A break in the input circuit of an input module.

55

Fault

Break in module output

A break in the output circuit of an output module.

56

Fault

Short circuit in mod. output

A short circuit in the output circuit of an output module.

57

Fault

Fault input activated

Input function for an input module is configured as Fault warning input . If the input activates, the panel indicates this fault.

58

Fault

Zone disabl. time exceeded

Input function for an input module is configured as Zone disablement input . If the maximum disablement time is exceeded, the panel indicates this fault.

59

Maintenance

Maint. input activated

Input function for an input module is configured as Maintenance warning input . If the input activates, the panel indicates this maintenance alert.

60

Maintenance

Contaminated detector

A dirty smoke detector. Smoke detectors have a drift compensation algorithm. When the smoke sensor reading exceeds the compensated limit, the panel indicates this maintenance alert. This maintenance alert can only be reset when the smoke sensor reading drops below the limit.

To find contaminated smoke detectors, log in to access level 3. Navigate to Tests > Report dirty detectors (level 3) and press the Activate the test button. If any detectors have reached their contamination limits, a maintenance alert is displayed.

61

Maintenance

6 months to CO cl expiration

The cell life of a sensor in a COPTIR detector expires in six months.

62

Fault

Conv.subloop break/shortc.

A break or short circuit in a conventional sub-loop of a conventional zone module.

63

Fault

Invalid response from device

Invalid response from an addressable device. Invalid responses can, for example, be caused by unstable readings from Ap SLC addressable devices, and SLC beam detectors 6500 in alignment mode.

Values that trigger this fault depend on the type, family/series and manufacturer of the addressable detector.

64

Fault

Device type changed while loop was running

An addressable device was replaced during normal operation. The device type or family does not match the configuration.

65

Fault

Remote LED config, not supported

Output function is configured for an addressable detector, but the installed addressable device does not support this feature.

If an addressable detector was replaced, this is indicated with fault 64.

NOTE: The System alarm ID text for this fault is not reflected in EcoStruxure™ Fire Operation. It says Unknown fault there.

66

Fault

Extinguisher input activated

Input configured as Extinguisher fault warning input . If the input activates, the panel indicates this fault.

67

Maintenance

Infrared saturation on det.

The infrared sensor in a COPTIR/PTIR detector has reached its saturation point.

68

Maintenance

80% drift limit reached

80% of the drift limit reached. Can be indicated after a user activates Report dirty detectors (level 3) .

69

Maintenance

99% drift limit reached

99% of the drift limit reached.

70

Fault

Unknown fault from device

An unknown fault in an addressable device.

71

Fault

Device mem. write failed

Could not write to the memory of an addressable device.

72

Fault

Device mem. read failed

Could not read from the memory of an addressable device.

73

Fault

Device comm. trouble

Unsuccessful communication with an addressable device.

74

Fault

Device self test failed

The internal test of an addressable device was unsuccessful.

75

Fault

Beam sensor CPU fault

A CPU fault in a beam detector.

76

Fault

Beam sensor align targeting

A beam detector has an alignment fault.

77

Fault

Beam sensor general fault

A beam detector has a general fault.

78

Fault

Beam sensor signal too high

The signal of a beam detector is too strong.

79

Fault

Detector CO cell expiration

The cell life of a sensor in a COPTIR detector has expired.

80

Fault

ALC SW not compatible

The software of an ALC2 Loop Controller is not compatible with the desired sounder mode.

81

Fault

Router fault input activated

Input module configured as Fault warning in fire alarm router input . If the input activates, the panel indicates this fault.

82

Fault

VoiceEvac fault input act.

Input module configured as Voice evacuation fault warning input . If the input activates, the panel indicates this fault.

NOTE: The System alarm ID text for this fault is not reflected in EcoStruxure™ Fire Operation. It says Unknown fault there.

84

Fault

Output mod. power failure

A power supply failure in the monitored output circuit of an output module.

85

Fault

Not Esmi device

The OEM code of an addressable device is incompatible.

86

Fault

Output control failure

Control of the output of an addressable device did not work.

87

Fault

Device SW not compatible

The software version of the addressable device is incompatible.

88

Maintenance

Isolator disappeared

An addressable device with a short circuit isolator was replaced with an addressable device without a short circuit isolator.

89

Maintenance

Isolator appeared

An addressable device without a short circuit isolator was replaced with an addressable device with a short circuit isolator.

90

Fault

Unacceptable device (family)

An addressable device is not a part of the Intellia family. The device can only be used with a special configuration license.

92

Fault

Break in CLC input

Break in an input line of a CLC Conventional Line Controller.

93

Fault

Short circuit in CLC input

Short circuit in an input line of a CLC Conventional Line Controller.

94

Fault

Voltage problem in CLC input

Voltage problem in an input line of a CLC Conventional Line Controller.

95

Fault

VoiceEvac mute input timeout

Maximum time for muting voice evacuation has been reached.

96

Fault

Unit memory checksum

Memory checksum of an addressable device is incomplete.

97

Fault

Beam sensor signal blocked

The signal of a beam detector is blocked. The receiver does not receive signals.

98

Maintenance

Simulated maint/serv command

A command has activated a simulated maintenance alert.

99

Fault

Simulated fault/serv command

A command has activated a simulated fault.

100

Fault

Beam sensor local test fail

A locally activated test alarm of a beam detector was unsuccessful.

101

Fault

Beam sensor remote test fail

A remotely activated test alarm of a beam detector was unsuccessful.

102

Fault

Memory fault in unit

A memory fault in an addressable device.

103

Fault

Sounder fault in unit

A sounder in an addressable device does not work correctly.

104

Fault

Beacon fault in unit

A beacon does not work correctly.

105

Fault

Sounder and beacon fault in unit

Sounder and beacon not working as expected.

106

Fault

Fault in unit

An internal fault in a sounder beacon.

110

Fault

Battery missing

A battery is missing from an XPander series ALC addressable detector.

111

Fault

Unit fault

Internal fault in an XPander series ALC addressable device.

112

Fault

Head missing

An XPander series ALC addressable detector has been removed from the base.

113

Fault

Sounder missing

An XPander series ALC sounder has been removed from the base.

114

Fault

Tamper

Tamper fault in an XPander series ALC addressable detector.

115

Fault

Signal strength

The signal strength of an XPander series ALC addressable detector is too low.

117

Fault

Battery fault

The battery power of an XPander series ALC addressable detector is too low.

118

Fault

CO element fault

Carbon monoxide element fault in a detector.

119

Fault

Heat element fault

Heat element fault in a detector.

120

Fault

Sensor and module unit have same address

200

Fault

Open circuit in loop

201

Fault

Short circuit in loop

202

Fault

Earth leakage fault (positive)

203

Fault

Earth leakage fault (negative)

204

Fault

Loop scanning trouble

205

Fault

PS mains fault

206

Fault

PS charger fault

207

Fault

PS charger overvoltage fault

208

Fault

PS battery low voltage fault

209

Fault

PS battery fault

210

Fault

Open circuit in monitored input

211

Fault

Short circuit in monitored input

212

Fault

Voice evac. fault input activated

213

Fault

Fault input activated

214

Fault

Fire router fault

215

Fault

Fault router fault

216

Fault

Extinguisher fault

217

Fault

Address configuration missing

218

Fault

Text configuration missing

219

Fault

Panel configuration missing

220

Fault

Event register cleared

221

Fault

Fire detection unit halted

222

Fault

Fire panel restarted

223

Fault

Short circuit in MC monitored output

224

Fault

Open circuit in MC monitored output

225

Fault

Short circuit in monitored output

226

Fault

Open circuit in monitored output

227

Fault

Too old sw version of (monitored output

228

Fault

Fire alarm device mute input timeout

229

Fault

Fault in info port comm.

231

Fault

IO-configuration missing

232

Fault

LC communication fault

233

Fault

LC communication restarted

234

Fault

I/O communication fault

235

Fault

I/O communication restarted

236

Fault

IOU installation conflict

237

Fault

PS communication fault

238

Fault

PS communication restarted

239

Fault

SA unit

240

Fault

Configuration information missing

241

Fault

Fault in MC power output PO

242

Fault

Fault in PS power output PO

243

Fault

Fault in power output PO

244

Fault

Fault in LC power output PO

245

Fault

LC installation conflict

246

Fault

Fault in MC power input PI

248

Fault

Connection fault to panel

249

Fault

Connection to panel restarted

250

Fault

Connection line to panel

251

Fault

Panel message queue overflow

252

Fault

Incompatible software in panel

255

Fault

More than 20 devices of 200-series in the loop

256

Fault

Communication failure in loop

257

Fault

Info port cannot handle address numbers higher than 255.

258

Fault

Extra battery package 1 connection fault

259

Fault

Extra battery package 2 connection fault

260

Fault

Extra battery package 3 connection fault

261

Fault

Extra battery package 4 connection fault

262

Fault

PS charger temperature fault

263

Fault

PS unknown HW version

264

Fault

Too high resistance in loop

265

Fault

Resistive load in loop

266

Fault

Too high current in loop

267

Fault

Too high voltage drop in loop

290

Maintenance

Maintenance service period expired

291

Maintenance

Maintenance input activated

300

Fault

Info external device fault 0

301

Fault

Info external device fault 1

302

Fault

Info external device fault 2

303

Fault

Info transmitter fault 3

304

Fault

Info receiver fault 4

305

Fault

Info external device fault 5

306

Fault

Info external device fault 6

307

Fault

Info external device fault 7

308

Fault

Info transmitter watchdog fault 8

309

Fault

Info receiver watchdog fault 9

310

Fault

Info unknown external device fault

311

Fault

User interface communication fault

312

Fault

Info device board not installed

313

Fault

Active config file content error

314

Fault

Active config file open error

315

Fault

Active config checksum file open error

316

Fault

Active config file checksum error

317

Fault

Configuration data missing

318

Fault

APU communication fault

319

Fault

APU communication restarted

320

Fault

Short circuit in APU monitored output

321

Fault

Open circuit in APU monitored output

322

Fault

APU installation conflict

323

Fault

Communication missing in APU line 1

324

Fault

Communication missing in APU line 2

325

Fault

Database out of memory

326

Fault

Connection fault in Ethernet line 0

327

Fault

Connection fault in Ethernet line 1

328

Fault

Failed to read factory settings

See the warning at the beginning of this section.

329

Maintenance

EcoStruxure Fire Operation Default password not changed

330

Maintenance

EcoStruxure Fire Operation Not running