earth_america
user_standard Log on
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: FDP Server
Functionalities: Engineering
6/2/2025

ALC, SLC, ELC and LC input functions

Day mode is intended to be changed a few times a day. When day mode has been enabled or disabled, you cannot immediately toggle it again.

Warning Warning

UNEXPECTED DAY MODE STATUS

  • Wait at least one minute before you toggle day mode again after you have enabled or disabled it.

  • Verify that the panel has the correct day mode status.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Toggling day mode generates numerous event messages. Consequently the fire detection panel rejects any requests to toggle day mode for a minute after it has been changed. The aim is to avoid overloading communication lines in the fire detection system.

In the address table, double-click the cell in the Input function column to see a menu of the available input functions.

Table: ALC, SLC, LC Conventional zone module

Input function

Description

Conventional zone input

Fire alarm

Beam detector input

Fire alarm

Table: ALC Wireless loop interface

Input function

Description

Wireless expander input

Transfers communication between the panel and wireless devices

Table: Other ALC, SLC, ELC and LC devices

Input function

Description

Not in use

None

Conventional line input

Fire alarm

Customer LED 1 activation input

Lights up the ‘Customer LED 1’ indicator

Customer LED 2 activation input

Lights up the ‘Customer LED 2’ indicator

Day mode enable input

Sets this panel and its visible panels in day mode

Day mode and delayed alarm enable input

Sets this panel and its visible panels in day mode and enables delayed alarms

Delayed alarm enable input

Enables delayed alarms for this panel and its visible panels

Delayed alarm zonal reset input

Resets delayed alarms in the same zone as the monitor module

Delayed alarm zonal silence input

Silences delayed alarms in the same zone as the monitor module

Evacuation activation input

Activates all alarm devices of this panel and its visible panels

External logic input

Provides a signal to an external control logic

Extinguisher activated input

Lights up the ‘Extinguisher Activated’ indicator

Extinguisher fault warning input

Activates a fault with the ‘Extinguisher fault’ indication

Fault warning input

Activates a fault

Fire alarm device mute input

Temporarily mutes (disables) the fire alarm devices of this panel and its visible panels when a Voice Evacuation message is announced

Fire alarm input

Fire alarm

General reset input

Resets the highest priority alarms

General silence input

Silences the highest priority alarms

Internal logic input

Provides a signal to the built-in control logic

Local day mode enable input

Sets this panel in day mode

Local day mode and delayed alarm enable input

Sets this panel in day mode and enables delayed alarms

Local delayed alarm enable input

Enables delayed alarms for this panel

Local evacuation activation input

Activates all alarm devices of this panel

Local fire alarm device mute input

Temporarily mutes (disables) fire alarm devices of this panel when a Voice Evacuation message is announced

Maintenance warning input

Maintenance alert

Manual call point

Fire alarm

Prealarm input

Pre-alarm

Silent technical alarm input

Technical alarm, excluding the buzzer

Smoke ventilation activated input

Activates the Smoke vents activated LED on the panel

Technical alarm input

Technical alarm

Voice evacuation fault warning input

Activates a fault with the ‘Voice evac. fault input activated’ indication

Zone disablement input

Disables the zone to which the module is configured