How to

How to


Products: Enterprise Central, Enterprise Server, Esmi Sense FDP
Functionalities: Trends
12/3/2024

Configuring a Multi Trend Log List 

You configure a multi trend log list to display values from multiple trend logs in one list so that you can compare the values, for example, when commissioning or validating an EcoStruxure BMS.

Important:

When you configure a multi trend log list, the changes override all configurations on the individual trend log series in the multi trend log list.

Show More
action_close

You configure a multi trend log list to display values from multiple trend logs in one list. You compare values in a multi trend log list when you commission or validate an EcoStruxure BMS.

For example, on a b3 BACnet device, there are two inputs: SpaceTemp and SpaceHumidity. Both inputs have logs set up intrinsically. You want to print the last 3 days of history for these inputs. You create a multi trend log list for both inputs. You can export the multi trend log list to a .CSV file or an .XML file, or .XLSX file, and then use an external editor to compare the values.

If a trend log has no available value for a given time stamp in a multi trend log list, then the trend log displays an empty cell for that specific time. You can fill that empty cell with the latest known value.

You can change the column order in the multi trend log list and save the change.

You can add, edit, or remove trend logs from the multi trend log list at any time. You can also edit how trend logs are displayed in the multi trend log list. For more information, see Configuring a Trend Log Series in a Multi Trend Log List  .

Tip:

You can add a trend log to a multi trend log list using drag and drop.

You can configure the individual trend log series in a multi trend log list.

Important:

All configurations on individual trend log series are overriden if you configure the multi trend log list.

Temporary multi trend log list

You can view a group of trend log lists in a atemporary multi trend log list without creating a multi trend log list. For more information, see Viewing Trend Logs in a Temporary Multi Trend Log List  .

Multi trend log lists in WebStation

Multi trend log list can be created and viewed in WebStation. Note that the setting Log space (records) is disregarded by WebStation. When viewed in WebStation, WebStation will always display all values in the multi trend log list regardless of the Log space (records) setting.

Time Zone Modes in a Trend Log List

​In a trend log list, you can present the records of a trend log in different time zones: local time zone, EcoStruxure BMS server time zone, and UTC time zone.

For more information, see Time Zone Modes in a Trend Log List .

Calculation Methods

​Use a calculation method to process the records of the trend log before presenting them in a trend log list or a trend chart. The original records in the trend log are not affected by the calculation method. The calculation method is applied to the trend log records grouped by a specific time interval.

For more information, see Calculation Methods .

Important:

If you have selected a calculation method on a series, event icons are not displayed on that series in the multi trend log list.

Floating Point Values NaN, INF, and -INF

In the EcoStruxure BMS software, the floating point values “Not a Number”, positive infinity, or negative infinity may be displayed in the Basic property tab, in a trend log list, or a trend chart.

For more information, see Floating Point Values NaN, INF, and –INF .

To configure a Multi Trend Log List 
  1. In WorkStation, in the System Tree pane, select the multi trend log list you want to configure.

  2. Click the Open multi trend log list settings button

     
    action_zoom_plus_stroke
    .

  3. Configure the properties on the General tab.

    Table: Multi Trend Log Settings – General Tab

    Property

    Description

    Log space (records)

    ​Select the maximum number of records to display in the list.

    Time zone

    Select the time zone in which the log records are presented.

    Calculation method

    Select a calculation method.

    For more information, see Calculation Methods .

    Delta over period

    Select True to apply a period to the delta calculation method.

    For more information, see Calculation Methods .

    Period  

    Select the time span for which the calculation method is to be executed.

    Custom period

    Enter a custom time span for which the calculation method is to be executed.

    Custom period alignment

    Enter the time when you want the custom period to start.

  4. Click OK .

  • Multi Trend Log Lists
  • Time Zone Modes in a Trend Log List
  • Calculation Methods
  • Adding a Trend Log to a Multi Trend Log List 
  • Configuring a Trend Log Series in a Multi Trend Log List 
  • Removing a Trend Log from a Multi Trend Log List 
  • Exporting a Multi Trend Log List to .XML 
  • Exporting a Multi Trend Log List to .CSV 
  • Exporting a Multi Trend Log List to .XLSX
  • Multi Trend Log Settings Dialog Box – General Tab
  • Multi Trend Log Settings Dialog Box – Series Tab
  • Multi Trend Log List Series Properties
  • Multi Trend Log List Properties - Basic Tab