How to

How to


Products: Enterprise Central, Enterprise Server, FDP Server
Functionalities: Alarms
12/3/2024

Checking the Integrity of an Alarm

You check the integrity of an alarm to verify that the path is valid.

Show More
action_close

When an alarm is triggered it appears in the alarm list. You can acknowledge, disable, or hide alarms in the alarm list. An acknowledged alarm disappears from the alarm list when it has been reset to normal state.

When the alarm database gets corrupted after an EcoStruxure BMS server crash, all alarms are re-evaluated. The alarms that are still active are resent to the alarm database. However, the information that an alarm has been acknowledged, disabled, or hidden is lost, and you have to repeat operations you performed on the alarm before the data loss.

When an alarm has been triggered and reset to normal state without having been acknowledged, the alarm remains in the alarm list until it is acknowledged. If the alarm is lost, an alarm refresh does not make the alarm reappear in the alarm list. The alarm is reset and has no alarm state to send.

Most system information alarms are only messages. These alarms cannot be in an alarm state, thus, an alarm refresh does not make the system information alarms reappear in the alarm list.

To check the integrity of an alarm
  1. In Workstation log on to the server that has the alarms you want to check.

    Important:

    You start with the server that is the lowest in the hierarchy.

  2. In the System Tree pane, select System , and then select Alarm Control Panel.

  3. In the Actions menu, click Advanced , and then click Alarms integrity check .

  • Alarm Handling Issues
  • Alarm Cannot be Acknowledged Due to Invalid Paths