earth_america
user_standard Log on
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
How to

How to


Products: Enterprise Central, Enterprise Server, FDP Server
Functionalities: Alarms
12/3/2024

Displaying Alarm Limits in a Trend Chart

You display alarm limits in a trend chart when you want to see the limits where the alarm triggers for the values that are presented in the chart.

Show More
action_close

You can display alarm limits for a value displayed in a trend chart in WebStation.

The value displayed in the trend log must be monitored by an alarm. The alarm must have the limit configured.

You cannot edit, or change, the displayed alarm in the properties for the trend chart or trend log. However, if you edit the limits in the alarm, the new limits are displayed in the chart.

If more than one alarm is monitoring the value that is displayed in the trend chart, the limits for all alarms are displayed. If many values are displayed in the chart and every value is monitored by an alarm with limits, all alarm limits are displayed in the trend chart.

To display alarm limits in a trend chart
  1. In WebStation, in the System Tree pane, select the trend chart.

  2. On the Trend Chart toolbar, click the Show alarm guides button

     
    action_zoom_plus_stroke
    .

  • Display Alarm Limits in a Trend Chart in WebStation
  • Trend Chart Toolbar in WebStation