How to

How to


Products: Enterprise Central, Enterprise Server, Esmi Sense FDP
Functionalities: Trends
12/3/2024

Configuring an Extended Trend Log

You configure the properties of an extended trend log to meet the unique needs of your site.

Show More
action_close

You use an extended trend log to store records from a trend log. An extended trend log can be connected to a trend log or connected in a series to another extended trend log. Only one extended trend log can be connected to a trend log​ or another extended trend log.

You create and configure extended trend logs from WorkStation.

Important:
  • The extended trend log cannot log a variable.

  • The extended trend log gets the initial value of the connected trend log.

  • Do not connect more than one extended trend log to a trend log or another extended trend log. If a trend log is connected to two or more extended trend logs, critical conflicts can occur.

  • The extended trend log must have the same unit as the monitored trend log to correctly display values.

 
action_zoom_plus_stroke Do not connect more than one extended trend log to a trend log or extended trend log.
Figure: Do not connect more than one extended trend log to a trend log or extended trend log.

The extended trend log is often saved on an Enterprise Server or an Enterprise Central with more storage capacity than the field server where the ordinary trend log is saved. This extra storage capacity enables the Enterprise Server or Enterprise Central to store more records before it overwrites old ones. The extended trend log can be viewed in a trend log list or a trend chart.

You can configure the extended trend log to transfer data several ways: Smart log, percentage, time interval, or force transfer.

Table: Extended Trend Log Transfer Criteria

Function

Explanation

Smart log

Automatically updates the transfer rate with respect to the frequency of records, network speed, and the capacity of the EcoStruxure BMS server that runs the trend log and the extended trend log.

Threshold

Transfers records every time a specific percentage threshold of records on the trend log is reached.

Maximum transfer interval

Transfers records at a specific time interval even though the threshold or Smart log condition is not reached.

Transfer trigger variable

Transfers records when triggered by a variable that changes state from false to true, for example, a digital schedule. The transfer takes place regardless of the transfer threshold. This function can be used to ensure that the extended trend log contains all records, for example, to generate a complete report at the end of every month.

Force transfer

Executed by the user to manually force a transfer even though transfer threshold is not reached.

When you create extend trend logs for BACnet or Xenta trend logs, be sure to create the extended trend log on the same EcoStruxure BMS server that hosts the BACnet or Xenta device and its trend log. This ensures that they remain synchronized in the event the server needs to be restored.

For more information, see Extended Logging for External BACnet Trend Logs Workflow .

 
action_zoom_plus_stroke Extended trend log that transfers records from a trend log each time the trend log exceeds a record volume of 20% or every hour.
Figure: Extended trend log that transfers records from a trend log each time the trend log exceeds a record volume of 20% or every hour.

When you edit a record in the extended trend log, the changes do not affect the connected trend log. If you edit a record in the trend log, the changes are transferred to the extended trend log next time a transfer occurs. You can edit both the trend log and the corresponding record in the extended trend log, but the edit is written twice in the extended trend log record under certain circumstances:

  • the record in the extended trend log is manually updated

  • the corresponding edit is transferred from the trend log to the extended trend log

The trend log list or trend chart displays the last written value of an edited record.

Example 1: You edit a record in a trend log that is connected to an extended trend log. The extended trend log is updated with the edited record. After the transfer, you update the corresponding record in the extended trend log. The trend log list and trend chart connected to the extended trend log display the last value of the record, which in this case is the extended trend log edit.

Example 2: You edit a record in a trend log that is connected to an extended trend log. Before the extended trend log is updated with the edited record, you edit the corresponding record in the extended trend log. After a while the trend log transfers its edited record to the extended trend log. The trend log list and trend chart connected to the extended trend log display the edited trend log record value and not the edited extended trend log record value. In this case, the trend log list and trend chart display the last value that was written to the extended trend log, not the last edited value.

You can view all edits, automatically transferred or manually added, in the record history.

Archive Overview

Archiving is the process of preserving historical data, which is comprised of selected events and extended trend logs. For example, some facilities are required to maintain archives to comply with government regulations. Another example is in secure facilities where they must maintain records of who logged in or who changed setpoints. Archiving is not a backup function because archive data cannot be imported back into the system.

For more information, see Archiving Overview .

Extended Trend Log Meter Support

You can view the meter properties of the connected trend log, if the meter function is enabled on the connected trend log. For more information, see Meter Function .

To configure an extended trend log
  1. In WorkStation, in the System Tree pane, select the extended trend log you want to configure.

  2. On the File menu, click Properties .

  3. In the properties dialog box, click the Basic tab.

  4. Edit the basic properties:

    Table: Extended Trend Log Properties - Basic Tab

    Component

    Description

    Monitored trend log

    Enter the path to the trend log you want to transfer records from.

    Unit

    The unit of an extended trend log created from the trend log wizard at the same time as the connected trend log inherits the unit of measurement from the connected trend log.

    The unit of an extended trend log that is manually connected to a trend log needs to be manually configured to use the same unit of measurement as the connected trend log.

    Smart log

    Select True to optimize the transfer of the monitored trend log to the extended trend log.

    Threshold

    Select the percentage threshold at which the trend log transfers its records to the extended trend log.

    Maximum transfer interval

    Select the maximum length of time that can pass between transfers from the monitored trend log to the extended trend log.

    Transfer trigger variable

    Enter a trigger variable to force a transfer of all records from the trend log to the extended trend log, for example, to generate a complete report.

    For more information, see Extended Trend Logs .

    Log size

    Select the number of records to store before old records are overwritten, including internal records generated by the trend log.

    For more information, see Log Record Storage .

    Include in report s

    Select True to include the extended trend log data in reports.

  5. Click the Meter Info tab.

  6. View the meter properties:

    Table: Meter Info Tab

    Property

    Description

    Is meter log

    Displays True if the trend log meter function is active.

    For more information, see Meter Function .

    Meter change time

    Displays the time when the meter was changed.

    Meter change user

    Displays the name of the user account that changed the meter.

    End time

    Displays the time when the old meter was replaced.

    End value

    Displays the value the old meter had when it was replaced.

    Start time

    Displays the time when the new meter was installed.

    Start value

    Displays the value of the new meter when it was installed.

    Meter constant

    Displays the constant of the new meter. If the meter counts in kilo (10 3 ), the constant is 1000.

    Min value

    Displays the first value of the new meter after roll-over.

    Max value

    Displays the last value of the new meter before roll-over.

    Note:

    Meter properties are only available if the meter properties of the connected trend log are active.

  7. Click OK .

  • Extended Trend Logs
  • Extended Trend Log Properties – Basic Tab
  • Trend Units
  • Log Record Storage
  • Meter Function
  • Configure Dialog Box – Operation Tab
  • Configure Dialog Box – Configuration Tab
  • Editing the Threshold Property of an Extended Trend Log
  • Editing the Maximum Transfer Interval Property of an Extended Trend Log
  • Editing the Log Size for a Trend Log
  • Editing an Extended Trend Log to be Included in Reports