earth_america
user_standard Log on
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: Enterprise Central, Enterprise Server, Esmi Sense FDP
Functionalities: Alarms
12/3/2024

Extended Acknowledgement

When you select the acknowledgement type Extended acknowledgment, the user needs to acknowledge the alarm in the alarm view in reset state, before the alarm returns to normal state and disappears from the alarm view.

If the user acknowledges the alarm when it is in alarm state, the alarm is set to acknowledged state. When the problem that triggered the alarm is corrected, that is when the monitored variable no longer meets the criteria to trigger the alarm, the alarm is set to reset state. The user needs to acknowledge the alarm in reset state to make it return to normal state.

 
action_zoom_plus_stroke Extended acknowledgement loop where the alarm reset state has to be acknowledged before the alarm returns to normal state
Figure: Extended acknowledgement loop where the alarm reset state has to be acknowledged before the alarm returns to normal state

If the user did not acknowledge the alarm when it was in alarm state and the monitored variable no longer meets the criteria to trigger the alarm, the alarm is set to reset state. The user needs to acknowledge the alarm in reset state to make it return to normal state. In this case, the alarm can toggle between alarm state and reset state several times before a user acknowledges the alarm.

 
action_zoom_plus_stroke Extended acknowledgement loop where the alarm toggles between alarm state and reset state
Figure: Extended acknowledgement loop where the alarm toggles between alarm state and reset state
  • Acknowledgements
  • Alarm Functions
  • Alarm States
  • Alarms Overview
  • Create Alarm Wizard – User Action Page
  • Configuring the Acknowledgement Type of an Alarm
  • Alarm Handling Issues