earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifications

Specifications


Products: RP-C
Functionalities: Engineering, Hardware
Product version: 3.1
6/14/2022

RP-C

 
action_zoom_plus_stroke RP-C
Figure: RP-C

Introduction

SmartX IP Controller – RP-C is a room-purpose, fully programmable, IP based field controller that suits a wide range of HVAC applications. The RP-C can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with a SmartX AS-P or AS-B server or an Enterprise Server as the parent server. The RP-C features a wireless chip that allows the mobile commissioning application and the mobile application for room comfort settings to connect directly to the controller.

The RP-C has the following features:

  • IP enabled with dual-port Ethernet switch

  • Full range of controller models

  • Versatile onboard I/O point mix

  • Optional covers

  • Wireless connectivity

  • Highly available

  • Sensor bus for living space sensors

  • Room bus for connected room solutions

  • Engage mobile application for room comfort settings

  • Mobile commissioning application

  • Full EcoStruxure Building Operation software support, providing efficient engineering tools

IP connectivity and flexible network topologies

The SmartX IP controllers are based on open protocols that simplify interoperability, IP configuration, and device management:

  • IP addressing

  • BACnet/IP communications

  • DHCP for easy network configuration

The SmartX IP controllers have a dual-port Ethernet switch, which enables flexible network topologies:

  • Star

  • Daisy chain

  • Rapid Spanning Tree Protocol (RSTP) ring

In a star topology, the controller and the parent EcoStruxure BMS server are individually connected to an Ethernet switch. Daisy-chain multiple controllers together to reduce installation time and cost. Use an RSTP ring topology when you want a non-operational controller to be detected and recovered quickly and efficiently.

Full range of controller models

The RP-C comes in four different models, which offer four different sets of I/O point types, named 12A, 12B, 12C, and 16A. The RP-C-12A, -12B, and -12C models support 24 VAC/DC power supply, whereas the RP-C-16A model is a 230 VAC model.

 
action_zoom_plus_stroke

Fully programmable

The fully programmable RP-C models provide flexibility through support of both Script and Function Block programming options. The RP-C promotes efficiency and standardization through the use of standard controller applications.

Models with a versatile mix of I/O points

The RP-C-12A, -12B, -12C, and -16A models provide 12 or 16 I/O points, consisting of four different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.

Table: I/O Point Types by RP-C Models

I/O Point Types

RP-C-12A model

RP-C-12B model

RP-C-12C model

RP-C-16A model

Universal I/O

Type Ub

8

8

4

8

Solid-state relay outputs

(MOSFET)

4

-

4

4

Relay outputs

Form A

-

3

3

3

High power relay outputs

Form C

-

1

1

1

Table: Configurations by I/O Point Types

Configurations

Universal I/O

Type Ub

Solid-state Relay Outputs

(MOSFET)

Relay Outputs

Form A

High Power Relay Outputs

Form C

Digital inputs

yes

-

-

-

Counter inputs

yes

-

-

-

Supervised inputs

yes

-

-

-

Voltage inputs

(0 to 10 VDC)

yes

-

-

-

Current inputs

(0 to 20 mA)

yes

-

-

-

Temperature inputs

yes

-

-

-

Resistive inputs

yes

-

-

-

2-wire RTD temperature inputs

yes

-

-

-

Voltage outputs

(0 to 10 VDC)

yes

-

-

-

Digital outputs

-

yes

yes

yes

Digital pulsed outputs

-

yes

yes

yes

PWM outputs

-

yes

yes

yes

Tristate outputs

-

yes

yes

-

Tristate pulsed outputs

-

yes

yes

-

Universal inputs/outputs

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs are capable of supporting analog outputs of type voltage outputs. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs should be connected to the controller universal inputs/outputs.

Solid-state relay outputs

The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.

Relay outputs

The relay outputs support digital Form A point types. The Form A relays are designed for direct load applications.

High power relay output

The high power relay output is of type Form C. The normally-open (NO) contact is ideal for switching resistive loads of up to 12 A, such as electrical heating elements. The normally-closed (NC) contact can be used to switch inductive loads of up to 3 A.

Optional covers

All RP-C models can be equipped with optional covers to reduce access to the screw terminals and wires.

 
action_zoom_plus_stroke RP-C with equipped with optional covers
Figure: RP-C with equipped with optional covers

Wireless connectivity

RP-C is a Bluetooth Low Energy (BLE) enabled product. You can use this wireless connectivity option to connect the RP-C with a smartphone or tablet running the eCommission SmartX Controllers mobile application or the Engage mobile application for room comfort settings.

Highly available

The SmartX IP controllers support local trends, schedules, and alarms, enabling local operation when the controller is offline or used in standalone applications.

The battery-free power backup of the memory and real-time clock helps prevent data loss and allows seamless and quick recovery after a power disruption.

In WorkStation, you update the firmware of multiple SmartX IP controllers at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the controllers and sensors. The server can host controllers of different firmware versions.

Sensor bus for living space sensors

The SmartX IP controllers provide an interface designed for the SmartX Sensor family of living space sensors. The SmartX Sensors offer an efficient way to sense the temperature, humidity, CO 2 , and occupancy in a room. The SmartX Sensors are available with different combinations of sensor types and various covers and user interface options, such as touchscreen, setpoint and override buttons, and blank covers.

 
action_zoom_plus_stroke SmartX Sensors
Figure: SmartX Sensors

The sensor bus provides both power and communications for up to four sensors that are daisy-chained using standard Cat 5 (or higher) cables. The maximum number of sensors that can be connected to a controller varies depending on the sensor model and the combination of cover and sensor base type:

  • Blank covers: Up to four sensors of any combination of sensor base types

  • 3-button and touchscreen covers:

    • Up to two sensor bases with CO 2 option

    • Up to four sensor bases without CO 2 option

  • SmartX LCD temperature sensors: Up to four sensors are supported

The maximum total length of the sensor bus is 61 m (200 ft). For more information, see the SmartX Living Space Sensors Specification Sheet.

Engage mobile application

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP-C controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Room bus for connected room solutions

The RP-C provides a room bus, which allows RP Series expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, and control of lights and window blinds.

The RP-C room bus supports up to six connected RP Series expansion modules and multi-sensors with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two multi-sensors

Maximum total length of the room bus is 72 m (236 ft).

For more information, see the RP-C-EXT-DALI-M-PD, RP-C-EXT-0-10V-4-PD, RP-C-EXT-BL-4-HV-PD, RP-C-EXT-BL-2-LV-PD, and RP-C-EXT-MS-BLE Specification Sheets.

Mobile commissioning application

The eCommission SmartX Controllers mobile application is designed for local configuration, field deployment, and commissioning of SmartX IP controllers. The mobile application reduces the commissioning time, allows flexibility in project execution, and minimizes dependencies on network infrastructure.

The mobile application is designed for use with Android, Apple (iOS), and Microsoft Windows 10 devices. For more information, see the eCommission SmartX Controllers Specification Sheet.

 
action_zoom_plus_stroke eCommission SmartX Controllers mobile app
Figure: eCommission SmartX Controllers mobile app

Using the eCommission SmartX Controllers mobile application, you can connect to one or many RP-Cs. You can connect to a single RP-C using the controller's built-in Bluetooth connectivity or using the eCommission Bluetooth Adapter connected to a SmartX Sensor. Using a wireless access point or a network switch, you can connect to a network of RP-Cs on the local IP network.

Device configuration

With the eCommission SmartX Controllers mobile application, you can easily discover SmartX IP controllers on the IP network. You can change the configuration of each controller, including the BACnet and IP network settings, location, and parent server. To save engineering time, you can save common device settings and then reuse them for controllers of the same model.

Field deployment and I/O checkout

The eCommission SmartX Controllers mobile application does not require an EcoStruxure BMS server or a network infrastructure to be in place. You can use the mobile application to load the controller application directly into the local SmartX IP controller and deploy the controller. The controller application can be created offline using Project Configuration Tool or WorkStation. You can use the mobile application to change the behavior of an installed standard controller application, such as configuring temperature setpoints. You can also perform an I/O checkout to verify that the controller's I/O points are configured, wired, and operating correctly.

Full EcoStruxure Building Operation software support

The power of the RP-C controller is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:

  • WorkStation/WebStation interface

  • Script and Function Block programming options

  • Device discovery

  • Engineering efficiency

  • Preconfigured HVAC applications

WorkStation/WebStation interface

WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor the SmartX IP controller and its I/O as well as its attached SmartX Sensors. For more information, see the WorkStation and WebStation specification sheets.

Script and Function Block programming options

The fully programmable RP-C controller models have both Script and Function Block programming options. Existing programs can easily be reused between the EcoStruxure BMS server and the controller.

Device discovery

The enhanced Device Discovery in WorkStation enables you to easily identify SmartX IP controllers on a BACnet network and to associate the controllers with their parent server.

Engineering efficiency

The engineering and maintenance of SmartX IP controllers can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete controller application that contains programs and all necessary objects such as trends, alarms, and schedules. The controller application in the Custom Types library is reusable across all controllers of the same model. You can use the controller application as a base for creating new controllers intended for similar applications. You can then edit the controller application, and the changes are automatically replicated to all controllers, while each controller keeps its local values.

WorkStation supports both online and offline engineering of SmartX IP controllers. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the controllers later.

Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the SmartX IP controllers before you deploy your server and controller applications to the servers and controllers on site. For more information, see the Project Configuration Tool specification sheet.

Preconfigured HVAC applications

To improve engineering efficiency and standardize engineering practices, fully designed and tested HVAC applications are available at bms-applications.schneider-electric.com for use with RP-C. This library contains applications for different RP-C models and application types, such as fan coil units and ceiling solutions. These preconfigured HVAC applications are packages that include all software programs, graphics, alarms, and documentation such as functional specifications and I/O wiring schedules needed for your projects. The online repository can be accessed using common web browsers on Windows PCs as well as mobile devices running Apple iOS 11.3 (or later) and Android 6.0 Marshmallow (or later). The download page provides an application selector to help you download an application that meets the needs for a specific room solution with regards to application type, actuator type, fan control type, and sensor type. You can search and view the applications without having to log on to the online repository. To download or email an application, you need to log on or have a valid subscription through single sign-on via a Schneider Electric Exchange account. Before you make your choice, you can view all assets included in the application package. You can download or email an export file, an image file, a selection of the available files, or the whole package. The export file is used when you deploy RP-C from WorkStation, while the image file is used when you deploy RP-C from the eCommission SmartX Controllers mobile app. Subscribe to the application to get a notification when the application is updated.

 
action_zoom_plus_stroke Download page application selector
Figure: Download page application selector

Table: Part Numbers

Product

Part number

RP-C-12A-F-24V
SXWRCF12A10001
RP-C-12B-F-24V
SXWRCF12B10001
RP-C-12C-F-24V
SXWRCF12C10001
RP-C-16A-F-230V
SXWRCF16A10002
Optional covers
SXWRPCCOV10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
eCommission Bluetooth Adapter
SXWBTAECXX10001

For more information on part numbers for Network Connectivity Accessories, see section “SmartX IP Controllers – Accessories” in the For more information, see Product Selection Guide - EcoStruxure Building ..

Specifications

AC input
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
23 VA
Power input protection
MOV suppression and internal fuse
RP-C-16A-F-230V
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 VA
Power input protection
MOV suppression and internal fuse
  
Separate PTC thermistor used as a resettable fuse for 24 VAC Out only
Overvoltage category
III
Pollution degree
2
DC input
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Nominal voltage
24 to 30 VDC
Operating voltage range
23 to 33 VDC
Maximum power consumption
14 W
Power input protection
MOV suppression and internal fuse
AC output
RP-C-16A-F-230V
Type
Isolated output
Nominal voltage
24 VAC
Frequency
Same frequency as the power supply (50/60 Hz)
Output power rating
19 VA
Environment
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
RP-C-16A-F-230V
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-C-12A-F-24V
0.370 kg (0.816 lb)
Weight, RP-C-12B-F-24V and RP-C-12C-F-24V
0.390 kg (0.860 lb)
Weight, RP-C-16A-F-230V
0.720 kg (1.587 lb)
Weight, optional covers
0.070 kg (0.154 lb)
Installation
DIN rail or flat surface
Terminal blocks
Fixed
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Software compatibility
EcoStruxure Building Operation software
version 3.1 and later
Agency compliances
RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V
Emission
RCM; BS/EN 61000-6-3; BS/EN 50491-5-2; FCC Part 15, Subparts B and C, Class B
Immunity
BS/EN 61000-6-2; BS/EN 50491-5-3
Radio
EN 300 328 V2.1.1
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN 50491-3; UL 916 C-UL US Listed a
FCC ID
DVE-RPC24
ISED certification number
IC: 24775-RPC24
Fire performance in air-handling spaces a
UL 2043
a) The RP-C-12A, -12B, and -12C models are approved for plenum applications.
RP-C-16A-F-230V
Emission
RCM; EN 61000-6-3; EN 50491-5-2
Immunity
BS/EN 61000-6-2; BS/EN 50491-5-3
Radio
EN 300 328 V2.1.1
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN 50491-3
Energy
eu.bac Certified Product (Licence No. 219832); BS/EN 15500
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
Sensor bus
24 VDC, 2 W, RS-485 (RJ45)
Sensor bus protection
Transient voltage suppressors on communication and power signals
Room bus
24 VDC, 3 W, RS-485 (RJ45)
Room bus protection
Transient voltage suppressors on communication and power signals
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BTL B-AAC (BACnet Advanced Application Controller) a
Wireless connectivity
Bluetooth Low Energy
Communication protocol
Bluetooth ® 5.0 Low Energy compliant
Frequency
2.402 to 2.480 GHz
Maximum output power
10 dBm
Maximum communication distance
Line-of-sight: 100 m (328 ft)
Antenna
Integrated antenna
RF connector for optional external antenna
SMA connector
External antenna (optional)
Restricted to the approved antenna type listed below (used in certification)

Manufacturer

Model (Part number)

Gain

Type

Impedance

Linx Technologies

ANT-2.4-WRT-MON-SMA

0.8 dBi

Monopole

50 ohm

CPU
Frequency
500 MHz
Type
ARM Cortex-A7 single-core
Internal SRAM
6 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile
Universal inputs/outputs
Channels, RP-C-12A-F-24V
8 Ub, Ub1 to Ub8
Channels, RP-C-12B-F-24V
8 Ub, Ub1 to Ub8
Channels, RP-C-12C-F-24V
4 Ub, Ub1 to Ub4
Channels, RP-C-16A-F-230V
8 Ub, Ub1 to Ub8
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Universal input/output protection
Transient voltage suppressor on each universal input/output
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
1.0 mV
Impedance
100 kohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
RTD temperature inputs
Supported RTDs
Pt1000, Ni1000, and LG-Ni1000
Pt1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

SmartX IP Controller device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +70 °C (-58 to +158 °F)

+/-0.5 °C (+/-0.9 °F)

0 to 50 °C (32 to 122 °F)

70 to 150 °C (158 to 302 °F)

+/-0.7 °C (+/-1.3 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-1.0 °C (+/-1.8 °F)

Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

SmartX IP Controller device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

LG-Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

SmartX IP Controller device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

RTD temperature wiring
Maximum wire resistance
20 ohm/wire (40 ohm total)
Maximum wire capacitance
60 nF
The wire resistance and capacitance typically corresponds to a 200 m wire.
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
5 kohm
Load range
-1 to +2 mA
Relay outputs, DO
Channels, RP-C-12A-F-24V
0
Channels, RP-C-12B-F-24V
3, DO1 to DO3
Channels, RP-C-12C-F-24V
3, DO5 to DO7
Channels, RP-C-16A-F-230V
3, DO5 to DO7
Contact rating
Pilot Duty (C300)
  
Resistive load: 250 VAC/30 VDC, 4 A (cos phi = 1)
  
Inductive load: 250 VAC/30 VDC, 4 A (cos phi = 0.4)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Commons
COM1 for DO1, DO2, and DO3 (on RP-C-12B model)
  
COM3 for DO5, DO6, and DO7 (on RP-C-12C and RP-C-16A models)
Isolation contact to system ground
3,000 VAC
Cycle life
At least 100,000 cycles
Minimum pulse width
100 ms
High power relay outputs, DO
Channels, RP-C-12A-F-24V
0
Channels, RP-C-12B-F-24V
1, DO4
Channels, RP-C-12C-F-24V
1, DO8
Channels, RP-C-16A-F-230V
1, DO8
Contact rating
Pilot Duty (B300)
  
Minimum current: 100 mA (5 VDC)
  
Normally Open contact, resistive load: 250 VAC/24 VDC, 12 A (cos phi = 1)
  
Normally Closed contact, inductive load: 250 VAC/24 VDC, 3 A (cos phi = 0.4)
Switch type
Form C Relay
  
Single Pole Double Throw
  
Normally Open and Normally Closed
Isolation contact to system ground
5,000 VAC
Cycle life
At least 100,000 cycles
Minimum pulse width
100 ms
Solid-state relay outputs, DO
Channels, RP-C-12A-F-24V
4, DO1 to DO4
Channels, RP-C-12B-F-24V
0
Channels, RP-C-12C-F-24V
4, DO1 to DO4
Channels, RP-C-16A-F-230V
4, DO1 to DO4
Output rating
Maximum 2 A load per output
  
Maximum 4 A total load for the 4 outputs
AC voltage range
Maximum 30 VAC
DC voltage range
Maximum 30 VDC
Commons
COM1 for DO1 and DO2 (on RP-C-12A, -12C, and -16A models)
  
COM2 for DO3 and DO4 (on RP-C-12A, -12C, and -16A models)
When the SSR outputs are used to switch AC, the common terminals can be connected to 0 to 30 VAC. When the SSR outputs are used to switch DC, the common terminals can be connected to -30 VDC to +30 VDC.
Common voltage range (AC)
0 to 30 VAC
Common voltage range (DC)
-30 to +30 VDC
Minimum pulse width
100 ms
Solid-state relay output protection
Transient voltage suppressor across each solid-state relay (SSR) output

Terminals

For more information on wiring, see Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-12A model (24 VAC/DC)
Figure: RP-C-12A model (24 VAC/DC)
 
action_zoom_plus_stroke RP-C-12B model (24 VAC/DC)
Figure: RP-C-12B model (24 VAC/DC)
 
action_zoom_plus_stroke RP-C-12C model (24 VAC/DC)
Figure: RP-C-12C model (24 VAC/DC)
 
action_zoom_plus_stroke RP-C-16A model (230 VAC)
Figure: RP-C-16A model (230 VAC)

Table: Part Numbers for SmartX Sensors, Sensor Bases

Product

Part number

Sensor base with temperature sensor

SXWSBTXXXSXX

Sensor base with temperature and humidity sensors

SXWSBTHXXSXX

Sensor base with temperature and CO 2 sensors

SXWSBTXCXSXX

Sensor base with temperature, humidity, and CO 2 sensors

SXWSBTHCXSXX

Table: Part Numbers for SmartX Sensors, Covers

Product

Housing

Part number

Blank cover

Medium matte white

SXWSCBXSELXX

Blank cover

Optimum glass white

SXWSCBXSELXW

Blank cover

Optimum glass black

SXWSCBXSELXB

Blank cover with occupancy sensor

Medium matte white

SXWSCBPSELXX

Blank cover with occupancy sensor

Optimum glass white

SXWSCBPSELXW

Blank cover with occupancy sensor

Optimum glass black

SXWSCBPSELXB

3-button cover

Medium matte white

SXWSC3XSELXX

3-button cover

Optimum glass white

SXWSC3XSELXW

3-button cover

Optimum glass black

SXWSC3XSELXB

3-button cover with occupancy sensor

Medium matte white

SXWSC3PSELXX

3-button cover with occupancy sensor

Optimum glass white

SXWSC3PSELXW

3-button cover with occupancy sensor

Optimum glass black

SXWSC3PSELXB

Touchscreen display cover

Medium matte white

SXWSCDXSELXX

Touchscreen display cover

Optimum glass white

SXWSCDXSELXW

Touchscreen display cover

Optimum glass black

SXWSCDXSELXB

Touchscreen display cover with occupancy sensor

Medium matte white

SXWSCDPSELXX

Touchscreen display cover with occupancy sensor

Optimum glass white

SXWSCDPSELXW

Touchscreen display cover with occupancy sensor

Optimum glass black

SXWSCDPSELXB

Touchscreen display cover with light control buttons

Optimum glass white

SXWSC2XSELXW

Touchscreen display cover with light control buttons

Optimum glass black

SXWSC2XSELXB

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass white

SXWSC2PSELXW

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass black

SXWSC2PSELXB

Touchscreen display cover with light and blind control buttons

Optimum glass white

SXWSC4XSELXW

Touchscreen display cover with light and blind control buttons

Optimum glass black

SXWSC4XSELXB

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass white

SXWSC4PSELXW

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass black

SXWSC4PSELXB

Table: Part Numbers for SmartX Sensors, Combination Models

Product

Housing

Part number

Complete SmartX Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Medium matte white

SXWSATXXXSLX

Complete SmartX Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass white

SXWSATXXXSLW

Complete SmartX Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass black

SXWSATXXXSLB

Complete non-communicating a SmartX Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Medium matte white

SLASXXX

Complete non-communicating a SmartX Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass white

SLAWXXX

Complete non-communicating a SmartX Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass black

SLABXXX

  1. The SmartX resistive temperature sensor (SLA...) is not designed to be connected to the sensor bus. This sensor is connected to I/O points/terminals on the SmartX IP controller using a two-wire connection.
  • Enterprise Server
  • SmartX AS-P Server
  • SmartX AS-B Server
  • WorkStation
  • WebStation
  • RP-C-EXT-DALI-M-PD
  • RP-C-EXT-0-10V-4-PD
  • RP-C-EXT-BL-4-HV-PD
  • RP-C-EXT-BL-2-LV-PD
  • RP-C-EXT-MS-BLE
  • Commission
  • Engage
  • Project Configuration Tool
  • Automated Engineering Tool