Flow Balancer Workflow

Use this workflow to perform flow balance on a single MP-V controller, using the eCommission SmartX Controllers mobile application. Related information can be found in the section after the flowchart.

For more information, see Flow Balancing .

 
action_zoom_plus_stroke Flow Balance workflow
Figure: Flow Balance workflow
Log in and start the eCommission application

Start the eCommission application and log in as either a Technician or Flow Balancer.

For more information, see Downloading and Starting the eCommission SmartX Controllers Mobile Application .

Connect to an MP-V

Discover controllers on the site, and connect to a single MP-V.

For more information, see Device Connection .

Configure air balancing setpoints

You configure the MP-V controller setpoints to set up the parameters by which the controller is flow balanced. These setpoints include the maximum flow setpoint, selected by default, and the intermediate and minimum flow setpoints, which are optional.

For more information, see Configuring MP-V Controller Setpoints .

Balance at setpoints

Using the eCommission application, you flow balance a VAV unit at each designated setpoint to achieve the desired air flow.

For more information, see Flow Balancing at Maximum, Intermediate, or Minimum Flow Setpoint .

Perform manual checkout

After flow balancing the MP-V controller, you can perform manual checkout on two components of the MP-V:

  • Manual checkouts of air flow

    After completing the automated flow balancing process, you can optionally verify and command the air flow values by performing manual checkout.

    For more information, see Performing Manual Checkout of Air Flow .

Generate a flow balance report

After completing flow balancing, you can use the eCommission application to create, append, view, or delete flow balance reports. For more information, see Managing Flow Balance Reports .

  • Flow Balancing
  • Downloading and Starting the eCommission SmartX Controllers Mobile Application
  • Copy Object Type Names
  • Configuring MP-V Controller Setpoints
  • Flow Balancing at Maximum, Intermediate, or Minimum Flow Setpoint
  • Manually Verifying the Direction of Damper Rotation
  • Performing Manual Checkout of Air Flow
  • Managing Flow Balance Reports