earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifications

Specifications


Products: RP-C-EXT-BL-2-LV-PD
Functionalities: Engineering, Hardware
Product version: 3.3
8/1/2023

RP-C-EXT-BL-2-LV-PD

arrow1_rotationIntroduction arrow1_rotationFeatures arrow1_rotationSpecifications arrow1_rotationConnections
 
action_zoom_plus_stroke RP-C-EXT-BL-2-LV-PD – Low-voltage blind module
Figure: RP-C-EXT-BL-2-LV-PD – Low-voltage blind module

Introduction

SpaceLogic* RP-C-EXT-BL-2-LV-PD blind module connects to the SpaceLogic RP room controllers and provides I/O expansion for low-voltage blind control.

The low-voltage blind module enables control and power supply (24 VDC) of motorized window blinds and shutters.

The blind module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

* Formerly known as SmartX.

Features

The low-voltage blind module has the following features:

  • Power and communications through the room bus

  • Two motor control outputs for control of 24 VDC powered blinds (opening, closing, positioning)

  • Four digital inputs for connection of blind switches and window contacts. The digital inputs are SELV (Safety Extra-Low Voltage).

  • Measurement of energy consumption per module

  • Wieland connectors for quick and easy installation

  • Engage mobile application for room comfort settings

  • Status LED for the device

  • One status LED for each blind output

  • Rotary switch for address configuration

Room bus

The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.

The RP-C room bus supports up to six connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of four multi-sensors

Maximum total length of the room bus is 72 m (236 ft).

Engage mobile application

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP-C controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Table: Part Numbers

Product

Part number

RP-C-EXT-BL-2-LV-PD
SXWREB2LVPD10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001

Specifications

Electrical
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Power consumption
75 VA
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Onboard 24 VDC power supply
RP-C-EXT-BL-2-LV-PD has an onboard 24 VDC power supply that is used to power the blind outputs.
Nominal voltage
24 VDC
Maximum supply current
1.3 A
Protection
Short-circuit protection
Environment
Ambient temperature, operating
0 to 40 °C (32 to 104 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.399 kg (0.880 lb)
Installation
DIN rail or flat surface a
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Blind outputs: 2 x 5-pin Wieland GST15i5 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Software compatibility
EcoStruxure Building Operation software
version 3.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN 50491-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN 50491-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN 50491-3
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Blind status indicator
One status LED (green) for each output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Energy metering
Energy consumption measurement
The energy consumption is measured in Wh, shared by the two outputs.
Accuracy class (according to IEC 61557-12)
Active energy measurement: Class 1
Typical measurement accuracy at room temperature
0.5 to 2 W: 5%
  
2 to 30 W: 1%
Blind outputs
Motor control outputs for 24 VDC powered blind motors with automatic end stop detection. An end stop at the top position is required. An end stop at the bottom position is recommended.
Outputs
2, Blind 1 to Blind 2
Output terminals
M- and M+
Power distribution
24 VDC
  
Maximum 1 A load per output
  
Maximum 1.3 A total load for the 2 outputs
  
Maximum 2 A starting current (<100 ms) per output
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Connections

Follow proper installation wiring diagrams and instructions. For more information on wiring, see Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-EXT-BL-2-LV-PD
Figure: RP-C-EXT-BL-2-LV-PD

Table: Required External Connectors

Use

Part number

Reference

Connector type

Suitable for cable diameters

mm (inches)

Marking

Color of coding

/housing

Minimum order quantity

Power supply input

SXWRPCCONWWPOW

91.931.4053.1

Female

5.6–11

(0.22–0.43)

L, PE, N

Black

/Black

100

Blind outputs

SXWRPCCONWBLLV

91.952.4353.0

Male

8.5–12.5

(0.34–0.49)

5, 4, 3, 2, 1

5, 4, 3: Not used

2: M-

1: M+

Light blue

/White

50

Digital inputs

SXWRPCCONWDI

91.921.2353.0

Female

3.4–5.5

(0.14–0.21)

1, 2

1: DI1..4

2: RET

Light blue

/White

100

The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.

Compatibility with the type and characteristics of the blind motors should be verified at an early stage in your project. In case of uncertainty, additional testing may be required.

  • RP-C
  • RP-C-EXT-MS-BLE
  • RP-C-EXT-DALI-M-PD
  • RP-C-EXT-0-10V-4-PD
  • RP-C-EXT-BL-4-HV-PD
  • RP-C-EXT-BL-SMI-2-LV-PD
  • RP-C-EXT-BL-SMI-4-HV-PD
  • RP-C-EXT-DALI
  • RP-C-EXT-0-10V-4
  • RP-C-EXT-REL-4
  • Commission
  • Engage