earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifications

Specifications


Products: AO-8
Functionalities: Central IO , Engineering, Hardware, Smoke Control
Product version: 3.3, 2022, 2023, 2024, 7.0
6/1/2025

AO-8 and AO-8-H

arrow1_rotationIntroduction arrow1_rotationFunction arrow1_rotationSpecifications
 
action_zoom_plus_stroke Central IO modules AO-8 and AO-8-H
Figure: Central IO modules AO-8 and AO-8-H

Introduction

SpaceLogic™ AO-8 and AO-8-H Central IO modules are analog output, 8-channel I/O modules.

The analog outputs are capable of supporting analog voltage or current point types. Therefore, analog outputs support a wide range of devices, such as actuators.

Function

Modular and scalable system

The modules are part of a modular system that delivers power and communications on a common bus. Connecting modules is a one-step process: just slide the modules together using the built-in connectors.

Patented two-piece design

Each module can be separated from its terminal base to allow the site to be wired prior to the installation of the electronics. The patented locking mechanism serves as handles for removing the module from its base. All critical components have a protective cover that permits convection cooling to occur.

 
action_zoom_plus_stroke Two-piece design
Figure: Two-piece design
Hot-connect and Hot-swap

Because critical applications require 24-hour operation, Schneider Electric designed the Central IO modules for hot-connection of terminal bases and hot-swapping of the modules to their bases. This design ensures continuous power and communication during service operations.

Auto-addressing

The auto-addressing feature helps eliminating the need for setting DIP switches or pressing commission buttons. Each module automatically knows its order in the chain and assigns itself accordingly – significantly reducing engineering and maintenance time.

Simple DIN-rail installation

Fasteners easily snap into a locked position for panel installation. The fastener has a quick-release feature for easy DIN-rail removal.

Efficient terminal management

The Central IO module terminals are clearly labeled and protected by transparent covers. The input and output terminals are at the top and bottom of each module and are accessible for maintenance without removing the module. The EcoStruxure Building Operation WorkStation software can generate custom as-built labels for each module. Pre-perforated letter and A4 size label sheets are available as an accessory.

Accommodates multiple row panel installations

The SpaceLogic devices use built-in connectors for single row connectivity, side by side. If a panel size requires multiple rows, extension cords are available.

LED status indicators

The Central IO module has a status indicator that denotes the health and status of the module.

Hand/Off/Auto switches

The front panel of the AO-8-H includes Hand/Off/Auto (HOA) switches to provide override control of the analog outputs.

Each output also has a potentiometer to modulate the output signal when the switch is in the Hand position.

The position of the HOA switch is readable through user interfaces, such as the EcoStruxure Building Operation WorkStation software, enabling more precise monitoring and control.

Protection

Protection components on the analog outputs protect against high-voltage short-duration transient events.

The analog outputs have current limits to protect against permanent short-circuit to ground.

Specifications

Output channels
8
DC input supply power
4.9 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.282 kg (0.62 lb)
Weight excluding terminal base
0.159 kg (0.35 lb)
Terminal base
TB-IO-W1
Agency compliances
Emission
RCM; BS/EN 61000-6-3; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2
Safety standards
BS/EN 61010-1; UL 916 C-UL US Listed
Product
BS/EN 61326-1
Smoke control product safety
UL 864
Part numbers
AO-8, Central IO module
8 analog voltage/current outputs
SXWAO8XXX10001
AO-8-H, Central IO module with HOA switches
8 analog voltage/current outputs with Hand/Off/Auto override switches
SXWAO8HXX10001
TB-IO-W1, terminal base for Central IO module
(Required for each Central IO module)
SXWTBIOW110001
Accessory part numbers
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
PRINTOUT-A4-W1, printout sheets for terminal labels
A4 sheet size, 100 sheets, 18 labels per sheet
SXWTERLBL10011
PRINTOUT-LTR-W1, printout sheets for terminal labels
Letter sheet size, 100 sheets, 16 labels per sheet
SXWTERLBL10012
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
1.5 m
SXWSCABLE10002
S-CABLE-L, S-cable extension cord for the I/O bus, L shaped connectors
0.75 m
SXWSCABLE10003
Analog outputs, AO
 
action_zoom_plus_stroke
Voltage
Range
0 to 10 VDC
Accuracy 
+/-100 mV
Resolution 
42 mV 
Minimum load resistance 
5 kohm 
Load range 
-1 to +2 mA 
Reliability check 
Yes 
Terminals
Voltage Output (VO), Return (RET)
Current
Range
0 to 20 mA
Accuracy 
+/-0.2 mA 
Resolution 
0.1 mA 
Load range 
0 to 650 ohm
Reliability check 
Yes 
Terminals 
Current Output (CO), Return (RET)

For protection from excess current that could be produced by field wiring, follow these instructions:

  • Connect one RET terminal on each of the Central IO modules to a common chassis/power ground rail in the control panel using a size 16 AWG (1.3 mm 2 ), or larger wire.

  • Individual 24 VDC power sources to the field must be current limited to maximum of 4 A for UL compliant installations, and no more than 6 A in other areas.

  • For more information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

  • UI-16
  • DI-16
  • RTD-DI-16
  • AO-V-8 and AO-V-8-H
  • DO-FA-12 and DO-FA-12-H
  • SpaceLogic DO-FC-8 and DO-FC-8-H
  • UI-8/AO-4 and UI-8/AO-4-H
  • UI-8/AO-V-4 and UI-8/AO-V-4-H
  • SpaceLogic UI-8/DO-FC-4 and UI-8/DO-FC-4-H