Hardware Installation Hardware Installation 9/20/2022
Products: AS-B
Functionalities: Hardware
Product version: 2022

SpaceLogic™ AS-B

Regulatory Compliance and Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Technical Literature

  • SpaceLogic Hardware Reference Guide, 04-XX001-XX-en

Dimensions

Installing the Device

Notice

REDUCED DEVICE LIFE SPAN

Install the device on a horizontal DIN rail to provide sufficient cooling air flow through the device.

Failure to follow these instructions can result in reduced life span of the device.

Installing a Terminal Block

Warning Warning

HAZARD OF ELECTRIC SHOCK OR DEVICE ELECTRONICS DAMAGE

Install only a wired terminal block that matches the labeling of the terminals on the device.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Notice

EQUIPMENT DAMAGE

  • Use only terminal blocks delivered with the device or ordered from Schneider Electric using the part number SXWASBCON10001.

  • Do not push the terminal block straight down into the connector header as this may crack the header.

Failure to follow these instructions can result in equipment damage.

Removing a Terminal Block

Labeling the Device

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Notice

EQUIPMENT DAMAGE

Do not connect 230 VAC or 110 VAC to any terminal.

Failure to follow these instructions can result in equipment damage.

Notice

DECREASED RS-485 NETWORK PERFORMANCE

Consider the RS-485 bus termination and biasing. For more information, see the Hardware Reference Guide.

Failure to follow these instructions can result in decreased performance and reliability of the RS-485 network.

Part Numbers

Product

Part number

AS-B-24

SXWASB24X10001

AS-B-24H

SXWASB24H10001

AS-B-24 - P
SXWASB24PX10001
AS-B-24H - P
SXWASB24HP10001

AS-B-36

SXWASB36X10001

AS-B-36H

SXWASB36H10001

AS-B-36 - P
SXWASB36PX10001
AS-B-36H - P
SXWASB36HP10001

AS-B connector kit

SXWASBCON10001

AS-B installer kit

SXWASBINS10001

  • AS-B servers with “H” in the product name are equipped with an override display.

  • AS-B servers with “P” in the product name are hardware only. An AS-B software package needs to be purchased separately for these models. For more information, see the AS-B - SpaceLogic Plant Room Controllers and Servers Specification Sheet.

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

For information on wiring, see the SpaceLogic Hardware Reference Guide.

AS-B Software

The AS-B server is delivered without software. Install the software on the AS-B server using Device Administrator.

Software License Notice

This product contains code that is covered by the GNU General Public License (GPL). The relevant code is available on the Schneider Electric extranet, ecoxpert.se.com

Specifications
AC input
Nominal voltage
24 VAC 50/60 Hz
Recommended transformer rating
≥15 VA
DC input
Nominal voltage
24 to 30 VDC
Power consumption
10 W
Port types
USB device port
Mini-B
USB host port
Type-A
Ethernet port 1 and 2
10/100BASE-TX RJ45
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
IP networking
IP address assignment methods
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
Ua – Universal I/O
Input rating
24 VDC , 2.4 mA
Output rating
0 to 10 VDC , 5 kohm (min.)
Channels
12 (Models with 24 I/O points)
  
20 (Models with 36 I/O points)
Ub – Universal I/O
Input rating
24 VDC , 2.4 mA
Output rating
0 to 10 VDC , 5 kohm (min.)
Channels
4 (Models with 24 I/O points)
  
8 (Models with 36 I/O points)
DO – Relay outputs
Relay contact rating
250 VAC / 30 VDC , 2 A
  
Pilot Duty (C300)
Channels
4
DO – Triac outputs
Triac rating
Max. 30 VAC , 0.8 A
Channels
4 (Models with 36 I/O points)
DI – Digital inputs
Input rating
24 VDC , 2.4 mA
Channels
4 (Models with 24 I/O points)

Addendum - California Proposition 65 Warning Statement for California Residents