earth_america
user_standard Zaloguj się
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Pojęcie

Pojęcie


Produkty: AO-8, AO-V-8, AS-P Smoke Control, Automation Server Smoke Control, DI-16, DO-FA-12, DO-FC-8, Kontrola rozprzestrzeniania się dymu IP-IO, Kontrola rozprzestrzeniania się dymu MP-C, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Funkcje: Smoke Control
Wersja produktu: 2022
2025-01-09

MP-C Controller and IP-IO Module Installation

arrow1_rotationMP-C Controller arrow1_rotationIP-IO Modules arrow1_rotationMP-C Display Module

The MP-C controller and IP-IO module, which are based on the same hardware platform, are installed using either of two methods: they can be snapped onto a DIN rail or screwed onto a flat surface inside a cabinet.

MP-C Controller

The MP-C controller is a multi-purpose, fully programmable, IP-based field controller with a flexible mix of I/O point types that suit a wide range of HVAC applications. The MP-C can be snapped onto a DIN rail or screw-mounted onto a flat surface inside a cabinet. There are 5 models of the MP-C, each equipped with a different quantity of the various I/O point types, as presented in the table below. All models of the MP-C provide a serial port for the sensor bus. This port and the room space sensors connected to it do not participate in smoke control applications. To accommodate the quantity of I/O points available, the MP-C is produced in two different physical sizes. In addition, any MP-C model can be fitted with an optional MP-C Display module, which is designed to be easily field-mounted. See the Display module section for UL 864 requirements related to that device. The MP-C can be applied in dedicated or non-dedicated smoke control applications.

 
action_zoom_plus_stroke MP-C Controller (MP-C-18A model shown)
Rysunek: MP-C Controller (MP-C-18A model shown)
I/O Point Types

The I/O point types and capacities for the various MP-C models are presented in the following table.

Tabela: MP-C Controller Models - I/O Point Types and Capacities

I/O Point Types

MP-C-15A-SMK

MP-C-18A-SMK

MP-C-18B-SMK

MP-C-24A-SMK

MP-C-36A-SMK

Universal I/O type Ub

8

10

10

16

20

Universal I/O type Uc

4

8

Triac outputs

6

4

8

Relay outputs (Form-A)

3

4

8

High power relay outputs (Form-A)

1

1

Universal Inputs and Outputs

All MP-C controller models have Universal I/O points designated as type Ub. The larger models provide additional Universal I/O points designated as type Uc. Both Ub and Uc point types can be configured in the application as any one of the Universal Input modes:

  • Digital Input (with or without circuit supervision)

  • Voltage Input (0 to 10V)

  • Current Input (0 to 20 mA)

  • Temperature Input (Thermistor or RTD sensing element)

  • Resistive Input (0 to 60,000 ohms)

Więcej informacji zawiera I/O Types for Modules and MP Controllers .

Analog Outputs

Type Ub points can be configured as Analog Outputs with 0 to 10 Volt output, in addition to their Universal Input functions. The two larger models, MP-C-24A and MP-C-36A, also feature type Uc points, which in addition to all the features of the type Ub point, can be configured as Analog Outputs with 0 to 20 mA Current output capability.

Digital Outputs

All MP-C controller models provide some number of Digital Outputs in one or more of the types listed in the following table.

Tabela: Digital Output Types for MP-C

Digital Output Types

Description

Triac

All Triac outputs provide an isolated Triac with a common terminal that can be connected to ground for low side switching, or connected to 24 VAC for high side switching. For UL864 applications, the Triac output current limit is derated to 0.25 A maximum (down from the product marking).

Relay outputs (Form-A)

For switching up to 250 VAC/30 VDC, 2 A

High power relay (Form-A)

For switching up to 250 VAC/24 VDC, 12 A

The Triac outputs can be used in many applications to switch up to 30 VAC at 0.25 A, on or off, for external loads such as actuators, relays, or indicators. The relay outputs provide a Form-A, normally open, SPST contact output capable of switching up to 250 VAC or 30 VDC at up to 2 A, or for versions with a single high-power relay, 250 VAC or 24 VDC, up to 12 A.

The relay outputs on MP-C controllers (and all other MP controller models) are rated for switching Nonpower-Limited circuits (up to 250 VAC). This feature is not typically applied in the United States, but when the relays are used to switch Nonpower-Limited circuits (>30 VAC), you must provide a minimum of ¼ inch separation between them and any Power-Limited circuits. When using the relays to switch both Power-Limited and Nonpower-Limited circuits, you must leave a vacant (unused) relay output terminal separating the two types of circuits in order to achieve the ¼ inch requirement at the terminal block entry. An exception is the high-power relay, which can be used with either power type, regardless whether there is an adjacent 2 A relay output in use.

All MP-C models are designed to operate on a supply voltage of 24 VAC or 24 to 30 VDC. However, for UL864 applications, all MP-C models must operate from 24 VAC, using one of the transformers listed in this guide. The DC power input, and the associated DC power sources required for those inputs, have not been evaluated and approved by UL864.

Mounting Dimensions

Tabela: MP-C Controller Mounting Dimensions

Model

Dimensions

MP-C-15A, MP-C-18A, MP-C-18B

153 W x 110 H x 64 D mm (6.0 W x 4.3 H x 2.5 D in.)

MP-C-24A, MP-C-36A

234 W x 110 H x 64 D mm (9.2 W x 4.3 H x 2.5 D in.)

 
action_zoom_plus_stroke MP-C Controller Mounting Dimensions
Rysunek: MP-C Controller Mounting Dimensions
Mounting Orientation

For the UL864 applications discussed in this guide, the MP-C controllers must be mounted in the common horizontal orientation as seen in the image above. This restriction is related to compliance with internal component temperatures required by UL864 derating for increased reliability.

Mounting on DIN Rail

Mounting the MP-C on a DIN rail is a simple, three-step, snap-on process, as illustrated below.

 
action_zoom_plus_stroke MP-C Installation on a DIN Rail
Rysunek: MP-C Installation on a DIN Rail
Mounting Inside an Enclosure

The MP-C can also be installed with screws on a flat surface inside a cabinet. Więcej informacji zawiera SpaceLogic MP-C-SMK Models Controller Models Installation Sheet GDE7787601-01 / 02-20041-02-en ., which includes a full-scale template for the required screw mounting holes.

MP-C-15A-SMK I/O Terminals

Model MP-C-15A-SMK has 15 I/O points, comprised of 8 Universal I/O (type Ub), 6 Triac DO outputs, and 1 High Power Relay (Form-A) DO output. This controller is equipped with 6 pluggable terminal blocks and 1 fixed terminal block.

 
action_zoom_plus_stroke MP-C-15A-SMK Controller
Rysunek: MP-C-15A-SMK Controller

Tabela: MP-C-15A-SMK Controller I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 22 VA (DC power, 12 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

DO Triac Outputs (<= 30 VAC, 0.25 A)

4

DO1

Triac output #1

5

COM1

Common connection #1 for DO1 and DO2. COMx terminal can be connected to 24 VAC for high-side switching or to ground for low-side switching.

6

DO2

Triac output #2

7

DO3

Triac output #3

8

COM2

Common connection #2 for DO3 and DO4, allows high-side or low-side switching.

9

DO4

Triac output #4

10

DO5

Triac output #5

11

COM3

Common connection for DO5 and DO6, allows high-side or low-side switching.

12

DO6

Triac output #6

High Power Relay Output

16

DO7

High power relay output, type Form-A

17

DO7

High power relay output, type Form-A

Universal Input/Output Points

18

Ub1

Universal input/output #1, type Ub

19

RET

Signal return/common/ ground

20

Ub2

Universal input/output #2, type Ub

21

Ub3

Universal input/output #3, type Ub

22

RET

Signal return/common/ ground

23

Ub4

Universal input/output #4, type Ub

24

Ub5

Universal input/output #5, type Ub

25

RET

Signal return/common/ ground

26

Ub6

Universal input/output #6, type Ub

27

Ub7

Universal input/output #7, type Ub

28

RET

Signal return/common/ ground

29

Ub8

Universal input/output #8, type Ub

MP-C-18A-SMK I/O Terminals

Model MP-C-18A-SMK has 18 I/O points, comprised of 10 Universal I/O (type Ub), 4 Triac DO outputs, 3 Relay (Form-A) DO outputs, and 1 High Power Relay (Form-A) DO output. This controller is equipped with7 pluggable terminal blocks and 1 fixed terminal block.

Uwaga

When using the relays on the MP-C-18A-SMK to switch Nonpower-Limited circuits, you must observe proper separation between Triacs and relay outputs. This is necessary in order to achieve the ¼ inch separation requirement at the terminal block entry. For example, when the DO5 relay is used to switch Nonpower-Limited circuits, then the DO4 Triac output must be left vacant (unused).

 
action_zoom_plus_stroke MP-C-18A-SMK Controller
Rysunek: MP-C-18A-SMK Controller

Tabela: MP-C-18A-SMK Controller I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 22 VA (DC power, 12 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

DO Triac Outpluts (<= 30 VAC, 0.25 A)

4

DO1

Triac output #1

5

COM1

Common connection #1 for DO1 and DO2. COMx terminal can be connected to 24 VAC for high-side switching or to ground for low-side switching.

6

DO2

Triac output #2

7

DO3

Triac output #3

8

COM2

Common connection #2 for DO3 and DO4, allows high-side or low-side switching.

9

DO4

Triac output #4

DO Relay Outputs (250 VAC/30 VDC, 2 A)

10

DO5

Relay output #1, isolated contact, type Form-A

11

DO5

Relay output #1, isolated contact, type Form-A

12

DO6

Relay output #2, isolated contact, type Form-A

13

DO6

Relay output #2, isolated contact, type Form-A

14

DO7

Relay output #3, isolated contact, type Form-A

15

DO7

Relay output #3, isolated contact, type Form-A

High Power Relay Output (Form-A, 12 A)

16

DO8

Relay output #4, isolated high power contact, type Form-A

17

DO8

Relay output #4, isolated high power contact, type Form-A

Universal Input/Output Points (Type Ub)

18

Ub1

Universal input/output #1, type Ub

19

RET

Signal return/common/ ground

20

Ub2

Universal input/output #2, type Ub

21

Ub3

Universal input/output #3, type Ub

22

RET

Signal return/common/ ground

23

Ub4

Universal input/output #4, type Ub

24

Ub5

Universal input/output #5, type Ub

25

RET

Signal return/common/ ground

26

Ub6

Universal input/output #6, type Ub

27

Ub7

Universal input/output #7, type Ub

28

RET

Signal return/common/ ground

29

Ub8

Universal input/output #8, type Ub

30

Ub9

Universal input/output #9, type Ub

31

RET

Signal return/common/ ground

32

Ub10

Universal input/output #10, type Ub

MP-C-18B-SMK I/O Terminals

Model MP-C-18B-SMK has 18 I/O points, comprised of 10 Universal I/O (type Ub) and 8 Triac DO outputs. This controller is equipped with 7 pluggable terminal blocks.

 
action_zoom_plus_stroke MP-C-18B-SMK Controller
Rysunek: MP-C-18B-SMK Controller

Tabela: MP-C-18B-SMK Controller I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 22 VA (DC power, 12 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

DO Triac Outpluts (<= 30 VAC, 0.25 A)

4

DO1

Triac output #1

5

COM1

Common connection #1 for DO1 and DO2. COMx terminal can be connected to 24 VAC for high-side switching or to ground for low-side switching.

6

DO2

Triac output #2

7

DO3

Triac output #3

8

COM2

Common connection #2 for DO3 and DO4, allows high-side or low-side switching.

9

DO4

Triac output #4

10

DO5

Triac output #5

11

COM3

Common connection #3 for DO5 and DO6, allows high-side or low-side switching.

12

DO6

Triac output #6

13

DO7

Triac output #7

14

COM4

Common connection #4 for DO7 and DO8, allows high-side or low-side switching.

15

DO8

Triac output #8

Universal Input/Output Points (Type Ub)

18

Ub1

Universal input/output #1, type Ub

19

RET

Signal return/common/ ground

20

Ub2

Universal input/output #2, type Ub

21

Ub3

Universal input/output #3, type Ub

22

RET

Signal return/common/ ground

23

Ub4

Universal input/output #4, type Ub

24

Ub5

Universal input/output #5, type Ub

25

RET

Signal return/common/ ground

26

Ub6

Universal input/output #6, type Ub

27

Ub7

Universal input/output #7, type Ub

28

RET

Signal return/common/ ground

29

Ub8

Universal input/output #8, type Ub

30

Ub9

Universal input/output #9, type Ub

31

RET

Signal return/common/ ground

32

Ub10

Universal input/output #10, type Ub

MP-C-24A-SMK I/O Terminals

Model MP-C-24A-SMK has 24 I/O points, comprised of 16 Universal I/O (type Ub), 4 Universal I/O (type Uc), and 4 Relay (Form-A) DO outputs. This controller is equipped with 7 pluggable terminal blocks.

 
action_zoom_plus_stroke MP-C-24A-SMK Controller
Rysunek: MP-C-24A-SMK Controller

Tabela: MP-C-24A-SMK Controller I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 22 VA (DC power, 12 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

Universal Input/Output Points (Type Uc)

4

Uc1

Universal input/output #1, type Uc

5

RET

Signal return/common/ ground

6

Uc2

Universal input/output #2, type Uc

7

Uc3

Universal input/output #3, type Uc

8

RET

Signal return/common/ ground

9

Uc4

Universal input/output #4, type Uc

DO Relay Outputs (250 VAC/30 VDC, 2 A)

16

DO1

Relay output #1, isolated contact, type Form-A

17

DO1

Relay output #1, isolated contact, type Form-A

18

DO2

Relay output #2, isolated contact, type Form-A

19

DO2

Relay output #2, isolated contact, type Form-A

20

DO3

Relay output #3, isolated contact, type Form-A

21

DO3

Relay output #3, isolated contact, type Form-A

22

DO4

Relay output #4, isolated contact, type Form-A

23

DO4

Relay output #4, isolated contact, type Form-A

Universal Input/Output Points (Type Ub)

32

Ub1

Universal input/output #1, type Ub

33

RET

Signal return/common/ ground

34

Ub2

Universal input/output #2, type Ub

35

Ub3

Universal input/output #3, type Ub

36

RET

Signal return/common/ ground

37

Ub4

Universal input/output #4, type Ub

38

Ub5

Universal input/output #5, type Ub

39

RET

Signal return/common/ ground

40

Ub6

Universal input/output #6, type Ub

41

Ub7

Universal input/output #7, type Ub

42

RET

Signal return/common/ ground

43

Ub8

Universal input/output #8, type Ub

44

Ub9

Universal input/output #9, type Ub

45

RET

Signal return/common/ ground

46

Ub10

Universal input/output #10, type Ub

47

Ub11

Universal input/output #11, type Ub

48

RET

Signal return/common/ ground

49

Ub12

Universal input/output #12, type Ub

50

Ub13

Universal input/output #13, type Ub

51

RET

Signal return/common/ ground

52

Ub14

Universal input/output #14, type Ub

53

Ub15

Universal input/output #15, type Ub

54

RET

Signal return/common/ ground

55

Ub16

Universal input/output #16, type Ub

MP-C-36A-SMK I/O Terminals

Model MP-C-36A-SMK has 36 I/O points, comprised of 20 Universal I/O (type Ub), 8 Universal I/O (type Uc), and 8 Relay (Form-A) DO outputs. This controller is equipped with 10 pluggable terminal blocks.

 
action_zoom_plus_stroke MP-C-36A-SMK Controller
Rysunek: MP-C-36A-SMK Controller

Tabela: MP-C-36A-SMK Controller I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz,33 VA (DC power, 18 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

Universal Input/Output Points (Type Uc)

4

Uc1

Universal input/output #1, type Uc

5

RET

Signal return/common/ ground

6

Uc2

Universal input/output #2, type Uc

7

Uc3

Universal input/output #3, type Uc

8

RET

Signal return/common/ ground

9

Uc4

Universal input/output #4, type Uc

10

Uc5

Universal input/output #5, type Uc

11

RET

Signal return/common/ ground

12

Uc6

Universal input/output #6, type Uc

13

Uc7

Universal input/output #7, type Uc

14

RET

Signal return/common/ ground

15

Uc8

Universal input/output #8, type Uc

DO Relay Outputs (250 VAC/30 VDC, 2 A)

16

DO1

Relay output #1, isolated contact, type Form-A

17

DO1

Relay output #1, isolated contact, type Form-A

18

DO2

Relay output #2, isolated contact, type Form-A

19

DO2

Relay output #2, isolated contact, type Form-A

20

DO3

Relay output #3, isolated contact, type Form-A

21

DO3

Relay output #3, isolated contact, type Form-A

22

DO4

Relay output #4, isolated contact, type Form-A

23

DO4

Relay output #4, isolated contact, type Form-A

24

DO5

Relay output #5, isolated contact, type Form-A

25

DO5

Relay output #5, isolated contact, type Form-A

26

DO6

Relay output #6, isolated contact, type Form-A

27

DO6

Relay output #6, isolated contact, type Form-A

28

DO7

Relay output #7, isolated contact, type Form-A

29

DO7

Relay output #7, isolated contact, type Form-A

30

DO8

Relay output #8, isolated contact, type Form-A

31

DO8

Relay output #8, isolated contact, type Form-A

Universal Input/Output Points (Type Ub)

32

Ub1

Universal input/output #1, type Ub

33

RET

Signal return/common/ ground

34

Ub2

Universal input/output #2, type Ub

35

Ub3

Universal input/output #3, type Ub

36

RET

Signal return/common/ ground

37

Ub4

Universal input/output #4, type Ub

38

Ub5

Universal input/output #5, type Ub

39

RET

Signal return/common/ ground

40

Ub6

Universal input/output #6, type Ub

41

Ub7

Universal input/output #7, type Ub

42

RET

Signal return/common/ ground

43

Ub8

Universal input/output #8, type Ub

44

Ub9

Universal input/output #9, type Ub

45

RET

Signal return/common/ ground

46

Ub10

Universal input/output #10, type Ub

47

Ub11

Universal input/output #11, type Ub

48

RET

Signal return/common/ ground

49

Ub12

Universal input/output #12, type Ub

50

Ub13

Universal input/output #13, type Ub

51

RET

Signal return/common/ ground

52

Ub14

Universal input/output #14, type Ub

53

Ub15

Universal input/output #15, type Ub

54

RET

Signal return/common/ ground

55

Ub16

Universal input/output #16, type Ub

56

Ub17

Universal input/output #17, type Ub

57

RET

Signal return/common/ ground

58

Ub18

Universal input/output #18, type Ub

59

Ub19

Universal input/output #19, type Ub

60

RET

Signal return/common/ ground

61

Ub20

Universal input/output #20, type Ub

IP-IO Modules

The IP-IO module is used with BACnet/IP controllers to provide expanded I/O to HVAC and smoke control applications over BACnet/IP. IP-IO modules can share their I/O resources across applications running in automation servers or BACnet/IP controllers. IP-IO modules can be installed near facilities in the field, where they are needed, and do not need to be located near the associated automation server or BACnet/IP controller. The various models of IP-IO module offer a flexible mix of I/O point types. All IP-IO models are based on the same hardware platform as the smaller MP-C controller models, which are 6 inches (153 mm) in length, and have the same mounting options. As with the controllers, the IP-IO modules can be snapped onto a DIN rail or screw-mounted onto a flat surface inside a cabinet. All IP-IO modules allow the field-installation of the optional MP-C Display module, which is used to present input and output conditions, as well as communications parameters.

Uwaga

In smoke control applications, the control output override capability must be fully supervised. This is the case with MP-C controllers, which are programmable. However, with Display modules installed on IP-IO modules, this override function must be disabled in all smoke control applications because while the function will work, it cannot be supervised. This is done in the IP-IO module application configuration by disabling the control output override capability of the Display module.

To support the override disable function, the IP-IO modules with a display module should use one of the following firmware versions:

  • version 2.00.03.02201 (and later)

  • version 4.00.03.02000 (and later)

Refer to the EcoStruxure BMS Smoke Control System Approved Software Revisions document (01-16001-xx-en) to identify later approved versions.

The IP-IO module pictured below is a representative model (IP-IO-UIO5DOFA4-SMK). There are three models of the IP-IO module, described in the subsequent sections. Each features terminal blocks and legends appropriate to the I/O configuration supported by that model.

 
action_zoom_plus_stroke IP-IO Module (Model IP-IO-UIO5DOFA4-SMK Shown)
Rysunek: IP-IO Module (Model IP-IO-UIO5DOFA4-SMK Shown)
I/O Point Types

There are three models of the IP-IO module. The I/O point types and capacities for the IP-IO models are presented in the following table.

Tabela: IP-IO Modules - I/O Point Types and Capacities

I/O Point Types

IP-IO-DI10-SMK

IP-IO-UIO10-SMK

IP-IO-UIO5DOFA4

Digital inputs

10

Universal I/O type Ub

10

5

Relay outputs (Form-A)

3

High power relay outputs (Form-A)

1

Digital Outputs

All IP-IO-UIO5DOFA4 model provides Digital Outputs in two types, listed in the following table.

Tabela: Digital Output Types for IP-IO

Digital Output Types

Description

Relay outputs (Form-A)

For switching up to 250 VAC/30 VDC, 2 A

High power relay (Form-A)

For switching up to 250 VAC/24 VDC, 12 A

Analog Outputs

The Universal I/O Type points can be configurred as Analog Outputs with 0 to 10 VDC output, in addition to their Universal Input function.

Mounting Dimensions

Tabela: IP-IO Module Mounting Dimensions

Model

Dimensions

All IP-IO models

153 W x 110 H x 64 D mm (6.0 W x 4.3 H x 2.5 D in.)

 
action_zoom_plus_stroke IP-IO Module Mounting Dimensions
Rysunek: IP-IO Module Mounting Dimensions
Mounting Orientation

For the UL864 applications discussed in this guide, the IP-IO modules must be mounted in the common horizontal orientation as seen in the dimensional drawing, above. This restriction helps to achieve compliance with internal component temperature limits, as required by UL864 derating for increased reliability.

Mounting on DIN Rail

Mounting the IP-IO on a DIN rail is a simple snap-on process, as illustrated below.

 
action_zoom_plus_stroke IP-IO Installation on a DIN Rail
Rysunek: IP-IO Installation on a DIN Rail
Mounting Inside an Enclosure

The IP-IO can also be installed with screws on a flat surface inside a cabinet. Więcej informacji zawiera the SpaceLogic IP-IO-SMK I/O Module Models Installation Sheet . which includes a full-scale template for the required screw mounting holes.

IP-IO-DI10-SMK I/O Terminals

Model IP-IO-DI10-SMK has 10 Digital input points, and is equipped with 4 pluggable terminal blocks. This IP-IO module provides expanded Digital Inputs to one or more controllers over the IP network, but in itself has no application programming features.

 
action_zoom_plus_stroke IP-IO-DI10-SMK Module
Rysunek: IP-IO-DI10-SMK Module

Tabela: IP-IO-DI10-SMK Module I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 17 VA (DC power, 9 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

Digital Input Points (DI only)

18

DI1

Digital input #1

19

RET

Signal return/common/ ground

20

DI2

Digital input #2

21

DI3

Digital input #3

22

RET

Signal return/common/ ground

23

DI4

Digital input #4

24

DI5

Digital input #5

25

RET

Signal return/common/ ground

26

DI6

Digital input #6

27

DI7

Digital input #7

28

RET

Signal return/common/ ground

29

DI8

Digital input #8

30

DI9

Digital input #9

31

RET

Signal return/common/ ground

32

DI10

Digital input #10

IP-IO-UIO10-SMK I/O Terminals

Model IP-IO-UIO10-SMK has 10 Universal Input/Output points, and is equipped with 4 pluggable terminal blocks. This IP-IO module provides expanded Universal I/O (type Ub) to one or more controllers over the IP network, but in itself has no application programming features. The Universal I/O (type Ub) in the IP-IO module is identical to those described for the MP-C controllers.

 
action_zoom_plus_stroke IP-IO-UIO10-SMK Module
Rysunek: IP-IO-UIO10-SMK Module

Tabela: IP-IO-UIO10-SMK Module I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 17 VA (DC power, 9 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

Universal Input/Output Points (Type Ub)

18

Ub1

Universal input/output #1, type Ub

19

RET

Signal return/common/ ground

20

Ub2

Universal input/output #2, type Ub

21

Ub3

Universal input/output #3, type Ub

22

RET

Signal return/common/ ground

23

Ub4

Universal input/output #4, type Ub

24

Ub5

Universal input/output #5, type Ub

25

RET

Signal return/common/ ground

26

Ub6

Universal input/output #6, type Ub

27

Ub7

Universal input/output #7, type Ub

28

RET

Signal return/common/ ground

29

Ub8

Universal input/output #8, type Ub

30

Ub9

Universal input/output #9, type Ub

31

RET

Signal return/common/ ground

32

Ub10

Universal input/output #10, type Ub

IP-IO-UIO5DOFA4-SMK I/O Terminals

Model IP-IO-UIO5DOFA4-SMK has 9 I/O points, comprised of 5 Universal I/O (type Ub), 3 Relay (Form-A) DO outputs, and 1 High Power Relay DO output (Form-A), and is equipped with 4 pluggable terminal blocks. This IP-IO module provides expanded I/O points to one or more controllers over the IP network, but in itself has no application programming features. The Universal I/O (type Ub) in the IP-IO module is identical to those described for the MP-C controllers.

 
action_zoom_plus_stroke IP-IO-UIO05DOFA4-SMK Module
Rysunek: IP-IO-UIO05DOFA4-SMK Module

Tabela: IP-IO-UIO05DOFA4-SMK Module I/O Terminals

Terminal Number

Designation

Description

Power Input

1

24 VAC

24 VAC, 50/60 Hz, 17 VA (DC power, 9 W, not approved for UL864)

2 or 3

 
action_zoom_plus_stroke

Low side of 24 VAC transformer and ground connection.

Terminals 2 and 3 internally connect to all RET terminals.

DO Relay Outputs (250 VAC/30 VDC, 2 A)

10

DO1

Relay output #1, isolated contact, type Form-A

11

DO1

Relay output #1, isolated contact, type Form-A

12

DO2

Relay output #2, isolated contact, type Form-A

13

DO2

Relay output #2, isolated contact, type Form-A

14

DO3

Relay output #3, isolated contact, type Form-A

15

DO3

Relay output #3, isolated contact, type Form-A

High Power Relay Output (Form-A, 12 A)

16

DO4

Relay output #4, isolated high power contact, type Form-A

17

DO4

Relay output #4, isolated high power contact, type Form-A

Universal Input/Output Points (Type Ub)

18

Ub1

Universal input/output #1, type Ub

19

RET

Signal return/common/ ground

20

Ub2

Universal input/output #2, type Ub

21

Ub3

Universal input/output #3, type Ub

22

RET

Signal return/common/ ground

23

Ub4

Universal input/output #4, type Ub

24

Ub5

Universal input/output #5, type Ub

25

RET

Signal return/common/ ground

MP-C Display Module

The optional MP-C Display module is designed to be mounted on any of the MP-C and IP-IO models. The Display module provides a backlit LCD display and 5 operator keys. On the Display module you can observe the condition or value of all digital and analog inputs and outputs. You can also manually override analog and digital outputs for testing, commissioning, and maintenance of equipment connected to those outputs.

 
action_zoom_plus_stroke MP-C Display Module
Rysunek: MP-C Display Module

The Display module can be easily installed in the receptacle located under the center cover plate of the MP-C controller or IP-IO module by removing the cover plate from the right side of the device and then pressing the Display module into place until the locking clips on the top and bottom snap into position. The Display module is designed to be mounted only once. Once installed, it cannot be removed without causing damage to the module or the device to which it is attached.

 
action_zoom_plus_stroke  MP-C Display Module Installation on an MP-C
Rysunek: MP-C Display Module Installation on an MP-C
UL864 Requirements When Installing on MP-C Controller

When the MP-C Display module is attached to the MP-C controller, the full set of functions and features are allowed. However, this requires override monitoring by the application and reporting to the FSCS. The I/O properties in the MP-C provide an indication to the application program, showing whether the point has been placed in the manual/Hand On or Off position. For all control points associated with the smoke control application, the manual control state must be supervised by the application, and if any of the points are found in the manual/Hand condition, the application must activate the system fault on the FSCS panel, including both audible and visual annunciations. The application may provide supplemental indication on the FSCS, showing the cause of the fault alarm to be output point override. This is the same requirement as that imposed on all other controller models that provide local, individual HOA override toggle switches that are monitored and whose alerts are indicated on the FSCS.

Więcej informacji zawiera FSCS Basics .

UL864 Requirements When Installing on IP-IO Modules

When the MP-C Display module is installed on an IP-IO module, the IP-IO application must be configured to disable all override functions from the Display module, so that the analog or digital outputs cannot be overridden. The reason for this requirement is that in the IP-IO application environment, the IP-IO module does not provide program objects capable of detecting and monitoring the output override conditions. The Display module may still be used to observe and control the IP communications properties and to display the condition and values associated with all analog and digital inputs and outputs.

To support the override disable function, the IP-IO modules with a display module should use one of the following firmware versions:

  • version 2.00.03.02201 (and later)

  • version 4.00.03.02000 (and later)

Refer to the EcoStruxure BMS Smoke Control System Approved Software Revisions document (01-16001-xx-en) to identify later approved versions.

  • EcoStruxure BMS Module Installation
  • FSCS Basics
  • Terminal Base Installation
  • Power Rating
  • Electronics Module Installation
  • PS-24V Power Supply Module
  • Automation Server Installation
  • RS-485 Field Bus Cable Routing
  • Module and MP Controller Status LEDs
  • Central IO Module Installation
  • I/O Types for Modules and MP Controllers
  • Central IO Modules Terminal Connections