earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Hardware Installation

Hardware Installation


Products: RP-C
Functionalities: Hardware
Product version: 2022, 2023, 2024, 7.0
9/1/2023

SpaceLogic™ RP-C 230 V

Part numbers: SXWRCF16A10003 and SXWRCF16B10002

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Reference Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Recommended Installation Location

It is recommended to install the controller in an enclosure (cabinet), unless local regulations allow an exception. The controller is intended for fan coil, ceiling systems, and other applications. It can be equipped with optional covers to reduce access to screw terminals and wires.

Dimensions

 
action_zoom_plus_stroke

Installation Orientation Restrictions

 
action_zoom_plus_stroke

Installing the Device on a DIN Rail in a Cabinet

Notice

CONTROLLER DAMAGE

Use the DIN rail end clip when you install the controller on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke

Installing the Device on a Flat Surface in a Cabinet

 
action_zoom_plus_stroke

Installing and Removing the Optional Covers

 
action_zoom_plus_stroke

Connections

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

  • Disconnect all line voltage connected to the controller and its relay outputs before working on the device.

  • More than one disconnect switch may be required to de-energize this equipment before servicing.

  • Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the controller universal inputs/outputs.

Failure to follow these instructions will result in death or serious injury.

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Never connect the 24 VAC supply output terminals 4 and 5 to any other power supply output, regardless of polarity.

Failure to follow these instructions will result in death or serious injury.

Warning Warning

HAZARD OF ELECTRIC SHOCK

For RP-C-16A-F-230V hardware version 9 and earlier, do not connect signal ground (RET terminals, USB shield, Ethernet network shield, or antenna shield) between RP-C controllers without connecting at least one of the RET terminals to protective earth ground.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Notice

EQUIPMENT DAMAGE

Do not connect signal ground (RET terminals, USB shield, Ethernet network shield, or antenna shield) between RP-C controllers.

Failure to follow these instructions can result in equipment damage.

Notice

CONTROLLER DAMAGE

Before powering up the controller, ensure that the input power voltage level meets the specifications of the controller.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke
 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)

For information on wiring, including connection diagrams, rating of and location of fuses (circuit breakers), and cable specifications, see the SpaceLogic and EasyLogic - Hardware Reference Guide.

Part Numbers

Product

Part number

RP-C-16A-F-230V
SXWRCF16A10003
RP-C-16B-F-230V
SXWRCF16B10002
Optional covers
SXWRPCCOV10001

DIN-rail end clip, 25 pieces

SXWDINEND10001

Isolated RS-485 adapter (cable not included)
SXWISORS48510001
Non-isolated RS-485 adapter (cable not included)
SXWNISORS48510001
RS-485 power adapter (cable not included)
SXWNISORS485P10001

For more information on the RS-485 adapters and the cable required, see the RS-485 Adapter and RS-485 Power Adapter Installation Sheets.

Specifications

AC input
Nominal voltage
230 VAC
 
action_zoom_plus_stroke
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 W
Overvoltage category
III
Pollution degree
2
AC output
Type
Isolated Class 2 output
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Power rating
19 VA
Port types
USB device port
Mini-B
USB host port
Type-A, 5 VDC, 0.5 A
Ethernet port 1 and 2
10/100BASE-TX RJ45
RS-485 port Com A and Com B
24 VDC, 3 W, RS-485 (RJ45)
Wireless connectivity
Bluetooth ® Low Energy (Bluetooth ® 5)
2.402 to 2.480 GHz, max. 10 dBm output power, 100 m (328 ft) line-of-sight range
Antenna
Integrated antenna
Approved external antenna (optional)
Manufacturer: Linx Technologies, Model: ANT-2.4-WRT-MON-SMA, Gain: 0.8 dBi, Type: Monopole, Impedance: 50 ohm, Connector: SMA
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
  
See section Installation Orientation Restrictions.
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
IP networking
IP address assignment methods
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
Ub – Universal I/O
Input rating
24 VDC
 
action_zoom_plus_stroke
, 2.4 mA
Voltage output rating
0 to 10 VDC
 
action_zoom_plus_stroke
, 2.4 kohm (min.)
Channels
8
DO – Relay outputs
Relay contact rating
Pilot Duty (C300)
  
Min. current: 100 mA (5 VDC)
  
Resistive: 250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
,
  
4 A (cos phi = 1)
  
Inductive: 250 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
,
  
4 A (cos phi = 0.4)
Channels
3
DO – High power relay outputs
Relay contact rating
Pilot Duty (B300)
  
Normally Open, resistive: 250 VAC
 
action_zoom_plus_stroke
  
/ 24 VDC
 
action_zoom_plus_stroke
, 12 A (cos phi = 1)
  
Normally Closed, inductive: 250 VAC
 
action_zoom_plus_stroke
  
/ 24 VDC
 
action_zoom_plus_stroke
, 3 A (cos phi = 0.4)
Channels
1
DO – Solid-state relay outputs
Output rating
30 VAC
 
action_zoom_plus_stroke
/ 30 VDC
 
action_zoom_plus_stroke
, 2 A
  
Max. 4 A total load
Channels
4

Differences from Previous Hardware Versions

For information on differences from previous versions, see the SpaceLogic and EasyLogic - Hardware Reference Guide.

eu.bac Approved Controller Applications

A eu.bac approved controller application must operate in the controller to maintain compliance with the eu.bac certification. Approved controller applications can be downloaded from the Schneider Electric BMS Applications website, bms-applications.schneider-electric.com.

 
action_zoom_plus_stroke