规格

规格


产品: RP-IO
功能: 工程, 硬件
产品版本: 7.0
2025/8/2

EasyLogic RP-IO

arrow1_rotation简介 arrow1_rotation原生 BACnet MS/TP 支持 arrow1_rotation全系列 I/O 模块型号 arrow1_rotation多种 I/O 点组合型号 arrow1_rotation内置绝缘电源 arrow1_rotation可选盖板 arrow1_rotation高级监控 arrow1_rotationEasyLogic 生效空间传感器 arrow1_rotation全面的 EcoStruxure Building Operation 软件支持 arrow1_rotation使用已签名的固件进行升级 arrow1_rotation规格 arrow1_rotation端子
 
action_zoom_plus_stroke RP-IO-16E-M-24V
图: RP-IO-16E-M-24V

简介

EasyLogic™ RP-IO 模块通过 BACnet MS/TP 对您的 HVAC 应用程序提供 I/O 扩展。I/O 模块可跨自动化服务器、RP 和 MP 控制器或第三方系统中运行的应用程序共享其 I/O 资源。借助对本地报警和本地趋势日志的支持,I/O 模块避免网络上不必要的流量,同时能够在本地记录重要的信息。I/O 模块可安装在现场设施附近,远离自动化服务器或 RP 或 MP 控制器。

RP-IO 具有以下功能:

  • 原生 BACnet MS/TP 支持

  • 全系列 I/O 模块型号

  • 通用板载 I/O 点组合

  • 内置绝缘电源

  • 可选盖板

  • 高级监控

  • EasyLogic 实时空间传感器

  • 全面的 EcoStruxure Building Operation 软件支持,提供高效的工程工具

  • 使用已签名的固件进行升级

A maximum of three RP-IO modules can be used with an RP or MP controller. For more information, see the Architectural Guidelines.

原生 BACnet MS/TP 支持

The EasyLogic range of RP and MP controllers and RP-IO I/O modules natively communicate with automation servers and field devices using the BACnet MS/TP protocol.

The RS-485 port with 3-pole screw terminal block is used for connection to the BACnet MS/TP network.

全系列 I/O 模块型号

基于 BACnet MS/TP 的 EasyLogic RP-IO 系列 I/O 模块包括两种不同的型号,它们提供两组不同的 I/O 点类型,分别命名为 12A 和 16E。这两种型号支持 24 伏交流/直流电源。

 
action_zoom_plus_stroke

多种 I/O 点组合型号

RP-IO-12A 和 -16E 模块提供 12 或 16 I/O 点,包括两组不同的 I/O 点类型。I/O 点类型的通用组合可匹配众多 HVAC 应用类型。通用输入/输出极其灵活度,既可配置为输入也可配置为输出。

表格: I/O Point Types by RP-IO Models

I/O Point Types

RP-IO-12A model

RP-IO-16E model

Universal I/O

Type Ub

8

16

Solid-state relay outputs

(MOSFET)

4

-

表格: Configurations by I/O Point Types

Configurations

Universal I/O

Type Ub

Solid-state Relay Outputs

(MOSFET)

Digital inputs

yes

-

Counter inputs

yes

-

Supervised inputs

yes

-

Voltage inputs

(0 to 10 VDC)

yes

-

Current inputs

(0 to 20 mA)

yes

-

Temperature inputs

yes

-

Resistive inputs

yes

-

Voltage outputs

(0 to 10 VDC)

yes

-

Digital outputs

-

yes

Digital pulsed outputs

-

yes

PWM outputs

-

yes

Tristate outputs

-

yes

Tristate pulsed outputs

-

yes

通用输入/输出

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs are capable of supporting analog outputs of type voltage outputs. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs should be connected to the universal inputs/outputs.

固态继电器输出

The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.

内置绝缘电源

The device has a built-in power supply designed to accommodate 24 VAC or 24 VDC input power. The AC/DC power input is galvanically isolated from the electronics. This minimizes the risk of damage due to earth currents and permits the input power to be wired without concern for AC polarity matching. With the isolated AC/DC power input, you can use a central transformer for many devices, instead of one transformer for each device, to reduce installation costs.

可选盖板

所有 RP-IO 型号可配备可选的盖板以减少对于螺钉端子和线的触及。

高级监控

The I/O module supports local trends and alarms, enabling local operation when the I/O module is offline.

With user-defined fallback values, the I/O module outputs will be in a predictable state in cases of network disruption.

The battery-free power backup of the memory helps prevent data loss and allows seamless and quick recovery after a power disruption.

In WorkStation, you update the firmware of multiple I/O modules at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the I/O modules. The server can host I/O modules of different firmware versions.

EasyLogic 生效空间传感器

The EasyLogic Sensor devices provide a cost-effective solution to measure, control, and communicate the temperature. The sensors are connected to analog inputs of the RP or MP controller. The EasyLogic Sensor devices are available in two models with different user interfaces, a blank cover or an LCD display with buttons for setpoint control. For more information, see the EasyLogic Sensors - Temperature Sensors – Analog - Specification Sheet.

 
action_zoom_plus_stroke EasyLogic 传感器设备
图: EasyLogic 传感器设备

全面的 EcoStruxure Building Operation 软件支持

The power of the I/O module is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:

  • WorkStation/WebStation interface

  • Device discovery

  • Engineering efficiency

WorkStation/WebStation 界面

WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor the I/O modules and RP and MP controllers. For more information, see the WorkStation and WebStation specification sheets.

设备发现

The enhanced Device Discovery in WorkStation enables you to easily identify the I/O modules on a BACnet network and to associate the I/O modules with their parent server.

工程效率

The engineering and maintenance of the I/O modules can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete I/O module application that contains I/O point configurations and all necessary objects such as trends and alarms. The I/O module application in the Custom Types library is reusable across all I/O modules of the same model. You can use the I/O module application as a base for creating new I/O modules intended for similar applications. You can then edit the I/O module application, and the changes are automatically replicated to all I/O modules, while each I/O module keeps its local values.

WorkStation supports both online and offline engineering of the I/O modules. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the I/O modules later.

Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the RP and MP controllers and the I/O modules before you deploy your server, controller, and I/O module applications to the servers, controllers, and I/O modules on site. For more information, see the Project Configuration Tool specification sheet.

使用已签名的固件进行升级

Using digitally signed firmware provides more secure upgrading of the device. During an upgrade, the device verifies that the firmware is authentic and uncompromised Schneider Electric firmware. If the device detects discrepancies in the authenticity or integrity of the firmware, it will reject the upgrade. Once the device is upgraded with signed firmware, all upgrades thereafter must be with a signed firmware version.

表格: EasyLogic RP-IO 的零件号

产品

部件号

RP-IO-12A-M-24V
SXWRIOF12AM10001
RP-IO-16E-M-24V
SXWRIOF16EM10001

表格: RP-C 配件的零件号

产品

部件号

Optional covers
SXWRPCCOV10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001

For more information on part numbers for Network Connectivity Accessories, see the 有关更多信息,请参阅 Product Selection Guide - EcoStruxure Building ..

规格

AC input
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
7 VA
Power input protection
MOV suppression and internal fuse
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
3 W
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-IO-12A-M-24V
0.336 kg (0.741 lb)
Weight, RP-IO-16E-M-24V
0.334 kg (0.736 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Terminal blocks
Power and I/O: Fixed
  
BACnet MS/TP communications: Removable
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, optional covers
0.070 kg (0.154 lb)
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 5.0.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed a
Fire performance in air-handling spaces a
UL 2043
Communication ports
RS-485 port
RS-485 (3-pole screw terminal block)
  
Transient voltage suppressors on communication signals
RS-485 transceiver characteristics
Transceiver type
Failsafe
  
Non-isolated
External biasing
None required
Total Unit Load (UL) per device
Maximum 0.5 UL
Communications
BACnet
BACnet MS/TP, maximum bus length: 1200 m (4000 ft), maximum baud rate: 76800
  
BTL B-ASC (BACnet Application Specific Controller) a
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 single-core
Internal SRAM
6 MB
NOR flash memory
32 MB
Memory backup
128 kB a , FRAM, non-volatile
Universal inputs/outputs
Channels, RP-IO-12A-M-24V
8 Ub, Ub1 to Ub8
Channels, RP-IO-16E-M-24V
16 Ub, Ub1 to Ub16
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Universal input/output protection
Transient voltage suppressor on each universal input/output
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
1.0 mV
Impedance
1 Mohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
2.4 kohm
Source current
+4.2 mA
Sink current
-1 mA (0 to 0.4 VDC)
  
-4.2 mA (0.4 to 10 VDC)
Solid-state relay outputs, DO
Channels, RP-IO-12A-M-24V
4, DO1 to DO4
Channels, RP-IO-16E-M-24V
0
Output rating
Maximum 2 A load per output
  
Maximum 4 A total load for the 4 outputs
AC voltage range
Maximum 30 VAC
DC voltage range
Maximum 30 VDC
Commons
COM1 for DO1 and DO2 (on RP-IO-12A model)
  
COM2 for DO3 and DO4 (on RP-IO-12A model)
When the SSR outputs are used to switch AC, the common terminals can be connected to 0 to 30 VAC. When the SSR outputs are used to switch DC, the common terminals can be connected to -30 VDC to +30 VDC.
Common voltage range (AC)
0 to 30 VAC
Common voltage range (DC)
-30 to +30 VDC
Minimum pulse width
100 ms
Solid-state relay output protection
Transient voltage suppressor across each solid-state relay (SSR) output

端子

For more information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

 
action_zoom_plus_stroke RP-IO-12A-M-24V 型号
图: RP-IO-12A-M-24V 型号
 
action_zoom_plus_stroke RP-IO-16E-M-24V 型号
图: RP-IO-16E-M-24V 型号
  • Enterprise Server
  • SpaceLogic AS-P
  • SpaceLogic AS-B
  • WorkStation
  • WebStation
  • 项目配置工具 - 版本 2
  • Wiring