Part numbers: SXWMPC15A10001, SXWMPC18A10001, SXWMPC18B10001, SXWMPC24A10001, and SXWMPC36A10001
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
|
Product |
Part number |
|
MP-C-15A |
SXWMPC15A10001 |
|
MP-C-18A |
SXWMPC18A10001 |
|
MP-C-18B |
SXWMPC18B10001 |
|
MP-C-24A |
SXWMPC24A10001 |
|
MP-C-36A |
SXWMPC36A10001 |
|
MP-C DISPLAY
(MP-C override display module)
|
SXWMPCDSP10001 |
|
Spare terminal blocks for all MP-C models |
SXWMPCCON10001 |
|
DIN-rail end clip, 25 pieces |
SXWDINEND10001 |
|
Non-isolated RS-485 adapter (cable not included)
|
SXWNISORS48510001
|
|
RS-485 power adapter (cable not included)
|
SXWNISORS485P10001
|
| AC input | |
Nominal voltage
|
24 VAC
|
Power consumption
|
MP-C-15A, -18A, -18B: 22 VA
|
MP-C-24A: 28 VA
|
|
MP-C-36A: 33 VA
|
|
| DC input | |
Nominal voltage
|
24 to 30 VDC
|
Power consumption
|
MP-C-15A, -18A, -18B: 12 W
|
MP-C-24A: 15 W
|
|
MP-C-36A: 18 W
|
|
| Port types | |
USB device port
|
Mini-B
|
USB host port
|
Type-A
|
Ethernet port 1 and 2
|
10/100BASE-TX (RJ45), IEEE 802.3 compliant
|
RS-485 port Com A
|
24 VDC, 2 W, RS-485 (RJ45)
|
| Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F) at normal operation
|
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
|
|
See section Installation Orientation Restrictions.
|
|
MP-C Display temperature range: -30 to +60 °C (-22 to +140 °F)
|
|
Humidity
|
Maximum 95 % RH non-condensing
|
| Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94-5VB
|
| IP networking | |
IP address assignment methods
|
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
|
| Ub – Universal I/O | |
Input rating
|
24 VDC
|
Voltage output rating
|
0 to 10 VDC
|
Channels
|
MP-C-15A: 8; -18A: 10; -18B: 10;
|
-24A: 16; -36A: 20
|
|
| Uc – Universal I/O | |
Input rating
|
24 VDC
|
Voltage output rating
|
0 to 10 VDC
|
Current output rating
|
0 to 20 mA, 650 ohm (max.)
|
Channels
|
MP-C-15A: 0; -18A: 0; -18B: 0;
|
-24A: 4; -36A: 8
|
|
| DO – Relay outputs | |
Relay contact rating
|
250 VAC
|
Pilot Duty (C300)
|
|
Channels
|
MP-C-15A: 0; -18A: 3; -18B: 0;
|
-24A: 4; -36A: 8
|
|
| DO – High power relay outputs | |
Relay contact rating
|
250 VAC
|
Pilot Duty (B300)
|
|
Channels
|
MP-C-15A: 1; -18A: 1; -18B: 0;
|
-24A: 0; -36A: 0
|
|
| DO – Triac outputs | |
Triac rating
|
Max. 30 VAC
|
Channels
|
MP-C-15A: 6; -18A: 4; -18B: 8;
|
-24A: 0; -36A: 0
|
|