earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
How to

How to


Products: Commission, IP-IO , MP-C, MP-V, RP-C
Functionalities: Engineering, BACnet/IP devices
Product version: 2022, 2023
3/6/2025

Restarting a BACnet/IP Controller

Use the Device Restart function to perform a device restart of the BACnet/IP controller.

Show More
action_close

Use the Device Restart function of the Commission mobile application to perform a restart of the BACnet/IP controller. There are four different ways to restart the BACnet/IP controller.

Restart Type

Description

Warm Start

Perform a Warm Start when you want to reset the controller and want to retain all Warm Start properties and Cold Start properties. Perform a Warm Start to troubleshoot any device malfunctions.

Cold Start

Perform a Cold Start when you want to reset the controller and want to retain all Cold Start properties which excludes Warm Start properties. Perform a Cold Start to troubleshoot any device malfunctions after a Warm Start has not resolved the issue.

Erase Controller Database

Erase the controller database to clear any applications in the controller and before deploying a new application. Erasing the controller database will retain only the network settings, RSTP, and BACnet ID. As a best practice, erase the controller database before deploying a new application to the controller.

For more information, see Restarting a BACnet/IP Controller .

To restart a BACnet/IP controller
  1. In the Commission mobile application, connect to one or more BACnet/IP controllers.

  2. On the tab bar, click Configure .

  3. Click Controller Restart .

  4. On the Device Restart page, select the type of restart you want to perform. For more information, see Restarting a BACnet/IP Controller .

    Important:

    You cannot restart a controller that is hosted.

  5. Click Restart .

  6. A Warning window displays. Click Ok .

Each controller is restarted.

  • Device Restart