Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
Product |
Part number |
RP-C-EXT-BL-2-LV-PD
|
SXWREB2LVPD10001
|
RP-C-EXT-BL-4-HV-PD
|
SXWREB4HVPD10001
|
DIN-rail end clip, 25 pieces |
SXWDINEND10001 |
Mounting plate - RP controller expansion modules, 5 pieces |
SXWREMPK510001
|
Use |
Part number |
Reference |
Connector type |
Suitable for cable diameters mm (inches) |
Marking |
Color of coding /housing |
Minimum order quantity |
Power supply input |
SXWRPCCONWWPOW |
91.931.4053.1 |
Female |
5.6–11 (0.22–0.43) |
L, PE, N |
Black /Black |
100 |
Blind outputs (RP-C-EXT-BL-2-LV-PD) |
SXWRPCCONWBLLV |
91.952.4353.0 |
Male |
8.5–12.5 (0.34–0.49) |
5, 4, 3, 2, 1 5, 4, 3: Not used 2: M- 1: M+ |
Light blue /White |
50 |
Blind outputs (RP-C-EXT-BL-4-HV-PD) |
SXWRPCCONWBLHV |
91.942.4053.1 |
Male |
8.5–12.5 (0.34–0.49) |
N, PE, 1, 2 1: ↑ (UP) 2: ↓ (DOWN) |
Black /Black |
50 |
Digital inputs |
SXWRPCCONWDI |
91.921.2353.0 |
Female |
3.4–5.5 (0.14–0.21) |
1, 2 1: DI1..4 2: RET |
Light blue /White |
100 |
The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.
AC input | |
Nominal voltage
|
230 VAC
![]() |
Power consumption
|
75 VA (RP-C-EXT-BL-2-LV-PD)
|
Maximum current consumption
|
8 A (RP-C-EXT-BL-4-HV-PD)
|
Overvoltage category
|
III
|
DC input | |
Room bus power consumption
|
0.3 W (24 VDC)
|
Port types | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Operation environment, RP-C-EXT-BL-2-LV-PD | |
Ambient temperature, operating
|
0 to 40 °C (32 to 104 °F)
|
See section Installation Orientation Restrictions.
|
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Operation environment, RP-C-EXT-BL-4-HV-PD | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94 V-0
|
Blind outputs, RP-C-EXT-BL-2-LV-PD | |
Outputs
|
2, Blind 1 to Blind 2
|
M+
|
|
M-
|
|
Power distribution
|
24 VDC
![]() |
Maximum 1 A load per output
|
|
Maximum 1.3 A total load for the 2 outputs
|
|
Maximum 2 A starting current (<100 ms) per output
|
|
Blind outputs, RP-C-EXT-BL-4-HV-PD | |
Outputs
|
4, Blind 1 to Blind 4
|
↑ : Blind UP
|
|
↓ : Blind DOWN
|
|
Power distribution
|
230 VAC (same voltage as power supply)
|
Maximum 2 A load per output
|
|
Maximum 8 A total load for the 4 outputs
|
|
DI – Digital inputs | |
Input rating
|
5 VDC
![]() |
Inputs
|
4
|