Specifications

Specifications


Products: RP-C-EXT-REL-4
Functionalities: Engineering, Hardware
Product version: 2023, 2024
5/15/2024

SpaceLogic RP-C-EXT-REL-4

arrow1_rotationIntroduction arrow1_rotationFeatures arrow1_rotationSpecifications arrow1_rotationConnections
 
action_zoom_plus_stroke RP-C-EXT-REL-4 – Relay module

RP-C-EXT-REL-4 – Relay module

Introduction

SpaceLogic™ RP-C-EXT-REL-4 relay module connects to the SpaceLogic RP room controllers and enables power supply and control of lights.

The relay module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

Features

The relay module has the following features:

  • Power and communications through the room bus

  • Four relay outputs for power supply and control of lights

  • Four digital inputs for connection of window contacts. The digital inputs are SELV (Safety Extra-Low Voltage).

  • Measurement of energy consumption per module

  • Wieland connectors for quick and easy installation

  • Engage mobile application for room comfort settings

  • Status LED for the device

  • One status LED for each relay output

  • Rotary switch for address configuration

Room bus

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

The RP-C Pro and RP-C Pro Plus controller room bus supports up to nine connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of seven Multi-sensor or Insight-Sensor devices

The RP-C Advanced controller room bus supports up to six connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of four Multi-sensor or Insight-Sensor devices

The RP-V Advanced controller room bus supports up to four connected RP controller expansion modules with the following restrictions:

  • Maximum of one DALI light module

  • Maximum of one SMI blind module

  • Maximum of two Multi-sensor or Insight-Sensor devices

Maximum total length of the room bus is 72 m (236 ft).

Engage mobile application

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Table: Part Numbers

Product

Part number

RP-C-EXT-REL-4
SXWREREL410001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
Mounting plate - RP controller expansion modules
package of 5 pieces
SXWREMPK510001

Specifications

Electrical
Nominal voltage
100 to 277 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum current consumption
10 A
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.378 kg (0.833 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
Relay outputs: 4 x 3-pin Wieland GST15i3 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Optional mounting plate
The mounting plate is used to facilitate mounting and cable management for the RP controller expansion module as well as to provide strain relief for the connectors.
Dimensions
202 W x 268.3 H x 17.8 D mm (8.0 W x 10.6 H x 0.7 D in.)
 
action_zoom_plus_stroke
Weight
0.306 kg (0.675 lb)
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 3.2.1 and later
Energy metering support
EcoStruxure Building Operation
version 3.3.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed
Fire performance in air-handling spaces a
UL 2043
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Relay status indicator
One status LED (green) for each output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Energy metering
Energy consumption measurement
The energy consumption is measured in Wh, shared by the four outputs.
Voltage range
230 to 277 VAC +/-10 %
Accuracy class (according to IEC 61557-12)
Active energy measurement: Class 1
Typical measurement accuracy at room temperature
20 to 100 W: 5%
  
100 to 3000 W: 1%
Relay outputs
Relay outputs for lights powered by 100 to 277 VAC.
Outputs
4, Relay 1 to Relay 4
Output terminals
N, PE, and L
Power distribution
100 to 277 VAC (same voltage as power supply)
  
Maximum 5 A load per output
  
Maximum 10 A total load for the 4 outputs
  
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Connections

Follow proper installation wiring diagrams and instructions. For more information on wiring, see the SpaceLogic Hardware Reference Guide.

 
action_zoom_plus_stroke RP-C-EXT-REL-4

RP-C-EXT-REL-4

Table: Required External Connectors

Use

Part number

Reference

Connector type

Suitable for cable diameters

mm (inches)

Marking

Color of coding

/housing

Minimum order quantity

Power supply input

SXWRPCCONWWPOW

91.931.4053.1

Female

5.6–11

(0.22–0.43)

L, PE, N

Black

/Black

100

Relay outputs

SXWRPCCONWWREL

91.932.4053.1

Male

5.6–11

(0.22–0.43)

N, PE, L

Black

/Black

100

Digital inputs

SXWRPCCONWDI

91.921.2353.0

Female

3.4–5.5

(0.14–0.21)

1, 2

1: DI1..4

2: RET

Light blue

/White

100

The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.

  • SpaceLogic RP-C Advanced
  • SpaceLogic RP-C-EXT-MS-BLE
  • SpaceLogic RP-C-EXT-DALI
  • SpaceLogic RP-C-EXT-0-10V-4
  • SpaceLogic RP-C-EXT-DALI-M-PD
  • SpaceLogic RP-C-EXT-0-10V-4-PD
  • SpaceLogic RP-C-EXT-BL-2-LV-PD
  • SpaceLogic RP-C-EXT-BL-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-2-LV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-4-HV-PD
  • Commission
  • Engage